Breaker ratings, FL AMPS vs Trip AMPS

I've got a 15 AMP Breaker. Full Load (FL) is 15A as expected. The Trip AMPS is 20.25. So this breaker is not going to trip until it hits 20+ amp? My 30 amp breaker has a trip amp at 40. That's 30% over the ratings?

So if I trip a breaker then I'm more that just over the rating. What gives?

The Brockerts
The Brockerts is offline   Reply With Quote
Old 03-14-2021, 04:51 PM   #2
Guru
 
twistedtree's Avatar
 
City: Walkabout Creek
Join Date: Jan 2013
Posts: 7,577
Is this something you are testing to get those numbers?


Breaker trip points are actually pretty complicated with the trip happening after some combination of current and time. This is specified as a curve plotting the current level and time before the breaker will trip. The more over current the load is, the quicker it will trip.


Is there a particular problem you are trying to solve, or just curious about it?
__________________
MVTanglewood.com
twistedtree is online now   Reply With Quote
Old 03-14-2021, 05:04 PM   #3
Senior Member
 
City: Corpus Christi
Vessel Name: Moonstruck
Vessel Model: 1990 Californian/Carver 48 MY
Join Date: Oct 2014
Posts: 185
Just curious about it, I was making sure everything was to code, i.e. 10ga wire on 30 amp breakers, connected to device rated at 30amp. After just catching a retrofit that was fire hazard I'm checking each thing I do and just noticed those numbers.

Thanks for the explanation

The Brockerts
The Brockerts is offline   Reply With Quote
Old 03-15-2021, 06:52 AM   #4
FF
Guru
 
FF's Avatar
 
Join Date: Oct 2007
Posts: 22,553
Many AC motors will pull 2 or 3 times the running amps to start.

Its called a locker rotor start. LRS

The breakers are set to allow this short burst of high amp draw .
FF is offline   Reply With Quote
Old 03-15-2021, 08:27 AM   #5
Guru
 
diver dave's Avatar
 
City: Palm Coast, FL
Vessel Name: Coquina
Vessel Model: Lagoon 380
Join Date: Jan 2017
Posts: 2,354
look here for a typical marine rated trip curve:
Note the grey area where there is uncertainty. Also, note that wires also have a "heating curve" that is not instantaneous.
It is also possible to specify a faster breaker, for electronic device protection, for instance; vs an airconditioner compressor load, pretty much two extreme examples of starting current loads.

ps: if you are seriously designing a power system, with several breakers from source to load, consider "overload coordination". This demands that the breaker or fuse nearest the load should be the one to trip during that load's overcurrent event, and not one that is upstream. If that is not designed correctly, you will have upstream breakers trip, with resulting wider effects, usually unwanted.

https://www.bluesea.com/products/725...le_Pole_60_Amp
diver dave is online now   Reply With Quote
Reply

Thread Tools Search this Thread
Search this Thread:

Advanced Search
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


» Trawler Port Captains
Port Captains are TF volunteers who can serve as local guides or assist with local arrangements and information. Search below to locate Port Captains near your destination. To learn more about this program read here: TF Port Captain Program





All times are GMT -5. The time now is 06:35 PM.


Powered by vBulletin® Version 3.8.8 Beta 4
Copyright ©2000 - 2022, vBulletin Solutions, Inc.
Search Engine Optimization by vBSEO 3.6.0
Copyright 2006 - 2012