Anyone update old generator with new mounts and exhaust?

The friendliest place on the web for anyone who enjoys boating.
If you have answers, please help by responding to the unanswered posts.

Steve91T

Guru
Joined
Sep 12, 2016
Messages
898
Location
USA
Vessel Name
Abeona
Vessel Make
Marine Trader 47’ Sundeck
Hey guys. Boating in the south east with small kids means we literally run the generator when we leave the dock and don’t shut it down until we get back to dock usually a few days later. When we anchor we are usually the only ones around so the noise of the generator isn’t an issue, but I feel bad for the times there is someone else around.

The generator is an old 8kw Westerbeke with 5600 hours on her. I know that’s a lot but she really runs great. It’s noisy though. And there’s quite a bit of vibration. I own an old 5.9 Cummins in my truck and when I got it the motor mounts were shot. The vibration was unreal. New mounts fixed it and it’s smooth as can be (for an old diesel).

The other thing is the exhaust. While the exhaust noise itself isn’t bad, it’s way louder than our mains, which are nearly silent. The water splashing is almost as bad as the exhaust noise itself.

A new generator is out if the question right now. But I figure mounts will be cheap and relatively easy. Not sure about the exhaust. I’ll save an underwater exhausts for the new generator.

So what have you guys done to lesson the vibration and noise?

Thanks
Steve
 
Onan MDJE

I think the major source of noise from my generator comes from the intake. The exhaust is relatively quiet.
 
You can get Centek Vernalift muffler and GenSep systems that help a whole lot. Intake sound suppressors are available too. 5600 hours on a genset is nothing as long as basic maintenance is adhered to.
 
sound suppression on gensets

I just finished supressing some of the sound on my genset.

I have a Northern Lights 5kw with a sound enclosure in my lazertte.

I had structural vibration noise so what I did was I increased the size of the plywood generator shelf to 3/4" plywood and installed rubber sound mounts between the generator base (a 3/8" plywood board) and the newly installed 3/4" plywood shelf which is installed on a frame within the lazertte. The frame itself rests on 1" rubber belting, cut from a conveyor belt.

I found noticible sound relief.

The only thing left to do now is to install an exhaust/water seperator at the exhaust exit. I saw one video of a guy who put an extra exhaust inboard and inline of the exsisting whater muffler.

Question to Duvie. What do you mean by sound on the intake? Do you mean air through the filter or intake to the cylinders?
 
Most bigger marine diesels have air silencers on the intake in place of a air filter. On the ocean you don't run into dust and an air filter can restrict the air flow too much.
 
I would change out the mounts, Soundown sell some that are supposed to help with noise. Then I would increase the thickness of the deck where the genset is mounted and if you can get to the underside add a stiffener to the bottom, like a 2x4 glued and screwed to the underside of the mounting platform. Make the platform as solid as possible. Like was suggested above, it will help with the vibration and noise.
 
You can make an intake silencer out of a rubber tube/hose attached to the intake. Route this hose to chamber hopefully cylindrical to reduce “oil canning”.

Re vibration mount generators to very substantial surfaces stiff enough and heavy enough that it won’t become a sounding board.
 
Thanks for the advice! I had no idea that a sturdy base would have anything to do with it. Makes sense though. I was thinking about starting with ripping the old insulation out and replacing it with dynamat. I think a water separator will make a big difference. That’s down the road.

A 2nd in-line muffler would probably really help.

I’ll look into the induction noise also. It is pretty loud.

Thanks guys!
 
Yes, a sturdy base will definitely help. I made one out of 2 layers of 3/4” plywood that I laminated together with epoxy and screws. Then I added a stiffener to the bottom. Whatever you do make sure it is solid.
 
New mounts are a comparatively cheap and simple way to take out heaps of vibration from an older genset.

Hamish.
 
I have a 3 year old 5.5 Westerbeke in an enclosure, on a platform 1 1/2" thick. The platform is mounted solidly on top of 2 stringers. The generator is directly below the salon. Very little vibration.

The exhaust consists of a Vetus Dual Stage Waterlock Muffler and a Centek GenSep water separater with the recommended hose loop. It is very quiet.

Other boaters think that an AC or frig is running instead of a generator. We can run it for hours without irritating anybody.

The GenSep is highly recommended.
 
Some excellent advice above. From the bottom up:
A stiff structure to support the generator allows the isolation mounts to do a better job. The shelf itself and the supporting structure, sometimes braces and gussets depending on the installation.

