Old 06-27-2020, 06:40 AM   #1
Guru
 
catalinajack's Avatar
 
City: Edgewater, MD
Country: USA
Vessel Name: Catalina Jack
Vessel Model: Defever 44
Join Date: Nov 2011
Posts: 1,434
Very Hot 60-amp Alternating Current Circuit Breaker

This is the breaker (Square D) on the feed from my 7.7kw Westerbeke. Yesterday, this breaker tripped twice with modest loads and was very hot to the touch. I opened the box this morning and could see nothing obviously wrong except the green line in from the generator is butt-spliced twice. The engine room was very hot but this is nothing new.

My thinking, my knowledge is very limited in this regard, is that the breaker has developed a high internal resistance over time. Am I on the right track or should I be looking elsewhere? We have used this generator extensively over the past two years but I have to admit that I never once felt the breaker box for heat so that this condition may have existed for a long time and is just now becoming acute.
__________________
Advertisement

catalinajack is online now   Reply With Quote
Old 06-27-2020, 07:04 AM   #2
Guru
 
DavidM's Avatar
 
City: Litchfield, Ct/Punta Gorda, Fl
Country: USA
Vessel Model: Atlas Pompano 23
Join Date: Aug 2012
Posts: 5,352
Circuit breakers should not be hot to the touch. Replace it.

David
__________________

DavidM is offline   Reply With Quote
Old 06-27-2020, 07:07 AM   #3
Guru
 
caltexflanc's Avatar
 
City: North Carolina for now
Country: USA
Vessel Name: Small Incentive
Vessel Model: Boston Whaler 130 Sport
Join Date: Aug 2011
Posts: 5,936
It is usually a symptom of a bad connection due to corrosion or looseness. Not always easy to see with a glance. Check all that thoroughly. Typically those sort of breakers are not very expensive, if that's where your investigation leads you.
__________________
George

"There's the Right Way, the Wrong Way, and what some guy says he's gotten away with"
caltexflanc is offline   Reply With Quote
Old 06-27-2020, 07:10 AM   #4
Guru
 
jleonard's Avatar
 
Join Date: Jun 2008
Posts: 3,884
Yes it is possible that the breaker has seen better days.
I used to work with manufacturing residential circuit breakers and they do wear out especially if they are cycled often with high load. The contact points can arc and get pitted then they heat up and trip.
I had a 30 amp breaker fail in my boat.
__________________
Jay Leonard
Attitude Adjustment
40 Albin
Mystic,Ct. /New Port Richey,Fl
jleonard is offline   Reply With Quote
Old 06-27-2020, 07:28 AM   #5
Guru
 
O C Diver's Avatar
 
City: Fort Myers, FL... Summers in Crisfield, MD
Country: USA
Vessel Name: Slow Hand
Vessel Model: Cherubini Independence 45
Join Date: Dec 2010
Posts: 8,780
Is that generator 120 VAC or 240 VAC? Normally I would expect a boat of your size to be wired with two 30 amp or one 50 amp 240 volt shore power connection. So, typically the breaker on that generator would be a double pole 35 amp breaker. Seems odd that you have a 60 amp breaker.

Ted
__________________
Blog: mvslowhand.com
I'm tired of fast moves, I've got a slow groove, on my mind.....
I want to spend some time, Not come and go in a heated rush.....
"Slow Hand" by The Pointer Sisters
O C Diver is online now   Reply With Quote
Old 06-27-2020, 08:31 AM   #6
Guru
 
City: Carefree, Arizona
Country: usa
Vessel Name: sunchaser V
Vessel Model: DeFever 48
Join Date: Apr 2008
Posts: 8,639
CJ
Is the breaker in question the one mounted on the genset itself? If so the "book" should have an electrical diagram noting the OEM breaker specs.
sunchaser is offline   Reply With Quote
Old 06-27-2020, 09:07 AM   #7
Technical Guru
 
Ski in NC's Avatar
 
City: Wilmington, NC
Country: USA
Vessel Name: Louisa
Vessel Model: Custom Built 38
Join Date: Jan 2014
Posts: 5,717
Most of these breakers have two trips: One is thermal where a heating element in line with the load trips it if they get too hot. The other is magnetic that trips it rapidly on a very high overload. So some heat is normal. But if the thing is noticeably hotter than surroundings on modest load, contacts are in bad shape or connections have high resistance.

