Problems changing Kohler 13.5CCOZ output from 120 to 240

I have a Kohler 11CCFOZ/13.5CCOZ marine generator that I am struggling with changing from 120v to 240v. The reason I say 11CCFOZ/13.5CCOZ is that the generator was mis-labeled when the boat was built (according to the previous owner) - the 11CCFOZ is a 50hz unit, and the 13.5CCOZ is 60hz. At some point the unit was "converted" to 60hz since the boat has always been in the US and used on 60hz power. I mention this only in case there is some history or limitation with the 11CCFOZ, but I don't think there is.

The unit is currently producing 120v AC @ 60hz and can pump out close to 100 amps of power. It also has a three pole, with only one pole being used for the hot L1, 100 amp output breaker that looks original.

Click image for larger version

Name:	gen1.png
Views:	17
Size:	152.2 KB
ID:	127952

The specs say that this generator can output 120 or 240 volts, single phase. I'm trying to use it with a split phase set of inverters and need two different legs of 120v @ 60hz to each of them.

I have a neighbor with what appears to be the same exact generator that is already setup this way. I have confirmed the wiring on his matches the wiring I switched mine to.

Click image for larger version

Name:	gen2.jpg
Views:	18
Size:	87.8 KB
ID:	127953

From the Installation and Operations manual, this is how the voltage connections are right now to produce 120v AC (picture above).

Click image for larger version

Name:	gen3.png
Views:	17
Size:	118.1 KB
ID:	127954

I have tried wiring it up like the above diagram, also from the operations and installation manual. This should give me two separate legs of 120v, but it doesn't. Instead, I get a pulsing amount of voltage ranging from 60v-130v (or sometimes higher or lower) depending on how I adjust the voltage regulator.

I've followed the process to adjust the voltage regulator several times, and never seem to be able to stabilize the voltage on either leg. I can see the lights on the voltage regulator and on the control board pulsing as the voltage goes up and down.

Click image for larger version

Name:	IMG_6362.jpg
Views:	13
Size:	44.1 KB
ID:	127955

The unit has the Powerboost voltage regulator, board B-258296, and when I flip it back to 120v it works just fine (after a quick adjustment).

I'm trying to determine whether it is even possible to produce 240v out of this set. I would think it would be since most all generators I've ever set hands on use a similar setup where you can convert them between 50/60hz and 120/240 volts with wiring and some patience.

I'm at a loss as to why I can't do it with this model, and am beginning to think there is a board or component that limits this unit to 120v, or I am being super stupid and forgot to do something.
__________________
Steve Mitchell - Editor SeaBits.com
m/v Kaos
55 Symbol Pilothouse
stevemitchell is offline   Reply With Quote
Old 04-24-2022, 06:23 PM   #2
Guru
 
diver dave's Avatar
 
City: Palm Coast, FL
Vessel Name: Coquina
Vessel Model: Lagoon 380
Join Date: Jan 2017
Posts: 2,392
Problems changing Kohler 13.5CCOZ output from 120 to 240

I dont know that generator. Saying that, i have seen gensets with two 120V windings. In parallel, you get 120V at 2x current. In series you get 240 at 1x current rating.

The fig 5-2 schematic looks flawed to me. You would get 240 from L1 to L2, not L0 to L2.
diver dave is offline   Reply With Quote
Old 04-24-2022, 06:41 PM   #3
Guru
 
City: Rochester, NY
Vessel Name: Hour Glass
Vessel Model: Chris Craft Catalina 381
Join Date: Aug 2019
Posts: 5,367
Do you have any 240v appliances on board? If not, is there a reason you couldn't run the inputs in parallel off the single 120v feed from the gen?

