At the full rated output, 20kW is 160 amps at 125V, 80 amps at 250V.
I would want the main breaker to permit full load but most boats under 60' or soBut you would not want to run it at that output for extended periods. I am sure there are wiser heads here than mine on this topic, but I like to run my little genny at about 50% load judging by the ammeter I have connected to it.
I have to ask - why have a 20KW generator on boat that only has 50a shorepower service. Can the boats internal wiring etc even handle that 20KW.
I have to ask - why have a 20KW generator on boat that only has 50a shorepower service. Can the boats internal wiring etc even handle that 20KW.
Shore power will vary depending on where you dock, of course.
Slips for big boats may have more than 50 amp service and multiple connections.
I can see bigger boats with lots of LiPo batteries to charge using a healthy
amount of that 20kW to charge a low battery pack while running AC and laundry, etc.
I have to ask - why have a 20KW generator on boat that only has 50a shorepower service. Can the boats internal wiring etc even handle that 20KW.
Matching the breaker to max generator output is OK as long as the protected conductors are rated for that amperage load.I would want the main breaker to permit full load but most boats under 60' or so
would be hard pressed to load their generator beyond half of that 20kW capacity.
Even my TIG welder only draws about 55 amps maximum at 240V.
For a 55' to 60' boat, I think 20kw is actually pretty common. If you are at anchor and want to charge batteries, do laundry, make water, heat water, and run the oven it's pretty easy to load up a 20kw generator. In fact you can probably only do 2-3 of those things at the same time. HVAC loads alone can push the limits of a 50A 240V (12kw) shore connection.
For a 55' to 60' boat, I think 20kw is actually pretty common. If you are at anchor and want to charge batteries, do laundry, make water, heat water, and run the oven it's pretty easy to load up a 20kw generator. In fact you can probably only do 2-3 of those things at the same time. HVAC loads alone can push the limits of a 50A 240V (12kw) shore connection.