.... I realized my 4 455 watt panels- 2 pairs in parallel ) were 48 volts. I already had them wired to two 100/30 mppt controllers. If they were 100/50, it would have worked.
Okay so I'm just thinking out loud about stuff you already know now.
You (originally) had two 900-watt "banks" of parallel wired panels at 48 volts. And each bank was slotted to be used with a 100/30 controller. The "100" stands for volts, so you were fine there with 48 volts, even in very cold weather when the voltage can go up a bit.
The 30 is amps. Your 900 watts would be around 54 amps into a 12-volt system. However if they are mounted flat (not constantly tilted and angled to the sun position), then I'd guess around 36-40 amps. I would also have gone to a pair of 100/50 with keeping two banks of panels in that case. Although in the back of my mind (meaning I think I used to know but have forgotten, heh), some of the larger controllers have some nicer features, so unless shading is a factor I might have gone with one larger controller (but kept the series parallel as I don't have any great urge to go above 48 volts). But I don't even know if the rest of your system could have taken advantage of those extra features (thinking they come into play once you have a Cerbo etc.).
One additional note (perhaps AI already mentioned this) is to look at any of your breakers/switches or what have you that are in the line before (on the sky side) of your controller, to be sure they can handle the highest voltage you could expect. Note that in cold weather the voltage will go up higher than even the rated Open Circuit voltage. I would have run a calculation for yours but I don't know all your specs. This one is decent though:
MidNite Solar is the industry leader and manufacture of quality Renewable Energy System electrical components and E-Panels.
www.midnitesolar.com
Or if you want to post your panel specs, I could run the calc. Or maybe AI already did this for you.
Example:
My two 100 watt panels wired in series only have a VMP voltage of 17.6, so that's 35.2 volts added together. Open Circuit voltage is 21.6 (so 43.2v added together). However at 0ºF the voltage could reach 49.2 volts (VMP could reach 41.8 volts) so I have to take that into account. (You can choose your theoretical lowest temperature in the calculator.)
They tend to reach the highest voltage first thing in the morning. When it's quite cold but the sun is just coming up.
**********
Just as a separate note of interest, right now (RV) I have 200 watts of panels (two 100 watt in series) on my roof, mounted flat. Then I have another 200 watts of panels (same specs) but sitting on the ground where they are tilted to the sun (and it's winter, so that matters more). I'd say on average the flat panels only give about 1/2 of the tilted ones at most (varies of course). It's kind of fun that the two panel banks are the same (and I have each on its own controller) so I can compare at any given moment to see how much the flat panels and the tilted panels differ. For example today (sunny) the flat bank provided 110wh by the time the battery bank was full. The tilted-to-the-sun bank provided 220wh. They are coordinated in a Victron Smart Network so both worked together. This shows how if a panel array is always going to be flat, they will produce much more in July than in winter.