What grahamdouglass described "installed rubber sound mounts between the generator base (a 3/8" plywood board) and the newly installed 3/4" plywood shelf" is called secondary isolation. This is not replacing existing mounts, but adding a second set between the frame of the generator and the shelf. This can often make a big difference. For a 500lb 8Kw unit these should not cost more than $50 each. Replacing the OEM mounts if over 10 years old is a good idea as well.

Enclosure insulation: Dynamat is a sheet metal damping product. Most small generators use 1" acoustic foam for insulation. A better upgrade than Dynamat would be 1" 1lb vinyl / foam insulation. The addition of the 1lb barrier increases the performance over the OEM acoustic foam. Make sure the air intake baffle on the enclosure is intact and lined w insulation.

A Centek Gen Sep in 2" from several sources is less than $300. You should only need a short piece of new hose to make the connection from your existing lift to the Gen Sep, and your existing to the hull run of hose should reach the Gen Sep. The hard part will be finding a way to discharge the water (1.5") below the waterline. Until your next haul out maybe you can find a thru hull to use, even an above the waterline thru hull which will still be quieter than the gas and water exiting together as they do now.

The air intake noise described above is particular to natural aspirated diesels, this is not a turbo diesel issue because the intake circuit is closed on a turbo diesel. An AirSep like Walker offers as well as others, work well to reduce this intake stroke noise which is low frequency and difficult to reduce once airborne. The hose technique Willy mentions makes the noise travel further and make several degrees of turns which reduces that noise.

$0.02 :socool:
 
Donaldson makes a nice air filter/silencer for things like skid-steers and small tractors with similar sized diesels. Does a good job of getting rid of intake noise, which on a 3 and 4cyl can be a lot of the noise. Can be mounted remotely and plumbed with tubing and hose sleeves.

Look also at your water lift muffler. Little ones don't do as good a job as bigger ones. If using a little one, see if you can fit in a bigger one. Wont help much with the splashing. but you are not at that point yet as you told.

If mounts are degraded, fresh rubber can really help too.
 
All things have natural resonances including vibration isolators. Also isolators are designed for both vertical and horizontal loads. Lower frequencies generated with single cylinder engines usually present the greatest difficulty to isolate. I suggest that before you rush out and purchase new isolators that you get product specifications showing frequencies vs attenuation and loads, both vertical and horizontal from the isolator manufacturers and determine which can provide the best solution for you.

I am critical of isolators that allow height adjustments on a threaded shaft especially for horizontal forces. A better way to correct for height adjustments is to shim under the isolator.
 
Last edited:
I have a 8.0 Westerbeke as well and HATE the noise.

I put a second, inline centek muffler onto it along with upsizing the centek lift muffler. It make a world of difference.
 
The newer sound enclosure are well designed to contain noise. They muffle the noise with baffled apertures and tightly gasketed openings.

Sound enclosures are no longer a simple box around a generator. The new ones are engineered to isolate vibration and contain noise effectively.

Add effective water lift mufflers and Gen Seps and the generator will be really quiet. The biggest noise reduction is from the lack of exhaust water noise with the GenSep. The dual chamber Vetus water lift muffler also reduces the exhaust noise significantly without increasing back pressure.
 
For max quiet a more complex system is required.

The unit is mounted on a frame with soft mounts , then the frame itself is mounted on soft mounts .

Works both for an engine and the noisemaker , but the hookups must be very compliant to handle the motion, and not pass on sound.

Usually too much expense except for Gov .
 
Thanks guys. I think my plan of attack is going to be to take care of the vibration first since that’s the biggest problem and the cheapest and easiest. So how are you guys lifting the genset high enough to redo the shelf?
 
A wet muffler and sound shied sounds like good advice. I have an Onan 8K in my cockpit. My A/C makes more noise than the genny.
 
Thanks guys. I think my plan of attack is going to be to take care of the vibration first since that’s the biggest problem and the cheapest and easiest. So how are you guys lifting the genset high enough to redo the shelf?

With an electric winch hung from a 4" X 4" straddling two sawhorses.
 

Attachments

  • 0000173_warn-industries-885000-winch.jpg
    0000173_warn-industries-885000-winch.jpg
    57.9 KB · Views: 43
Pry bars and blocks of wood work.
 
It isn’t too bad to lift because it is probably around 300 pounds or so. Can you get access above it? If so the sawhorses and 4x4 would work with a come along. Maybe post some photos of it in place and a general photo of the area.
 