On my boat, there's no 240v stuff, so the generator is wired for straight 120v and the 2 panel legs just run in parallel on generator power (in my case the inverter sub panel is only on 1 leg). Doing it that way means I can use the full output of the generator (6.5kw / 54 amps in my case) distributed however I want rather than being limited to 27 amps per leg if I wired the gen for 120/240.
rslifkin is offline   Reply With Quote
Old 04-24-2022, 06:59 PM   #4
Guru
 
stevemitchell's Avatar
 
City: Seattle
Vessel Name: Kaos
Vessel Model: Symbol 55 Pilothouse
Join Date: Sep 2018
Posts: 505
Quote:
Originally Posted by diver dave View Post
I dont know that generator. Saying that, i have seen gensets with two 120V windings. In parallel, you get 120V at 2x current. In series you get 240 at 1x current rating.

The fig 5-2 schematic looks flawed to me. You would get 240 from L1 to L2, not L0 to L2.
I believe this set has 2 windings, and they're combined right now which is why I am getting 120v. And yes, the diagram text is wrong, but the wiring isn't, well at least as far as I know

Quote:
Originally Posted by rslifkin View Post
Do you have any 240v appliances on board? If not, is there a reason you couldn't run the inputs in parallel off the single 120v feed from the gen?

On my boat, there's no 240v stuff, so the generator is wired for straight 120v and the 2 panel legs just run in parallel on generator power (in my case the inverter sub panel is only on 1 leg). Doing it that way means I can use the full output of the generator (6.5kw / 54 amps in my case) distributed however I want rather than being limited to 27 amps per leg if I wired the gen for 120/240.
I do not have 240 stuff on board now, but I may in the future.

I have the generator and inverters in parallel now, which is fine when I am charging via generator where I can get around 80-85 amps continuous across the two inverters and for various things.

At the dock is where it sucks where I have to limit the amount of power I can pull from a 50 amp, 240v, two leg connection down to just 50 amps at 120 volts. The inverters I am using (Victron Quattro) cannot be wired to have one configuration for generator, and one for AC shore power, similar to other manufacturers.

I have a large LiFePO4 battery bank, and having both inverters able to charge at full capacity while connected to shore power would be nice.

I'm less worried about balancing the legs if I were to be using 240v split phase for generator/inverter/shore as it's pretty well balanced now.
__________________
Steve Mitchell - Editor SeaBits.com
m/v Kaos
55 Symbol Pilothouse
stevemitchell is offline   Reply With Quote
Old 04-24-2022, 08:10 PM   #5
Senior Member
 
City: St. Petersburg
Join Date: Oct 2007
Posts: 333
Steve
I see two errors on Figure 5-2: as noted in Post #2 and also N and G are not bonded at the connection block as they should be.

So, two issues with the techman schematic give me pause and I would suggest the dreaded phone call to Kohler Tech Support.
__________________
Charlie Johnson
ABYC Master Technician
CharlieJ is offline   Reply With Quote
Old 04-24-2022, 08:23 PM   #6
Guru
 
twistedtree's Avatar
 
City: Walkabout Creek
Join Date: Jan 2013
Posts: 7,928
Steve, I'd suggest checking to see where the voltage regulator sense wires are connected. It may be that once re-wired for split phase, the sens wires are now picking up at the wrong points.


Since it was running in a 120V config, I expect that the regulator senses and regulates based on 120V. In a split phase configuration, it will need to sense one of the two L-N halves. Using the diagram lingo, that would be L0-L1, or Lo-L2.
__________________
MVTanglewood.com
twistedtree is offline   Reply With Quote
Old 04-24-2022, 08:34 PM   #7
Guru
 
twistedtree's Avatar
 
City: Walkabout Creek
Join Date: Jan 2013
Posts: 7,928
It's also possible that the diagram has other mistakes in it. In particular, the polarity of the two windings. Based on the 120V diagram, winding 1-2 is in phase with winding 3-4. The split phase diagram shows 1-2/3-4, but in that config I think the two windings are in phase rather than out of phase. I have a suspicion that the correct wiring should be 1-2/4-3.
__________________
MVTanglewood.com
twistedtree is offline   Reply With Quote
Old 04-27-2022, 12:31 PM   #8
Senior Member
 
