AC Condensate Drain - Vent?

Nothing like the high-humidity early start of summer in FL to show you the flaws in your AC systems...
I found it 'raining' in the engine room the other day as the salon AC condensate drain was not doing its job, and the water was running down into the ER. I used a garden hose connected to hot water to flush the line but it was never clogged. Still was not draining the way it should, so I took a closer look at how it was routed.

PO had attached the hose to the ER ceiling for a run of about 8 feet, then down the aft bulkhead to the overboard fitting which is above the water line. A few small 'dips' in the hose plus some unnecessary unions meant that the gravity flow of water just couldn't get through the way it should. Very little slope, if any, overall for that 8 foot run. I rerouted the hose to give it some slope and remove the low spots. It's working much better. However, the drain pan does not stay as dry as I'd like nor does it stay as dry as the other systems aboard.

I am thinking about venting the condensate line to put some "air behind water" as is common in household systems. I wonder if adding a simple standpipe about 3" tall at the AC drain pan connection would help? I've never seen this on any boat we've owned but wonder why / why not...
markpj23 is offline   Reply With Quote
Old 05-24-2022, 07:51 AM   #2
Guru
 
City: Rochester, NY
Vessel Name: Hour Glass
Vessel Model: Chris Craft Catalina 381
Join Date: Aug 2019
Posts: 5,226
I found with mine the most important thing is to get some vertical drop as close to the A/C unit as possible. One of mine drops a few inches from the pan into the engine room, then even with an almost level run for a while until it drops down to a thru hull, the pan drains well. Standing water is no more than a 1/2 inch, and I think improving that would require tilting the A/C unit a bit.

What does your A/C drain to?
rslifkin is offline   Reply With Quote
Old 05-24-2022, 09:46 AM   #3
TF Site Team
 
Comodave's Avatar
 
City: Au Gres, MI
Vessel Name: Black Dog
Vessel Model: Formula 41PC
Join Date: Jul 2015
Posts: 15,794
Yes, maybe try shimming up the opposite end from the drain to give the condensate pan some help in getting the water to the drain hole. May not take a lot. Just loosen the screws on that side and slide some wood shims in to see if it helps or not.
__________________
Boat Nut:
If you are one there is no explanation necessary.
If you arenít one, there is no explanation possible.
Comodave is offline   Reply With Quote
Old 05-24-2022, 11:52 AM   #4
Senior Member
 
markpj23's Avatar
 
City: Bradenton FL
Vessel Name: Deja Blu
Vessel Model: Marine Trader 62
Join Date: Mar 2021
Posts: 158
Quote:
Originally Posted by rslifkin View Post
I found with mine the most important thing is to get some vertical drop as close to the A/C unit as possible. One of mine drops a few inches from the pan into the engine room, then even with an almost level run for a while until it drops down to a thru hull, the pan drains well. Standing water is no more than a 1/2 inch, and I think improving that would require tilting the A/C unit a bit.

What does your A/C drain to?
From the pan it drops straight down a few inches into the engine room, then goes to an overboard discharge.
markpj23 is offline   Reply With Quote
Old 05-24-2022, 11:54 AM   #5
Guru
 
City: Rochester, NY
Vessel Name: Hour Glass
Vessel Model: Chris Craft Catalina 381
Join Date: Aug 2019
Posts: 5,226
Quote:
Originally Posted by markpj23 View Post
From the pan it drops straight down a few inches into the engine room, then goes to an overboard discharge.

Sounds similar to my setup then. Does the pan have a drain on more than 1 corner? If so, you may want to connect more than 1 and tee them together. The unit won't be 100% level all the time, so it may drain better that way.



I also found that I had to work to avoid a slight rise in the hose when it left the drain pan and made the turn down through the floor. Getting rid of that slight rise made a big difference in how low the water level in the pan stayed.
rslifkin is offline   Reply With Quote
Old 05-24-2022, 11:55 AM   #6
Senior Member
 
markpj23's Avatar
 
City: Bradenton FL
Vessel Name: Deja Blu
Vessel Model: Marine Trader 62
Join Date: Mar 2021
Posts: 158
Quote:
Originally Posted by Comodave View Post
Yes, maybe try shimming up the opposite end from the drain to give the condensate pan some help in getting the water to the drain hole. May not take a lot. Just loosen the screws on that side and slide some wood shims in to see if it helps or not.
It's already shimmed up on the opposite side so the pan draining is not the issue. With the hoses disconnected in the engine room, the pan would completely dry out.
Even after fixing the slope there is apparently some resistance to gravity flow as the pan has water in it most all the time. Not overflowing, but not dry either.
I've dumped hydrogen peroxide through the system also after having done a hot water flush.
All this leads me to believe that adding a standpipe as a plumbing vent would help.
markpj23 is offline   Reply With Quote
Old 05-24-2022, 12:10 PM   #7
Senior Member
 
HTurner's Avatar
 
City: Corpus Christi
Vessel Model: Willard Vega Horizon
Join Date: May 2021
Posts: 370
Besides making sure all "runs downhill, add:


https://www.amazon.com/AC-Safe-Pan-T...s%2C608&sr=8-2


They won't unclog you line, but they will keep you line from clogging. Keep in mind that keeping you pan clean prevents Legionella...
HTurner is offline   Reply With Quote
Old 05-24-2022, 03:05 PM   #8
Guru
 
rgano's Avatar
 
City: Southport, FL near Panama City
Vessel Name: FROLIC
Vessel Model: Mainship 30 Pilot II since 2015. GB-42 1986-2015. Former Unlimited Tonnage Master
Join Date: Oct 2007
Posts: 4,321
Quote:
Originally Posted by hturner View Post
besides making sure all "runs downhill, add:


https://www.amazon.com/ac-safe-pan-t...s%2c608&sr=8-2


they won't unclog you line, but they will keep you line from clogging. Keep in mind that keeping you pan clean prevents legionella...
amen!
__________________
Rich Gano
FROLIC (2005 MainShip 30 Pilot II)
Panama City area
rgano is offline   Reply With Quote
Reply

Thread Tools Search this Thread
Search this Thread:

Advanced Search
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


» Trawler Port Captains
Port Captains are TF volunteers who can serve as local guides or assist with local arrangements and information. Search below to locate Port Captains near your destination. To learn more about this program read here: TF Port Captain Program





All times are GMT -5. The time now is 05:44 AM.


Powered by vBulletin® Version 3.8.8 Beta 4
Copyright ©2000 - 2022, vBulletin Solutions, Inc.
Search Engine Optimization by vBSEO 3.6.0
Copyright 2006 - 2012