I absolutely would not recommend trying to get 240 from this setup over any length of time. There's no guarantee that someone swapping a breaker or other wiring change won't put them back on the same leg
Unless I am reading something wrong with all the non-standard marina outlets.....that's how every 125/250 pedestal is that I know of....some marinas are screwed up and have every other pedestal wired for out of phase...but worrying about it changing without notice seems a bit over the top.

And you really aren't looking for 240, just 2 legs of 110 out of phase so your smart Y will work.

The boat only needs 110, but the Y assumes you might need 250.
 
Right. And if you measure 208V then you have picked up two legs of a three phase system.

I don't know if a reverse-Y will activate if you have 2 legs of a three phase system as opposed to the two legs of a split phase system.

Anyone know?


I don't know.. but the instructions for our reverse-Y (Marinco product) says we need 208V minimum.

-Chris
 
Mine came with 2 30 amp receptacles. Was tripping breaker when running all 4 A/C units so dealer converted to 1 50 amp receptacle.

I use this "Smart Y" to connect to the 2 30 amps on the shore power pedestal. I do take all of it with me when traveling.

By the way, the dealer put in a CATV connection in place of the abandoned 30 amp receptacle.
 

Attachments

  • IMG_7911.jpg
    IMG_7911.jpg
    106.5 KB · Views: 92
  • IMG_7908.jpg
    IMG_7908.jpg
    85.4 KB · Views: 109
Looking at a a new-ish (two year old boat) that has a 50 amp connection. My dock only has 30 amp connections available. I am more confused after reading this thread but am guessing I can just get a 30 amp to 50 amp adapter and just need to manage my load to keep the boat draw under 30 amps as to not trip any breakers? Where does 125 v 250 come into play if at all? I think all appliances on the boat are 110v. If I happen to get access to a second 30 amp at my dock or when traveling, can I use any Y-adapter or do I need to worry about 125 v 250 with that? Thank you in advance!
 
You will need access to two 30 Amp connections and a "Y" adapter, like the one in the photo.

I found out (the hard way) that my "Smart Y" requires that the 30's be "out of phase" in order to work. I believe that this simply means that the black and white wires need to be dissimilarly connected to the two 30 amp receptacles.

Someone with more electrical expertise can confirm and advise you better.
 
You will need access to two 30 Amp connections and a "Y" adapter, like the one in the photo.

I found out (the hard way) that my "Smart Y" requires that the 30's be "out of phase" in order to work. I believe that this simply means that the black and white wires need to be dissimilarly connected to the two 30 amp receptacles.

Someone with more electrical expertise can confirm and advise you better.

Why wouldn't something like this work: https://www.westmarine.com/buy/mari...to-50a-125-250v-female--12998381?recordNum=24 ?
 
Mystery:

Your newish boat almost certainly has two 120V busses. Each buss is fed from one leg of the 240V supply to produce 120V. Most boats of this size don't have any 240V users. All users are supplied from one of the 120V busses.

If the boat doesn't have any 240V loads like most, then with a special adapter you can feed both busses from one 120V 30A supply. But some combination of appliances may pull more current than 30A can supply and you will trip the shore power breaker. You can do the same thing with a 120V 50A supply but that is rare.

As noted above if you can find two 30A shorepower outlets nearby that are opposite phases then with a smart reverse Y adapter you can combine the two to supply 240V 30A which will feed each buss on your boat independently and double your wattage supply.
 
You will need access to two 30 Amp connections and a "Y" adapter, like the one in the photo.

I found out (the hard way) that my "Smart Y" requires that the 30's be "out of phase" in order to work. I believe that this simply means that the black and white wires need to be dissimilarly connected to the two 30 amp receptacles.

Someone with more electrical expertise can confirm and advise you better.
Not quite right about black and white wires...actually there are 2 hots coming to each pedestal that are opposite. One 30A should be one and the other on the other hot leg that is 180 out in phase...

I hate simplifying it as some tech guy knows better, but basically that what a smart y cord needs.
 
Mystery:

Your newish boat almost certainly has two 120V busses. Each buss is fed from one leg of the 240V supply to produce 120V. Most boats of this size don't have any 240V users. All users are supplied from one of the 120V busses.

If the boat doesn't have any 240V loads like most, then with a special adapter you can feed both busses from one 120V 30A supply. But some combination of appliances may pull more current than 30A can supply and you will trip the shore power breaker. You can do the same thing with a 120V 50A supply but that is rare.

