I understand that you have tested the shutoff solenoid when removed from the injection pump, and see it moving. At the same time, everything you describe is consistent with a shutoff solenoid that is not operating correctly. So I think I'd go back over that again.
Some sort of internal injection pump failure that causes the generator to go from running fine to no-start seems very unlikely. On the other hand, the little cube solenoids do go bad over time, contacts get pitted, and current slow can be restricted. Perhaps, for example, the cube relay is marginal and allowing enough current to operate the solenoid when removed from the pump, but not enough to actually move the internal mechanism.
I believe there are four of the cube relays; Run, Shutdown, Pre-heat, and Start. Try swapping the Run and Pre-heat relays. Then see if you get fuel at the injectors while cranking with the override switch engaged.
Also check the ground wire connection on the generator end, typically on the side below the junction box. I'm not positive about this particular model, but typically there is a 10mm bolt securing a few ground wires to the chassis. Check that to be sure it's clean and tight. They tend to work loose. Maybe the fuel solenoid ground is marginal, and preventing it from turning on fuel. It's energize-to-run, so without it working, you won't get any fuel out of the injection pump, exactly like you are seeing.[/QUOTE
Hi Twistedtree,
Thanks for digging into this!
The solenoid pops in and out with the override switch activated and I can feel the valve (or sleeve) inside moving in and out when i push it with a small tool. Im not sure what else to check there. I may throw a new one at it just to make sure.
I did swap out the cube relays to different positions and I am getting start and solenoid operation either way.
Also I may try pulling the delivery valve assemblies on the IP to see if there is anything obstructing them.