If connections are solid (snug them) and it is still hot, replace it.
Ski in NC is offline   Reply With Quote
Old 06-27-2020, 11:08 AM   #8
Guru
 
Boat's Avatar
 
City: SchoolHouse Branch
Country: USA
Join Date: Jul 2018
Posts: 591
Breakers go bad in normal use and from abnormal conditions. Check the loads with a clamp meter. Check voltages on both legs to neutral and ground, and to each other, loaded and no load.

Bad breakers can make a freak show of oddball electrical problems.


Be sure to get the right replacement. Don't just match the existing breaker.

Mostly, protect yourself while working with electrical issues. Ever see one of those hot dog cookers where the hot dog is the conductor? Don't be a hot dog.
Boat is offline   Reply With Quote
Old 06-27-2020, 11:23 AM   #9
Guru
 
Comodave's Avatar
 
City: Au Gres, MI
Country: US
Vessel Name: Never Say Never
Vessel Model: President 41 DC
Join Date: Jul 2015
Posts: 8,004
I would certainly swap it out. If it is a Square D breaker it will be cheap and easy to swap so why not give it a try. If it still trips then look more closely at the system.
__________________
Boat Nut:
If you are one there is no explanation necessary.
If you arenít one, there is no explanation possible.
Comodave is offline   Reply With Quote
Old 06-27-2020, 11:57 AM   #10
Guru
 
C lectric's Avatar
 
City: Gibsons, B.C.
Country: Canada
Vessel Name: Island Pride
Vessel Model: xxxx
Join Date: Oct 2007
Posts: 2,908
Circuit breakers do indeed fail.
However, do some checks first. If the fault is not the C.B. itself then a new one will repeat the problem.

Check the actual connections for ANY sign of oxidation which is darkening the lug and the wire .
Check the wire insulation for any sign of discolouring indicating heat buildup.
Check also for looseness as looseness will lead to oxidation .
Any looseness and resulting oxidation will create resistance which will create heat buildup which will discolour the wire itself, its insulation AND likely the C.B. terminal
THat heat buildup will also cause nuisance tripping.

I have had decent results with reterminating the wire back to bright wire or heavy wire brushing, SS wire brush, both the wire and the C.B. side terminals if discoloured and then applying some NoAlox or similar.

But if all are not tight and clean it will repeat.

Before I forget check the actual current flowing through the C.B. Maybe the draw is borderline and with a wee bit of oxidation it goes over the edge.

If the terminals are tight and clean now then the C.B. itself is the likely culprit.
C lectric is offline   Reply With Quote
Old 06-27-2020, 01:08 PM   #11
Guru
 
catalinajack's Avatar
 
City: Edgewater, MD
Country: USA
Vessel Name: Catalina Jack
Vessel Model: Defever 44
Join Date: Nov 2011
Posts: 1,434
Thanks guys for your ideas. I will replace the breaker and report back. This is a 50-amp boat.
catalinajack is online now   Reply With Quote
Old 06-27-2020, 01:10 PM   #12
Guru
 
catalinajack's Avatar
 
City: Edgewater, MD
Country: USA
Vessel Name: Catalina Jack
Vessel Model: Defever 44
Join Date: Nov 2011
Posts: 1,434
Another thought. Why do I even have a circuit breaker? On board is another generator, a Perkins-powered Kohler 12.5kw. The output is wired directly to the panel, no circuit breaker.
catalinajack is online now   Reply With Quote
Old 06-27-2020, 02:33 PM   #13
Senior Member
 
City: St. Petersburg
Country: USA
Join Date: Oct 2007
Posts: 139
Kohler genset is non-compliant as the wire run from the generator to the panel is unprotected by an overcurrent protection device (OCPD).
__________________
Charlie Johnson
CharlieJ is offline   Reply With Quote
Old 06-27-2020, 03:35 PM   #14
Guru
 
catalinajack's Avatar
 
City: Edgewater, MD
Country: USA
Vessel Name: Catalina Jack
Vessel Model: Defever 44
Join Date: Nov 2011
Posts: 1,434
Ah, I always wondered about that. I will look into adding protection on that circuit. Question: how would over current occur coming from a generator that puts out a constant?
Quote:
Originally Posted by CharlieJ View Post
Kohler genset is non-compliant as the wire run from the generator to the panel is unprotected by an overcurrent protection device (OCPD).
catalinajack is online now   Reply With Quote
Old 06-27-2020, 03:40 PM   #15
Senior Member
 
