Quote:
Originally Posted by Cigatoo View Post
Started wiggling things and found something that looks like Sa fuse holder on the back of one of the terminals where the thermostat connects to the compressor unit. Not sure what it is yet. Hard to see. When I wiggled it compressor started and has run correctly since.

A loose connection in the thermostat circuit - as well as a thermostat that's chattering can easily create problems. It causes the compressor to start/stop/start, and that will cause it to lock out on a high starting current fault. The module will lock out for a time, and the diagnostic LED will flash 3X....3X....3X... during that period. It will self-reset and try again. It will also tell you if there's a problem with voltage, among other things. The LED will tell the tale, and is the 1st step in DX any problem with the Danfos/SECOP module, as noted in post #7. Without it, you're guessing. You can post symptoms to the forum, then you get six guys all guessing.



Here's a good explanation of the LED use by Coastal Climate Control. They will sell you the LED, you can make one up with a loose LED and resistor if you've got the materials on hand. Start with that and find the problem.