Can you run through the recovery and repair of a single cell in a purpose built pack with single integrated BMS? Maybe also what a cell failure looks like in practice? Also, can you point to an example of a battery system that you are likely thinking of to contrast? Maybe even a picture. I am sure you have made a post before. Maybe just point me in the right direction so I can take a gander. Much appreciated.
I get the feeling we are still adding ALL the details in a pro/con list still. I think that list is incomplete as of yet. I also get the feeling there will be more than one way to do these things in a perfectly acceptable manner. But IMo we still need to add details to the discussion.
I think the most likely unexpected shutdown cause for a BMS is a cell that is out of balance WRT to other cells. The battery voltage will look fine and charging or discharging will be underway, currents are comfortably in range, but the BMS disconnects because that one cell is too high or too low. This WILL eventually happen if 1) there is no balancer, 2) the balancer is inadequate as they appear to be in some drop-ins, or 3) the battery isn't charged in such a way that allows the balancer to run enough. Also note that even with balanced cells, an improperly controlled charger that tries to overcharge the batteries will likely trigger a BMS disconnect. But I would consider that a fault condition, not an operational disconnect.
The next most likely, I believe, is an over-current disconnect, and this is much more likely with a FET-based (solid state vs contactor) BMS disconnect switch. FET disconnects are more limited in current capacity than a contactor, and cheaper FET disconnects have lower capacity. That's why you see some 100Ah batteries with a 50A rating and others with a 100A rating. FET switches are also subject to getting fried by large current surges (thrusters, engine starters, windlasses) that smoke the FETs before the BMS can disconnect. If over-currents like these occur, it's really because of a poorly designed/sized system. This is why most FET-based batteries prohibit use with such high surge current devices.
Next would be high or low temp disconnects. This obviously relates to ambient temp, but high charge and discharge currents will drive up cell temps.
These are the operational causes of disconnects, and should NEVER happen in a properly working system.
As for diagnostics and repair of a failed cell, I'm not aware of any manufacturer that allows field replacement of a cell. Their BMS can typically show a failed cell, but field replacement is of the whole battery, not the cell. The only situation where a cell would be replaced would be with a discrete system. At this point I don't think very many people are going that route anymore, but some still do, and quality battery systems can be built up this way. I built my home battery system this way and it is running great, now 4 years in. Cell replacement would depend greatly on the physical build, but presumably would be possible.
There are a few examples of what I would consider to be full-function battery systems, and I'll describe the one I have on my boat. It's built by MG Energy, and consisted of batteries with built-in cell sensing and balancing, coupled with an external BMS and contactor. Cat5 cables connect the batteries and BMS for communications and control, and the battery DC cables connect back to the BMS where they share a single contactor. The BMS is rated for 1000A.
The BMS provides two key signals, ATC and ATD which are used to enable/disable chargers and loads. All my chargers are programmed to charge within the allowed ranges for the batteries, so ATC always says charging is allowed. That said, ATC is wired to my shore chargers, inverters, and alternators and will turn them off if for any reason ATC shuts off. Referring to the above discussion, if cells have become imbalanced, battery bank voltage can appear OK and chargers will keep running, even though a single cell is heading out of range. This is where ATC shuts off charging, and averts what would otherwise be a BMS shutdown and potential alternator surge event.
ATC also protects against over temp and other events that are otherwise undetectable by chargers, and would lead to a BMS disconnect.
ATD controls the inverters and will shut them down if batteries become critically low. But my other DC loads will not shut off. I use ATD as an alarm, but specifically do not want other loads to shut down. I would rather have power as long as possible to give time to get an alternate power source going, etc. I also have generator autostart that kicks in well before ATD triggers.
As a result of all this, if a BMS disconnect happens, something is pretty broken, either on the charging side, or in the BMS itself or a cell.