Last weekend I went to the boat with the proper equipment to repair a small leak on our front unit, a Marine Air 16000 btu VR16KH. After repairing the leak and pulling a vacuum for an hour it was time to recharge. A friend of mine is very good at this and coaches me via text messages and iPhone pics
. When I appeared to be finished I used two quality analog matching probe thermometers. One in the return air register and one in the closest supply register per his directions. After running overnight I was showing a 20 degree TD (temperature differential). Wow! Awsome! Let me mention that by the time I checked that morning it was about 11:00 and the heat index in Biloxi was 111 degrees outside.
Chuck said I needed to be sure I was not overcharged(280 psi HP)- as this could cause damage to the compressor over time. The data plate showed a value of 12 amps FLA (full load amps) on cool or heat. I put my clamp on amp meter over one leg and showed 13.6 amps. Too high! He had me check the blower amps (3) and then check all 3 wires at the compressor. 1 orange, 1 white and one black. I pulled the schematic out and saw the black wire came from the over heat switch. It had about 10.5 amps.
I ended up removing a small amount of freon and watched the FLA drop immediately. I ended up at about 11.8 FLA. Checked my TD and I was down to about 11 degrees. HUGE difference! I slowly added freon in stages and finally settled on 12.15 FLA which gave me a 14 degree TD. High pressure was around 245.
I was amazed at how close the line is between great cooling/ too many amps and decent cooling/ normal operating amps. I would encourage anyone charging their own system to get a clamp on amp meter and use this along with your gauges for proper settings.
Chuck said I needed to be sure I was not overcharged(280 psi HP)- as this could cause damage to the compressor over time. The data plate showed a value of 12 amps FLA (full load amps) on cool or heat. I put my clamp on amp meter over one leg and showed 13.6 amps. Too high! He had me check the blower amps (3) and then check all 3 wires at the compressor. 1 orange, 1 white and one black. I pulled the schematic out and saw the black wire came from the over heat switch. It had about 10.5 amps.
I ended up removing a small amount of freon and watched the FLA drop immediately. I ended up at about 11.8 FLA. Checked my TD and I was down to about 11 degrees. HUGE difference! I slowly added freon in stages and finally settled on 12.15 FLA which gave me a 14 degree TD. High pressure was around 245.
I was amazed at how close the line is between great cooling/ too many amps and decent cooling/ normal operating amps. I would encourage anyone charging their own system to get a clamp on amp meter and use this along with your gauges for proper settings.