Weight from Westerbeke for the current 8kw model says 450lb. Any combination of comealong/bottlejacks/muscle maybe a skid and slide it out of the way?
A comealong or winch like you show take up a lot of space between the 4 x 4 and the generator, you may need a combination of lift and jack

If you are going to work under a slung generator be sure and secure it real careful. I would try and block it rather than hang it once you get it up

:socool:
 
Weight from Westerbeke for the current 8kw model says 450lb. Any combination of comealong/bottlejacks/muscle maybe a skid and slide it out of the way?
A comealong or winch like you show take up a lot of space between the 4 x 4 and the generator, you may need a combination of lift and jack

If you are going to work under a slung generator be sure and secure it real careful. I would try and block it rather than hang it once you get it up

:socool:

I actually use a snatch block hung from the 2 X 4 and mount the winch on the beam away from the work area to gain more lift.
 
Alight spent some time a few days ago running new ac water lines and I was near the generator exhaust and had time to really look at it. Good thing is I have tons of space to get to and upgrade.

Here are two videos of the generator running, one from the engine room, the other from outside.

I definitely want to do something with the exhaust. I’m thinking a larger lift muffler might do the trick. Or the water separator if I can find a through hull. One question about that though. Once separated, does the water flow smoothly and no more splashing? The splashing along with the exhaust noise is really loud and annoying.

https://youtu.be/07_-ONPmOLo

https://youtu.be/qlbVYvv_SDA
 

Attachments

  • 48B5BBF0-8433-4B7C-977E-29B32DC0067A.jpg
    48B5BBF0-8433-4B7C-977E-29B32DC0067A.jpg
    130.1 KB · Views: 45
Hey can I add a 2nd lift muffler? That’s an empty tool box next to the muffler. There’s room for 2nd muffler. I could have a 90 degree outlet from the first muffler into a top in/top out muffler.

Or is that too much back pressure?
 
I think you will need to get the allowed back pressure specs for the generator, then talk to a muffler supplier to spec out something. Both the muffler and separator will contribute to back pressure.



And yes, the whole point of the separator is to get rid of the splashing water. The water discharges below the waterline, so completely silent. And the exhaust gas discharges above, presumably through your existing outlet. But you would need to add a water outlet, so it's a haul-out project.


On my last boat the exhaust at the side of the boat sounded like a dryer vent, so nice and quiet.
 
Even if you discharge the separated water above the waterline it should come out in a more steady stream with the separator compared to coming right off the lift muffler.
 
Even if you discharge the separated water above the waterline it should come out in a more steady stream with the separator compared to coming right off the lift muffler.

I was thinking I could find an unused through hull that’s above the water line but I think they are all used. Any idea how large of a through hull is required? For example if I find one for a Bildge pump that is no longer there, will that work?

Also, I’d imagine the water separator will act like a muffler as well...at least a little but.

I’m trying to decide what to do. I could easily add a 2nd lift muffler. Don’t want to throw away a perfectly good muffler If I don’t have to.

And/Or, I could add the water separator. I have 3 Bildge pump switches bit I believe I only have two pumps. So I believe I have an unused above water exit. Maybe I could discharge the water from the separator out that one. Shouldn’t be much of a run.

What would you guys do?
 
I was thinking I could find an unused through hull that’s above the water line but I think they are all used. Any idea how large of a through hull is required? For example if I find one for a Bildge pump that is no longer there, will that work?

Also, I’d imagine the water separator will act like a muffler as well...at least a little but.

I’m trying to decide what to do. I could easily add a 2nd lift muffler. Don’t want to throw away a perfectly good muffler If I don’t have to.

And/Or, I could add the water separator. I have 3 Bildge pump switches bit I believe I only have two pumps. So I believe I have an unused above water exit. Maybe I could discharge the water from the separator out that one. Shouldn’t be much of a run.

What would you guys do?

I'd do a maintenance haul to install the thru-hull for the Gen Sep. Some yards will lift the boat before lunch time and leave it on the travel lift so you can change zinks or do a quick project. Have the thru hull trimmed and ready to install with the seacock before the lift to save time if you know the thickness of your hull. Or a dry grid if you have access to one. I installed my thru-hull on a dry grid.

The Gen Sep if installed correctly with the recommended hose loop will quiet your exhaust significantly. The water exits underwater so no splashing noise and as someone described, the dry exhaust exiting above the water sounds like a drier vent.

I adjust the water flow with the seacock and can fine tune for quieter operation. The hose loop recommended on the Gen Sep installation instructions should be installed for maximum noise attenuation.

With the new style sound shield on our 5.5 Westerbeke, it is so quiet that we sometimes forget it is running and don't to turn it off when no longer needed.

The size of the thru hull will be dictated by the hose connections on the Gen Sep. It should be equal to the diameter of the thru-hull for the generators raw water intake.
 
Last edited:
Back