twistedtree
Guru
BTW, you can send in formal "Requests for Interpretation" (RFI) and ABYC will respond. It may take a while, but it will happen.11.10.1.2 tells us that OCP's are to be "readily accessible." We also know from info. upthread what the definition is for "readily accessible."
Then the Exceptions come into play and this list of things only need to be "accessible." I have no idea if the text of E-11 further defines "accessible" so let's just use the definition in Websters, which is: capable of being reached, used, or understood; available; or easy to approach.
That seems like a rather insignificant change in the actual text and in the meaning of that text that I would think a lot of people simply won't recognize. Specifications or Standards reading is never easy and you really need the entire text.
Regardless, of the Exceptions, Note 3. seems to apply to fuse holders and fuses as I would think in order to comply to E-11.5. a guard on the fuse holder would be required.
If I have this right, the guard requirement of E-11.5. results in the requirement to remove a fuse assembly from the "readily accessible" group and the Exception clause places it in the slightly different "accessible" group.
Unless it's noted elsewhere this "accessible group" is not required to be capable of being reached quickly & safely for effective use in emergency conditions without the use of tools, like the "readily accessible" group.
That being the case, a Class T fuse inside a battery (isn't that an electrical device?) may well comply with ABYC.
I believe the exception about fuses that are internal to electrical device is intended to cover internal fuses commonly found in inverters, autopilots, etc. But you would need to send in an RFI to get ABYC's take on it.