“Marine-Puck complies with ABYC Standard E11.17.3.5, Polarization Transformers, except for the enclosure being non-metallic.”
Polarization, but not isolation... That's very relevant.
Do they meet UL1561?
What standard is E509703? I'm unable to find it other than in reference to this transformer (and Carvers, which seem to have used them).
And...there is no such thing as E-11.17.3.5. Assume that's a typo as this section has nothing to do with shore power transformers. Here's E-11.18.3.5 "The secondary of the polarization transformer is grounded (polarized) on the boat (see E-11.5.3.2.2 and E-11.5.3.2.3 EXCEPTION)." If that's what they are referencing it has nothing to do with the transformer itself, it's related to installation.
Here is section E-11.17.3 in its entirety.
11.17.3 DC Grounding Bus
11.17.3.1 The DC grounding bus shall be connected directly to the engine negative terminal or the DC main negative bus.
11.17.3.2 The DC grounding bus serving more than one electrical device shall comply with E-11.17.2 for the largest device, and shall be manufactured and installed in accordance with the following:
11.17.3.2.1 If the DC grounding bus is fabricated from copper or bronze strip, it shall have a thickness not less than 1/32 in (0.8 mm) and a width of not less than 0.5 in (13 mm); and
11.17.3.2.1.1 shall be drilled and tapped providing its thickness ensures no less than three full threads of engagement for the terminal screws; or
11.17.3.2.1.2 shall be through-drilled, and the connections made with machine screws and lock nuts.
NOTE: Copper pipe may be used providing its wall thickness is sufficient for the pipe to be drilled and tapped as required above.
11.17.3.2.2 Copper braid shall not be used.
Polarization transformers are covered under E-11.18.3, see below.
These are the isolation transformer requirements from ABYC
11.7.1 Shore Power Transformers
11.7.1.1 ISOLATION TRANSFORMERS - Devices used as isolation transformers shall be either encapsulated, dry type or high frequency/switch mode.
11.7.1.1.1 Encapsulated, dry type transformers shall meet the requirements of UL 1561, Dry Type General Purpose and Power Transformer (see E-11.18, DIAGRAM 6, and DIAGRAM 7).
11.7.1.1.1.1 Encapsulated, dry type transformers shall have a metallic shield located between the primary and secondary winding and be electrically insulated from all other portions of the transformer. It shall be designed to withstand, without breakdown, a high potential test of 4000 VAC, 60 Hz, for one minute, applied between the shield and all other components such as windings, core, and outside the enclosure.
NOTE: Breakdown is considered to have occurred when the current which flows as a result of the application of the test voltage rapidly increases in an uncontrolled manner.
11.7.1.1.1.2 Encapsulated, dry type transformers shall have a separate, insulated wire lead or terminal identified as the shield connection that shall be solidly connected only to the shield, and brought out for external connection and shall be equal to or greater than the aggregate circular mil area of the largest transformer phase conductor(s).
11.7.1.1.1.3 The shield and its connection shall be of sufficient ampacity to provide a sustained fault current path for either the primary or secondary windings to ensure operation of the main shore power disconnect circuit breaker when subjected to a fault current level in accordance with TABLE 3A.
11.7.1.1.2 Isolation transformer cases shall be metallic with a grounding terminal provided.
11.7.1.1.3 Isolation transformers shall be tested and labeled by an independent laboratory.
11.7.1.1.4 High frequency/switch mode transformers shall:
11.7.1.1.4.1 meet the safety requirements of IEC/UL 62368, Audio/video, information and communication technology equipment, and
11.7.1.1.4.2 the environmental requirements of IEC 60945, Maritime Navigation and Radio Communication Equipment and Systems: Methods of Testing and Required Results.
11.7.1.2 POLARIZATION TRANSFORMERS - Devices used as a polarization transformer shall be of the encapsulated type and meet the requirements of UL 1561, Dry Type General Purpose and Power Transformers.
EXCEPTION: High-frequency switch mode isolation transformers connected as polarization transformers.
11.7.2 If installed, a galvanic isolator shall meet the requirements of ABYC A-28, Galvanic Isolators.
And requirements for polarization transformers...
11.18.3.1 Each ungrounded shore current carrying conductor is connected from the shore power inlet to the primary winding of the polarization transformer through an ELCI (see E-11.11.1) and overcurrent protection device that simultaneously opens both ungrounded current carrying shore conductors. Fuses shall not be used instead of simultaneous trip devices (see E-11.10.2.5.2).
11.18.3.2 The shore grounded (white) terminal of the shore power inlet is not connected on the boat.
11.18.3.3 The shore grounding (green) conductor is connected, without interposing switches or overcurrent protection devices (see E-11.5.3.5), from the shore power inlet to:
11.18.3.3.1 an optional galvanic isolator, and then to
11.18.3.3.2 the transformer grounded neutral secondary terminal, and
11.18.3.3.3 the transformer metal case, and
11.18.3.3.4 to all noncurrent carrying parts of the boat’s AC electrical system, including
11.18.3.3.5 the engine negative terminal or its bus.
11.18.3.4 If an optional galvanic isolator is used, the shell of a metallic shore power inlet shall be electrically insulated from the boat.
11.18.3.5 The secondary of the polarization transformer is grounded (polarized) on the boat (see E-11.5.3.2.2 and E-11.5.3.2.3 EXCEPTION).
11.18.3.6 If the boat's AC electrical system includes branch circuit breakers, the branch circuit breakers shall simultaneously open both current carrying conductors unless a polarity indicating device is provided (see E-11.10.2.3.2 EXCEPTION).
11.18.3.7 240 V branch circuit breakers shall simultaneously open all current carrying conductors (see E-11.10.2.3.3).
11.18.3.8 Polarization of conductors shall be observed in all circuits.
Again, a lot to like about the Bridgeport product, but it is not ABYC compliant, and their incorrect ABYC citation makes me a little nervous. Perhaps someone can ask them to clarify.