City: St. Petersburg
Country: USA
Join Date: Oct 2007
Posts: 139
Compromised insultation on the output cable.
__________________
Charlie Johnson
CharlieJ is offline   Reply With Quote
Old 06-27-2020, 06:28 PM   #16
Guru
 
City: Clearwater, FL
Country: United States
Vessel Name: Seas the Bay
Vessel Model: 1981 42' Hardin Europa
Join Date: Aug 2016
Posts: 957
Which Kohler 12.5kw genset do you have? What is the model, drawing, and/or build number? Some have over-current protection built into the unit rather than leaving it for one to wire up in a nearby electrical box.
gkesden is offline   Reply With Quote
Old 06-28-2020, 12:21 AM   #17
Guru
 
C lectric's Avatar
 
City: Gibsons, B.C.
Country: Canada
Vessel Name: Island Pride
Vessel Model: xxxx
Join Date: Oct 2007
Posts: 2,908
The RATING you see is not a constant. That rating is the maximum current that it can produce safely without overheating and causing damage to itself.

Under a short circuit condition the amperage could climb greatly although the output voltage would falter.

A C.B. or fuse is needed to protect against shorts. Are you sure there is not one installed as part of the gen set itself?
C lectric is offline   Reply With Quote
Old 06-28-2020, 01:33 PM   #18
Guru
 
catalinajack's Avatar
 
City: Edgewater, MD
Country: USA
Vessel Name: Catalina Jack
Vessel Model: Defever 44
Join Date: Nov 2011
Posts: 1,434
Report - The breaker had to be pried out with a screwdriver. The spring contacts were highly encrusted. Much resistance right there. The plastic housing near the contacts was melted from the heat. The box is being replaced as well. Now, take a look at the picture. Notice the corroded, breaking and broken strands in one of the wires (after I removed the electrical tape) that were connected in an unacceptable manner. Frightening, isn't it? Needless to say, the wiring and connections will be updated properly. There are three black wires that were connected together. Two come from the generator head. The third is the run to my electrical panel along with a white wire and a green wire, all 6 AWG.
Attached Thumbnails
Click image for larger version

Name:	BadWiring.jpg
Views:	29
Size:	78.6 KB
ID:	104345  
catalinajack is online now   Reply With Quote
Old 06-28-2020, 02:02 PM   #19
Guru
 
Comodave's Avatar
 
City: Au Gres, MI
Country: US
Vessel Name: Never Say Never
Vessel Model: President 41 DC
Join Date: Jul 2015
Posts: 8,004
That is some great electrical work there... I would replace the wiring if it is damaged and instead of using a nut and bolt put them on a terminal block. Maybe do an electrical survey of the boat. If they did this, what else have they done? Glad you found the problem.
__________________
Boat Nut:
If you are one there is no explanation necessary.
If you arenít one, there is no explanation possible.
Comodave is offline   Reply With Quote
Old 06-28-2020, 02:12 PM   #20
Guru
 
O C Diver's Avatar
 
City: Fort Myers, FL... Summers in Crisfield, MD
Country: USA
Vessel Name: Slow Hand
Vessel Model: Cherubini Independence 45
Join Date: Dec 2010
Posts: 8,780
Before you get too far into your remediation plan, flex the cables where accessible between the breaker and the main boat panel. The cable should be bendable. I would want to check for stiff sections from compromised insulation or strands fusing together. Might be worth disconnecting the wires at both ends and doing a resistance test with an ohm meter.

Ted
__________________

__________________
Blog: mvslowhand.com
I'm tired of fast moves, I've got a slow groove, on my mind.....
I want to spend some time, Not come and go in a heated rush.....
"Slow Hand" by The Pointer Sisters
O C Diver is online now   Reply With Quote
Reply

Thread Tools Search this Thread
Search this Thread:

Advanced Search
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off





All times are GMT -5. The time now is 06:54 AM.


Powered by vBulletin® Version 3.8.8 Beta 4
Copyright ©2000 - 2020, vBulletin Solutions, Inc.
Search Engine Optimization by vBSEO 3.6.0
Copyright 2006 - 2012
×