1.7.6
Installation
Cylinder And Connected Devices - Location and
1.7.6.1 LPG cylinders, cylinder valves, regulating
equipment, and safety devices shall be readily accessible,
secured for sea conditions, and protected from the weather
and against mechanical damage, and shall b e
1.7.6.1.1 installed in a ventilated location on the exterior
of the boat where escaping gases will flow directly
overboard, or,
1.7.6.1.2 if the escaping vapors will not flow directly
overboard, the cylinder shall be installed in a dedicated
locker meeting the requirements o f A-1.8.
1.8 LPG LOCKERS
1.8.1 Lockers used to contain LPG cylinders, cylinder
valves, regulating equipment and safety devices shall b e
designed to minimize the likelihood of use as a gear
storage locker and shall be,
→ 1.8.1.1
vapor tight to the hull interior, and
1.8.1.2
located above the waterline, and
1.8.1.3 constructed of, o r lined with, corrosion resistant
materials, and
1.8.1.4 shall open only from the top with
→ 1.8.1.5 a gasketed cover that shall latch tightly, and
1.8.1.6 shall be capable of being quickly and
conveniently opened without tools.
A-1
7/00
1.8.2 Installation:
> 1.8.2.1 LPG lockers shall b e installed so that the locker
opens only directly to the outside atmosphere, and
> 1.8.2.2 If a LPG locker i s installed inside a boat locker,
the LPG locker shall be located as high and as close to the
boat locker's opening a s possible in order to comply with
A-1.8.2.1.
When means of access to the LPG equipment
locker or housing is open, the cylinder valves shall be
capable of being conveniently and quickly operated, and
the system pressure gauge dials shall be fully visible.
Lockers shall be vented at the bottom by a
dedicated vent, with a minimum diameter of
component in the vent system that shall be not less than 1/2
inch (12.5 mm) inside diameter.
Locker vents shall be led outboard, without
pockets, through the hull t o a point lower than the locker
bottom and above the waterline with the boat i n the static
floating position.
1.8.6 Locker vent openings shall b e located at least 20
inches (508 mm) from any hull opening to the boat
interior.
1.8.7 LPG lockers shall not be used for storage of any
equipment other than LPG cylinders, cylinder valves,
regulating equipment, and LPG safety devices. See A-
1.8.1.
1.8.8 Storage provisions for unconnected reserve
cylinders, filled or empty, shall be the same as for the
cylinder in use.