Jul 8, 2020 #31 O C Diver Guru Joined Dec 16, 2010 Messages 12,880 Location USA Vessel Name Slow Hand Vessel Make Cherubini Independence 45 angus99 said: The only terminations will be at the breaker, the solenoid, the winch and the DC negative bus. Click to expand... Ted
angus99 said: The only terminations will be at the breaker, the solenoid, the winch and the DC negative bus. Click to expand... Ted
Jul 8, 2020 #32 DrissZougari Senior Member Joined Mar 13, 2019 Messages 243 Location North Carolina Vessel Name BZ interlude Vessel Make MS390 I totally agree O C Diver "wire it for near the maximum capacity (100 or 130 amps) and then adjust the fuse size to match the load." Once you are setup, measure the current draw (during the lift) and add 25% to size up the fuse.
I totally agree O C Diver "wire it for near the maximum capacity (100 or 130 amps) and then adjust the fuse size to match the load." Once you are setup, measure the current draw (during the lift) and add 25% to size up the fuse.