As noted above if you can find two 30A shorepower outlets nearby that are opposite phases then with a smart reverse Y adapter you can combine the two to supply 240V 30A which will feed each buss on your boat independently and double your wattage supply.

I will check to see if there are any 240v appliances. What is the difference between 220/230/240/250? The manual does reference 230v appliances but the spec sheet says they are all 110v so there is some conflict there I need to get to the bottom of. I think I can manage the load OK by running 1-2 of the 4 AC units and turning them or one off for water heater use. I currently have one 30 amp on my boat and I guess I can see if she trips with everything running at once...
 
Last edited:
I know the 50A, 125 volt is rare, but my 1984 Albin has this inlet and I find it more convenient than the dual 30 amp cords, I just need more adapters than most other boats.
 
For your boat you might consider a std 50A240V plug with a 50A 120V socket on each of the leads of a Y .

In many marinas the 240 is split to create the 120V , and it happens that one leg has way more boats than the other.

Selecting the leg with the higher V will give your electric goodies a break.
 
Looking at a a new-ish (two year old boat) that has a 50 amp connection. My dock only has 30 amp connections available. I am more confused after reading this thread but am guessing I can just get a 30 amp to 50 amp adapter and just need to manage my load to keep the boat draw under 30 amps as to not trip any breakers?

You are 100% correct. This is exactly what I do at my home dock.

I have two 30A power inlets which feed independent breaker panes. I can theoretically consume 60A of power by running everything at once. I have an adapter which allows me to run the two panels off one 50A outlet.

I've found that I don't need to do that. I can manage the loads to keep the total draw under 30A. I feed that with a "Y" adapter - one 30A to two 30A.

In the past three seasons, over three thousand miles of travel, I've never removed the 30A to 30A "Y", feeding BOTH panels from ONE 30A outlet. Even when more is available, it's not worth the effort of changing out adapters.

It's actually easier for me to use a 50A to 30A pigtail adapter if 50A is all that's available.

I've also been able to scrape by on 20A or even 15A "household" style outlets, with the appropriate pigtail. It requires a closer watch on load, but it keeps the essential systems running, and maybe even an air conditioner or water heater.

My point is you may find you don't NEED 50A power, at which point your options become much easier, and many of the admonishments and proclamations above may not apply to you.
 
so the reverse Y 2x 30a shore power males that have a 50a boat-side female means the boat will have 50 amps of power available or is it only 30 amps? if only 30 amps, why not just use the straight (non Y) adapter so its 1x 30a shore to 1x 50a boat-side? thanks
 
so the reverse Y 2x 30a shore power males that have a 50a boat-side female means the boat will have 50 amps of power available or is it only 30 amps? if only 30 amps, why not just use the straight (non Y) adapter so its 1x 30a shore to 1x 50a boat-side? thanks

The Smart Y starts with twin 30s and provides twin 30s to the boat -- but through a 50A cord and follow-on distribution system. 60A total.

A straight single non-Y 30-to-50A adapter delivers only one 30A (total) feed to the boat, which would then mean 15A per leg on the boat.

But then some boats also have isolation transformers... and I understand in that case, the single 30-to-50A adapter won't energize the boat systems at all.

-Chris
 
Last edited:
so the reverse Y 2x 30a shore power males that have a 50a boat-side female means the boat will have 50 amps of power available or is it only 30 amps? if only 30 amps, why not just use the straight (non Y) adapter so its 1x 30a shore to 1x 50a boat-side? thanks
If the boat is 125/250V 50A, then you will have 2 legs of 30A each. A total of 60A.

A 125/250V 50A boat normally has almost 100 amps (50 per leg) available.

I always thought it was 50A per leg, but an engineer showed how it wasnt quite a full 100A possible. I forget the engineering and just live with it. :D
 
If the boat is 125/250V 50A, then you will have 2 legs of 30A each. A total of 60A.

A 125/250V 50A boat normally has almost 100 amps (50 per leg) available.

I always thought it was 50A per leg, but an engineer showed how it wasnt quite a full 100A possible. I forget the engineering and just live with it. :D



Rather than confuse the issue by trying to total up amps per leg, figure watts. No, you can't wring 100A out of a 50A cordset. You can get 2 legs of 120V @ 50A for a total of 12kW, or a 240V @ 50A for 12kW, but 2 legs of 240V isn't in the equation. 240V IS 2 legs of 120V each.
 