tozz's Avatar
 
City: Seattle
Vessel Name: Conundrum
Vessel Model: Nordlund 63' Pilothouse
Join Date: Feb 2017
Posts: 289
Quote:
Originally Posted by stevemitchell View Post
I believe this set has 2 windings, and they're combined right now which is why I am getting 120v. And yes, the diagram text is wrong, but the wiring isn't, well at least as far as I know
Here's the diagram I have steve. See attached.
Attached Thumbnails
IMG_3779.jpg  
tozz is offline   Reply With Quote
Old 04-27-2022, 12:36 PM   #9
Guru
 
stevemitchell's Avatar
 
City: Seattle
Vessel Name: Kaos
Vessel Model: Symbol 55 Pilothouse
Join Date: Sep 2018
Posts: 505
Quote:
Originally Posted by tozz View Post
Here's the diagram I have steve. See attached.
Unless I am going crazy, that looks the same as the one I have....
__________________
Steve Mitchell - Editor SeaBits.com
m/v Kaos
55 Symbol Pilothouse
stevemitchell is offline   Reply With Quote
Old 04-27-2022, 01:56 PM   #10
Guru
 
twistedtree's Avatar
 
City: Walkabout Creek
Join Date: Jan 2013
Posts: 7,928
Quote:
Originally Posted by stevemitchell View Post
Unless I am going crazy, that looks the same as the one I have....

The text is corrected, showing L1-L2 as 240V
__________________
MVTanglewood.com
twistedtree is offline   Reply With Quote
Old 04-27-2022, 01:59 PM   #11
Guru
 
stevemitchell's Avatar
 
City: Seattle
Vessel Name: Kaos
Vessel Model: Symbol 55 Pilothouse
Join Date: Sep 2018
Posts: 505
Quote:
Originally Posted by twistedtree View Post
The text is corrected, showing L1-L2 as 240V

True. The diagram itself is the same though.

Ultimately I’ve reverted back to a single leg 120v, 100 amp setup for now. Kohler was very little help and I would rather not damage something experimenting.
__________________
Steve Mitchell - Editor SeaBits.com
m/v Kaos
55 Symbol Pilothouse
stevemitchell is offline   Reply With Quote
Old 04-27-2022, 05:15 PM   #12
TF Site Team
 
Comodave's Avatar
 
City: Au Gres, MI
Vessel Name: Black Dog
Vessel Model: Formula 41PC
Join Date: Jul 2015
Posts: 16,398
Quote:
Originally Posted by stevemitchell View Post
True. The diagram itself is the same though.

Ultimately I’ve reverted back to a single leg 120v, 100 amp setup for now. Kohler was very little help and I would rather not damage something experimenting.
Yes, you certainly don’t want to let the smoke out of it…
__________________
Boat Nut:
If you are one there is no explanation necessary.
If you aren’t one, there is no explanation possible.
Comodave is offline   Reply With Quote
Old 04-27-2022, 06:33 PM   #13
Guru
 
diver dave's Avatar
 
City: Palm Coast, FL
Vessel Name: Coquina
Vessel Model: Lagoon 380
Join Date: Jan 2017
Posts: 2,392
Yeah really. Like paralleling out of phase 120v windings
diver dave is offline   Reply With Quote
Old 04-27-2022, 09:14 PM   #14
Senior Member
 
jgtrucking's Avatar
 
City: Camden, TN
Vessel Name: Toscana
Vessel Model: Island Gypsy 44 Flushdeck
Join Date: Jul 2019
Posts: 102
Quote:
Originally Posted by stevemitchell View Post

At the dock is where it sucks where I have to limit the amount of power I can pull from a 50 amp, 240v, two leg connection down to just 50 amps at 120 volts. The inverters I am using (Victron Quattro) cannot be wired to have one configuration for generator, and one for AC shore power, similar to other manufacturers.
If you have 50A240v in AND you have only 120v loads, there is no difference. Connect L1 and L2 to your gen output. If you are using a break before you make switch to change from gen to shore power you are fine. When on gen, L1 and L2 will be in synch, but who cares. 1 inverter and some other loads wired L1, 2nd inverter and different loads wired for L2. They will all work no matter if on shore or gen.

