I’ve read most of the threads on LFP battery upgrades and now that I have decided on my battery selection, I am still a little confused on fusing options, between MRBF and class T. I will have 3 LiTime 230AH batteries in a single bank (they all fit in my starboard battery box) connected to a 600A busbar then going to the battery switch. Since my inverter is a Multiplus 12/3000, the maximum possible current draw is between 250-300A. So if we say house draw should not exceed the 50 amp panel breaker, then the max current should be less than 350 amps. The only exception to that is where the start battery bank needs help and the emergency parallel solenoid is engaged. At that point the upper limit would be driven by the BMS at 200A and the three in parallel at 600A coming from the bus. Options:
1. Class T 300A on each battery and nothing on the bus bar. (Allows most amps for emergency start)
2. 250A MRBF on each battery and 400A class T on bus bar.
3. 250A Class T on each battery and 400A MRBF on bus bar.
4. TBD
Tom
1. Class T 300A on each battery and nothing on the bus bar. (Allows most amps for emergency start)
2. 250A MRBF on each battery and 400A class T on bus bar.
3. 250A Class T on each battery and 400A MRBF on bus bar.
4. TBD
Tom