All room thermostats related to the Kabola system stopped triggering the fans at the heat exchanger. The kabola works fine, heats water as normal, the cooling lines are boiling hot at the heat exchangers but the fans are not being tuned on. I tried setting the thermostat 4, 7, 10, 12 degrees above ambient.. I hear the thermostat click as if it is starting a heating cycle but the fans do not activate.
I checked all fuses inside the kabola box, I switched thermostats between rooms, I applied external power to the fans and they run fine.. the only things I noticed is this.. when I remove the front of the thermostat, the voltage in the wires going into it is negative (-12V for example).. since its the same scenario at all thermostats I am thinking that it’s normal?
I would very much appreciate any and all input and suggestions.
Streff
I checked all fuses inside the kabola box, I switched thermostats between rooms, I applied external power to the fans and they run fine.. the only things I noticed is this.. when I remove the front of the thermostat, the voltage in the wires going into it is negative (-12V for example).. since its the same scenario at all thermostats I am thinking that it’s normal?