ONAN MDKC running 220vac issue
My generator runs fine with a 110vac load. Recently I added a 220vac Compressor to fill my scuba tanks. When I turn in the generator and run the compressor only the generator start to throw a bunch of black smoke out the exhaust. It’s not oil as it dissipates quickly in the water. When I run the compressor on shore power everything runs fine. Any thoughts on what this could be? Would it have anything to do with the governor or kicking into a higher speed to support the 220vac requirement?
|
|
|
02-20-2023, 05:13 PM
|
#2
|
Guru
City: Long island
Vessel Model: Eastern
Join Date: Aug 2018
Posts: 614
|
Fist question , what is the load from the compressor? Preferably tested with an amp meter
|
|
|
02-20-2023, 05:16 PM
|
#3
|
Member
City: Lathrup Village
Vessel Name: Heart Warrior
Vessel Model: 1988 Island Gypsy 40
Join Date: Sep 2019
Posts: 22
|
Each leg is pulling 14.2 amps. I verified this while it was running under AC power.
|
|
|
02-20-2023, 05:20 PM
|
#4
|
Guru
City: Long island
Vessel Model: Eastern
Join Date: Aug 2018
Posts: 614
|
Is your Mdkc a 4k ?
|
|
|
02-20-2023, 05:25 PM
|
#5
|
Member
City: Lathrup Village
Vessel Name: Heart Warrior
Vessel Model: 1988 Island Gypsy 40
Join Date: Sep 2019
Posts: 22
|
Yes it is.
__________________
Heart Warrior-Island Gypsy 40
Daniel & Barbara Silverman
|
|
|
02-20-2023, 05:45 PM
|
#6
|
Guru
City: Long island
Vessel Model: Eastern
Join Date: Aug 2018
Posts: 614
|
Did you read 14 amps from leg to ground or from hot legs?
|
|
|
02-20-2023, 05:51 PM
|
#7
|
Member
City: Lathrup Village
Vessel Name: Heart Warrior
Vessel Model: 1988 Island Gypsy 40
Join Date: Sep 2019
Posts: 22
|
From the hot legs
__________________
Heart Warrior-Island Gypsy 40
Daniel & Barbara Silverman
|
|
|
02-20-2023, 05:54 PM
|
#8
|
Guru
City: Long island
Vessel Model: Eastern
Join Date: Aug 2018
Posts: 614
|
Ok so you should get about 18 amps @220v if you gen is running nicely. Does the smoke clear up or is it constant?
|
|
|
02-20-2023, 06:10 PM
|
#9
|
Member
City: Lathrup Village
Vessel Name: Heart Warrior
Vessel Model: 1988 Island Gypsy 40
Join Date: Sep 2019
Posts: 22
|
Right now it is constant, I have only let it run for about 10 minutes on the generator.
__________________
Heart Warrior-Island Gypsy 40
Daniel & Barbara Silverman
|
|
|
02-20-2023, 06:21 PM
|
#10
|
Guru
City: Long island
Vessel Model: Eastern
Join Date: Aug 2018
Posts: 614
|
Here are some possibilities
Air filter,
Low fuel pressure
Governor adjustment [ check hertz under load ]
Armature shorting. [ check for voltage drop ]
You could try bringing on load slowly up to 35 amps and see if it happens
|
|
|
02-20-2023, 06:40 PM
|
#11
|
Guru
City: Seattle
Vessel Name: AZZURRA
Vessel Model: Ocean Alexander 54
Join Date: Aug 2017
Posts: 3,730
|
Assuming you have the 4K generator. It appears that the diesel engine is not getting enough air. The black smoke is essentially unburnt fuel do to a lack of air. Usually as the engine gains RPM’s it gets enough air and the smoke goes away. With a generator you run at a constant RPM.
So this leads uS to one of two conclusions. obstructive air flow, like a dirty air filter or there is more load on the generator than the generator is rated for.
When running the air compressor on the generator, are you sure there are no other loads. Is it possible that some house loads in conjunction with the air compressor are maxing out the generator?
|
|
|
02-20-2023, 07:11 PM
|
#12
|
Guru
City: Palm Coast, FL
Vessel Name: Coquina
Vessel Model: Lagoon 380
Join Date: Jan 2017
Posts: 2,507
|
Quote:
Originally Posted by HeartWarrior
Each leg is pulling 14.2 amps. I verified this while it was running under AC power.
|
I am very surprised a 4kVA gen will start a 240/14A compressor. My 3HP air compressor is barely started with a 5.5 kVA genset with a softstart.
Something suspicious here. Is the compressor running at rated speed?
|
|
|
02-21-2023, 12:04 PM
|
#13
|
Guru
City: Gibsons, B.C., Canada
Vessel Name: Island Pride
Vessel Model: Palmer 32'
Join Date: Oct 2007
Posts: 4,253
|
Yes, check/change the air filter. If it cannot get air easily then the engine cannot produce power and it needs all it can get in this case.
I can think of some other problems although I am not a generator mechanic.
Motors often draw 3 to 5 times the running current to get started. Check the
start up current both on the generator AND the shore power and compare the two.
Check the running current AND the voltage on both also and compare.
Does the generator slow down. THe note will change of course with the load but does it actually slow. It will slow a few rpms but maybe to much. THis can be checked by reading the HZ.
Or get and use a laser pointer digital phototach or borrow one. Both Ebay and Amazon offer these tools for $20 to $40.
