I saw this effect with 3 LiTime batteries in parallel. However it seemed to be self correcting a short time after the batteries started discharging. When the charging source was removed one or two of the bank would start discharging and within 30 minutes the third would be discharging. Within a few hours the SOC on all three would be within a couple % of each other. Once I configured the charging sources to keep the bank out of FCP, I never saw this behavior again.
LiTime doesn’t think this is a problem. Their DC-DC chargers would always push the battery into FCP. Pushing it into FCP wasn’t a problem since once the charging source was removed a single battery would always assume the load. The problem was a parallel bank where they wouldn’t all come on line at the same time to assume the load.
Tom
LiTime doesn’t think this is a problem. Their DC-DC chargers would always push the battery into FCP. Pushing it into FCP wasn’t a problem since once the charging source was removed a single battery would always assume the load. The problem was a parallel bank where they wouldn’t all come on line at the same time to assume the load.