Shot in the dark – thanks in advance. I’m not a mechanic.
model 12 5 MDL3A 31150A, serial A890 200 886
Symptoms – Will not shut down: stop switch / emergency switch, remote panel. Fuel must be cut in ER.
Summary - Solenoid contact get 12v when engine is running. Zero volts when Stop switch engaged but engine continues to run. With engine off and apply 12v directly to solenoid contact I can hear the solenoid engage / disengage and feel it at the throttle lever.
Data –
Generator runs properly. Oil, temp & voltage OK. AC voltage OK in all load conditions.
With battery power to the generator 0 volts across fuel shutoff solenoid contacts [There is no backfeed to the solenoid]
With preheat on 0.13 volts across solenoid contacts.
With engine start 8.5volts across contacts which builds to 12.5v+ as engine starts
With engine Stop or Emergency Stop voltage across contacts is 0v. RPM drops. AC voltage drops to ~90v. Engine continues to run.
With engine off disconnect 12v+ lead from solenoid contact. Impose 12v+ directly to contact. Can hear solenoid engage and disengage. Does not sound like a “clunk”. Sounds more like a “chirp”. When connecting/disconnecting I can feel the throttle lever bump. Throttle lever can only be moved 1-2mm between hard stops.
Resistance measures 4ohms.
Is the solenoid bad or is the linkage jammed up…..
I’m on a mooring and do not want to take this apart without a degree of confidence I can fix it. Plus – the solenoid is $300+
model 12 5 MDL3A 31150A, serial A890 200 886
Symptoms – Will not shut down: stop switch / emergency switch, remote panel. Fuel must be cut in ER.
Summary - Solenoid contact get 12v when engine is running. Zero volts when Stop switch engaged but engine continues to run. With engine off and apply 12v directly to solenoid contact I can hear the solenoid engage / disengage and feel it at the throttle lever.
Data –
Generator runs properly. Oil, temp & voltage OK. AC voltage OK in all load conditions.
With battery power to the generator 0 volts across fuel shutoff solenoid contacts [There is no backfeed to the solenoid]
With preheat on 0.13 volts across solenoid contacts.
With engine start 8.5volts across contacts which builds to 12.5v+ as engine starts
With engine Stop or Emergency Stop voltage across contacts is 0v. RPM drops. AC voltage drops to ~90v. Engine continues to run.
With engine off disconnect 12v+ lead from solenoid contact. Impose 12v+ directly to contact. Can hear solenoid engage and disengage. Does not sound like a “clunk”. Sounds more like a “chirp”. When connecting/disconnecting I can feel the throttle lever bump. Throttle lever can only be moved 1-2mm between hard stops.
Resistance measures 4ohms.
Is the solenoid bad or is the linkage jammed up…..
I’m on a mooring and do not want to take this apart without a degree of confidence I can fix it. Plus – the solenoid is $300+