If you rewire the gen for 240v you have to balance the loads of l1 and l2 for it to run most efficiently. If you run them together as mentioned the load will always naturally split between the winding and ballance. Until such time you need 240v for an appliance, you are better to leave it as wired and wire to the panel as described.
jgtrucking is offline   Reply With Quote
Old 05-06-2022, 12:56 PM   #15
Senior Member
 
EngNate's Avatar
 
City: Bella Bella
Vessel Name: Tenacious
Vessel Model: Uniflite 31 FB Sedan
Join Date: Feb 2019
Posts: 283
I suspect the voltage regulator sense connections are wrong for 120/240. And, is this a digital control unit? If so there is a menu setting for output configuration.
__________________
Experience develops good judgement, bad judgement develops experience
EngNate is offline   Reply With Quote
Old 05-06-2022, 02:33 PM   #16
Veteran Member
 
City: Hinckley
Vessel Name: Erie Sponsible
Vessel Model: Uniflite 42DC
Join Date: Feb 2019
Posts: 36
This is all single-phase. No chance of getting anything out of phase.
sparky66 is offline   Reply With Quote
Old 05-06-2022, 03:35 PM   #17
Guru
 
diver dave's Avatar
 
City: Palm Coast, FL
Vessel Name: Coquina
Vessel Model: Lagoon 380
Join Date: Jan 2017
Posts: 2,392
Quote:
Originally Posted by sparky66 View Post
This is all single-phase. No chance of getting anything out of phase.


Transformers and generator systems can have separate windings, where winding phasing is of extreme importance. 3 phase or single phase.
diver dave is offline   Reply With Quote
Old 05-06-2022, 03:39 PM   #18
Veteran Member
 
City: Hinckley
Vessel Name: Erie Sponsible
Vessel Model: Uniflite 42DC
Join Date: Feb 2019
Posts: 36
Quote:
Originally Posted by diver dave View Post
Transformers and generator systems can have separate windings, where winding phasing is of extreme importance. 3 phase or single phase.

I don't follow. A single-phase transformer or generator is just that.
sparky66 is offline   Reply With Quote
Old 05-06-2022, 04:04 PM   #19
Guru
 
diver dave's Avatar
 
City: Palm Coast, FL
Vessel Name: Coquina
Vessel Model: Lagoon 380
Join Date: Jan 2017
Posts: 2,392
Problems changing Kohler 13.5CCOZ output from 120 to 240

https://www.electronics-tutorials.ws...?fit=297%2C190

Shown is a single phase transformer. The dots indicate “phasing”. In this context, it means the polarity of the voltages, with a given core flux. So, all the dotted windings will have a rising voltage (positive current) at the same time.
The non-dotted windings will have a falling voltage (negative current) at that time. Of course, current only when loaded.
diver dave is offline   Reply With Quote
Old 05-06-2022, 04:36 PM   #20
Veteran Member
 
City: Hinckley
Vessel Name: Erie Sponsible
Vessel Model: Uniflite 42DC
Join Date: Feb 2019
Posts: 36
Quote:
Originally Posted by diver dave View Post
https://www.electronics-tutorials.ws/wp-content/uploads/2013/09/trans61.gif?fit=297%2C190

Shown is a single phase transformer. The dots indicate “phasing”. In this context, it means the polarity of the voltages, with a given core flux. So, all the dotted windings will have a rising voltage (positive current) at the same time.
The non-dotted windings will have a falling voltage (negative current) at that time. Of course, current only when loaded.

OK, now I know what you mean. I think that is polarity, not phasing.
sparky66 is offline   Reply With Quote
Reply

Thread Tools Search this Thread
Search this Thread:

Advanced Search
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


» Trawler Port Captains
Port Captains are TF volunteers who can serve as local guides or assist with local arrangements and information. Search below to locate Port Captains near your destination. To learn more about this program read here: TF Port Captain Program





All times are GMT -5. The time now is 03:15 AM.


Powered by vBulletin® Version 3.8.8 Beta 4
Copyright ©2000 - 2022, vBulletin Solutions, Inc.
Search Engine Optimization by vBSEO 3.6.0
Copyright 2006 - 2012