Voltage and HZ are intimately tied together. Low HZ will offer low voltage.
If the HZ are down to much at the generator the voltage will be low so the compressor cannot get the power it needs meaning the generator is overloaded.
Read the manual. It should also show unloaded HZ and then full load HZ.
THey will be different with full load lower. You may be able to turn the loaded HZ up a few Hz to regain some voltage. But not over the unloaded HZ or you may cause other problems. Once the compressor is off then turn the HZ back to it normal position.
Often small gens are rated at peak output which is a short term condition . But they cannot sustain that long term.
Talk to the compressor supplier. Depending upon the motor you may be able to install a HARD START capacitor. Intended to help with starting on RV air conditioners it MAY be a help here.
Another possibility would be to change compressor speed so although it pumps less air per minute it will unload the generator. If the compressor is driven by belts then a smaller motor side pulley and belt would help.
|
|
|
02-21-2023, 12:39 PM
|
#14
|
Senior Member
City: Langhorne
Vessel Name: Quiet Storm
Vessel Model: Nordlund 61
Join Date: Sep 2022
Posts: 223
|
Just like you main engines on a boat. If you are getting black smoke you are overloading the engine. Black smoke = Not enough air for the diesel injected.
You have
bad air cleaner or too much load. ( too small of a genset for the load)
Watts = volts x amps
4000/220=18 amps
a little math and you only have available 18 amps of power at 220. Most likely you have an unsized genset. What is the start up amps on the compressor.
I have a dive compressor on a 220 circuit and on a breaker of 20 amps.
With the shock load or anything else running at all you will probally not be able to get it started. Do the lights dim too? if so genset too small if running correctly
|
|
|
03-01-2023, 12:42 PM
|
#15
|
Guru
City: south kingstown
Vessel Name: Albatross
Vessel Model: 1973 Grand Banks 36
Join Date: May 2019
Posts: 505
|
Quote:
Originally Posted by HeartWarrior
My generator runs fine with a 110vac load. Recently I added a 220vac Compressor to fill my scuba tanks. When I turn in the generator and run the compressor only the generator start to throw a bunch of black smoke out the exhaust. It’s not oil as it dissipates quickly in the water. When I run the compressor on shore power everything runs fine. Any thoughts on what this could be? Would it have anything to do with the governor or kicking into a higher speed to support the 220vac requirement?
|
Black smoke is unburned fuel. Oil smoke would be blueish/white. Poor combustion due to low compression would also be blueish/white but wouldn't be intermittent. It sounds like over fueling or air restriction. How old is the mix loop? also how does the coolant temp behave when this happens? A bad/clogged mix loop would restrict breathing and also contribute to overheating. My instinct would be to look at the mix loop first. Always go for the simplest thing first.
|
|
|
03-17-2023, 01:54 PM
|
#16
|
Member
City: Lathrup Village
Vessel Name: Heart Warrior
Vessel Model: 1988 Island Gypsy 40
Join Date: Sep 2019
Posts: 22
|
And winner is........low voltage caused by low RPM's. Adjustment of rpm to move the Voltage from 195 to 220 fixed the problem and the Generator is running fine. Thanks for everyone's input.
__________________
Heart Warrior-Island Gypsy 40
Daniel & Barbara Silverman
|
|
|
03-17-2023, 05:35 PM
|
#17
|
Guru
City: Palm Coast, FL
Vessel Name: Coquina
Vessel Model: Lagoon 380
Join Date: Jan 2017
Posts: 2,507
|
ONAN MDKC running 220vac issue
Running a 3HP compressor now? Sometimes it takes 2 or 3 tries to get mine going.
|
|
|
03-17-2023, 05:44 PM
|
#18
|
Member
City: Lathrup Village
Vessel Name: Heart Warrior
Vessel Model: 1988 Island Gypsy 40
Join Date: Sep 2019
Posts: 22
|
It starts and runs fine all the way to 3000 psi no problem. To be safe it’s the only thing I have running when I fill a tank. We did some testing and it still had room for a couple of other ac things but it only takes 20 minutes to fill a tank and since I have a good house setup with 800 ah and 630watt solar I’m good with the other stuff.
Run amps on the motor is 14.2. The unit is built by American Air products in SC. It is there Fast 35 unit. Great machine and nice to know know we can ho dive while anchoring out as we are just starting a 3 year cruise of the Bahama Islands.
|
|
|
03-17-2023, 05:50 PM
|
#19
|
Guru
City: Palm Coast, FL
Vessel Name: Coquina
Vessel Model: Lagoon 380
Join Date: Jan 2017
Posts: 2,507
|
Thats awesome. We have charged around 20 fills, half on nitrox32, during our current bahamas cruise. Have a 20’ fill whip so we dont need to carry tanks from dink.
Its liberating to have HP air and RO too.
|
|
|
03-20-2023, 06:17 AM
|
#20
|
Guru
City: south kingstown
Vessel Name: Albatross
Vessel Model: 1973 Grand Banks 36
Join Date: May 2019
Posts: 505
|
Quote:
Originally Posted by HeartWarrior
And winner is........low voltage caused by low RPM's. Adjustment of rpm to move the Voltage from 195 to 220 fixed the problem and the Generator is running fine. Thanks for everyone's input.
|
Something to be aware of regarding RPM is HZ. There is less flexibility with cycles than voltage. Might be worth checking. 60HZ is your target.
|
|
|
 |
|