Rather than confuse the issue by trying to total up amps per leg, figure watts. No, you can't wring 100A out of a 50A cordset. You can get 2 legs of 120V @ 50A for a total of 12kW, or a 240V @ 50A for 12kW, but 2 legs of 240V isn't in the equation. 240V IS 2 legs of 120V each.

thank you!
 
240/120V, 50A service is 4-wire (L1,L2,N,G) 240V L1-L2, 120V L1-N and L2-N. If you plug into a 120V/30A 3-wire service (L,N,G) the adapter will usually connect L to both sides of your service panel so that all 120V loads can get power. No harm to 240V devices, they just won’t work. If you plug into two 120V/30A outlets, then two possibilities. If both outlets are on the same hot leg, your 240V devices still won’t work, but you now have 60A available for your 120V loads, assuming the two outlets are on separate circuit breakers. If the two outlets are on different legs (L1 and L2), then you get 240V/30A service and 120V/30A to each side of your panel. Not familiar with the expensive “reverse Y” adaptor, but from what has been described here it sounds like it will only permit power to flow if the two 30A outlets are on opposite legs. I fail to see the advantage of that. BTW: Most circuit breakers will only carry ~80% of the rated value continuously. Thus a “50A” breaker will carry about 40A continuous without tripping and a “30A” breaker about 24A. YMMV. There are breakers that will carry their full rated load continuously, but they use a different, and more expensive, technology.
 
These Blue Seas breakers have intetesting trip curves.

Seems like thrir breakets hold the rated amperage. Think my Paneltronics do too.
 

Attachments

  • Toggle_CB.jpg
    Toggle_CB.jpg
    44.9 KB · Views: 42
Looks like you have excellent circuit breakers. I presume these are the ones in your boat. It’s the breakers at the shorepower pedestal that matter.
 
In case the OP didnt get his answer on "what would run on 240"; this would typically be something like a laundry dryer, or perhaps a large air conditioner system.
I too have a 50A cord on board but i don't do a lot of brain damage when i come to a marina with 30A, nor do i mess with a reverse-Y. I just use a simple 50 to 30A adaptor cord, and I don't run my dryer or in winter, i dont run all my heaters at the same time.
You'll need the cord on board if you cruise around and visit other marinas.
By the way i've run into that prob where my cord is in the cockpit and they have those bow angle slips;often I will just go ahead and back stern-in anyway as long as your bow isnt sticking out too much in the fairway.
 
One more time: Two 30 amp 120v outlets through a Smart Y thence to a single 50amp/250 cord yields you 30 amps of 240v at the boat, comprised of two separate 30 amp 120v legs. You will not have 60 amps of anything on any one circuit.
 
No, but you will have 30 amps available on each of your two legs, inlets...etc....if only asking 120V per leg.....?

Except not full power if the CBs are as what someone posted before, derated ....that I am not sure about.
 
Last edited:
Agreed caltexflanc. What I forgot to mention is that there is a potential downside to using two 120V/30A outlets if they are on the same leg. In a true 240/120 service the L1 and L2 currents flow in opposite directions in the Neutral, so the maximum current in the Neutral is 50A and the neutral conductor is usually sized for that, i.e., the same as the L1 and L2 conductors. If the two 120V/30A outlets are on the same leg, one on each side of the distribution panel, the currents in the neutral will add. Thus it might be possible to have 60A in the neutral and it typically is not sized for that. That would like only be a problem if someone was drawing a full 30A on both legs for a long time, which from the other posts here seems unlikely.
 
some unfortunate semantics at work here. Popular opinion is that if you supply 2 x 30A conductors plus a neutral, then you have 60Amps of 120V power available. That is true, but it is also true that no conductor has 60Amps on it. So, no ammeter will read 60 Amps. clear?

H3: a proper panel has overcurrent protection for the hots plus neutral. 240/120 panels should have 3 pole main breaker. so, a 60A neutral, caused by 30A on each side, should trip out a 50A panel.
 
Last edited:
I beg to differ. If the two 30A supplies are in phase and not 180 degrees out of phase, the currents will add in the neutral and could be as high as 60A.
 
... in the neutral. The current would have to be measure in the neutral.
 
And thats the purpose of a smart y...not to allow you to plug into 2 30s in the same phase and get power.
 