Northern Light genset tripping internal fuse

The friendliest place on the web for anyone who enjoys boating.
If you have answers, please help by responding to the unanswered posts.

Searios

Senior Member
Joined
Nov 11, 2012
Messages
247
Location
Hong Kong
I have a NL M843 NW3 - it has shut down twice after being operated for some hours - all engine parameters are normal so it appears to be a hot generator head - although I can't find anything describing this in the generator head manual...

The symptons are: normal engine data, temperature is OK, water flow, oil pressure etc....then it suddenly looses RPM, then shuts down. The fuse on the generator head has popped out, and the way to get it started again is to reset the internal breakers and then reset the fuse....

So - I assume its the generator head that either overheats or overloads although there is no indication of either - except for the fact that it only happens after several hours of use at about 60-70% load.

Any idea?
 
That's another option, but it only happens when the genset has been running for some hours - not when its cold...
 
Also, it requires some time to cool down after the fuse reset before being able to start again...
 
Has this always happened with the same load, same time, same ambient conditions. If so then maybe your installation doesn't have enough air flow cooling, and the engine room gets too hot for it.

If it is in an enclosure, open it up, and point a small fan at the generator end and run and see what happens. If not in an enclosure do the same. If you can easily open up the engine room (not if access is from the cabin sole obviously) then do that as well.

David
 
You state that both internal breakers trip, and an external fuse...both needing to be reset. Did you really mean external "fuse" that needs resetting? Or is it another breaker?

Can you post pics or describe where they are, what they look like, and their rstinhs?
 
Could be a variety of breakers/fuses on this thing based on age and options:

DC control breaker
Exciter field breaker/fuse
Main output breaker
Maybe something else??

Figure out what is tripping/blowing.

There is no temperature sensor in gen end that causes a trip.

Note that DC control breaker has a thermal element in it, and if ambient temp gets real high (hot engine room), it can trip even if amps are lower than trip point.

Also, I have replaced several DC control breakers on NL units. Seems the vibes wear them out.

This does not really fit your scenario as a trip on the DC control breaker will cause an instant shutdown, not a loss of rpm THEN a trip.

And a loss of rpm due to fuel or overload will not cause DC control breaker amps to go high resulting in a trip.

An overload will cause rpms to drop, tripping either exciter field breaker or output breaker, but once that happens, engine will continue running. Unless they have changed the control logic since I last troubleshot one of these.
 
I had a voltage regulator go out I put an blower to push more air into the gen to cool the regulator and the gen
 
You state that both internal breakers trip, and an external fuse...both needing to be reset. Did you really mean external "fuse" that needs resetting? Or is it another breaker?

Can you post pics or describe where they are, what they look like, and their rstinhs?

The fuse blows, and can only be reset once I have turned the 2 breakers off then on again.

The fuse and the breakers are on the generator head control box inside the sound enclosure.

About the RPM drop....it happened really quickly so maybe theres just an instant shutdown.

The genset is 130 hours old...so age should't be the issue
 
As the end bearing old, the sealed in grease goes away. The bearing gets hot, transfers heat to the generator and would trip any thermal safety. End bearings in most generators I have used are supposed to be replaced about every 5 years regardless of hours.
ditto on high engine room temps.
 
The fuse blows, and can only be reset once I have turned the 2 breakers off then on again.

The fuse and the breakers are on the generator head control box inside the sound enclosure.

About the RPM drop....it happened really quickly so maybe theres just an instant shutdown.

The genset is 130 hours old...so age should't be the issue

never heard of a fuse being able to be reset, only breakers....

are the other w breakers A/C?
 