OMG, shortening the battery cables... Inverter in engine room.

My, new to me boat, came with some really long runs of DC cables, but what do I know?

I had a marine surveyor inspect the boat before buying. the survey basically says, "the electrical systems generally comply with ABYC standards".

Some issues were obvious, some were a bit of a puzzle.

For example the bilge pumps weren't working, bad ground got some action going but still not right, ... They were wired in improperly on the 4 battery bank and only getting 6 volts.

After sorting out the systems a bit to make sure 1, that I generally understood the systems and 2, that the cables were following electrically logical and safe paths and 3, had some confidence the whole thing would not burn down; I decided to run a higher load test.

My microwave was to heat some water using the Xantrex Freedom XC 2000 inverter. The batteries were fully topped up, a bank of 4 Trojan T125's.

The microwave was set to use 1000w of cooking power which means after it's overhead is added it needs just shy of 1200 watts of 120, 10 amps from the inverter.

The microwave ran!

There's always a but though, The battery monitor was showing 188 amps being sucked out of the battery bank, the cables could only get 10.5 volts delivered to the inverter.

That 188 amps is just under the 192 amp input limit of the inverter so I stopped the test fast just after reading the numbers.

I'm skilled enough to be able to guess that the wires were too long, but after down loading the owners manual for the inverter I got a good schooling on inverters and just how bad the installation was botched on this boat.

To start the recommended minimum size battery cables for a 5 foot run are 3/0 to the battery and Chassis ground at 2/0.

WTF? The installed cables, 1/0 at ~20 feet with 10 AWG running to the house bus bar for the chassis ground.

Similarly the starter cable makes about a 50 foot circuit. The bow thruster and windlass have runs way too long also.

If this is anywhere near the norm for a DIY or semi-pro-non-specialist install, it's a wonder more boats don't burn down.

Rant over.

Productive thought follows. To fix this I need to shorten the cables, a lot. That means 1, getting the inverter close to the batteries and 2, moving the batteries around the boat some.

It's a 1977 Ocean Marine 40 foot with a Lehman 120.

So first, I know it's not safe to put an inverter in an engine room with gasoline power but I'm getting the impression that it's ok around diesel power (with a caveat about heat). Is that right?

Second, I'm including a hand drawn 'plan' for your educated comment. This plan only deals with the Start and Aux batteries. It gets the aux battery out of the engine room up under the V-berth floor and uses heavy relays to be able to run the heavy cables direct and use control wires for the run to the helm.

Thanks for your help.

Click image for larger version

Name:	move batteries.jpg
Views:	75
Size:	128.6 KB
ID:	110983
__________________
Advertisement

markbarendt is offline   Reply With Quote
Old 12-06-2020, 07:38 PM   #2
TF Site Team
 
Comodave's Avatar
 
City: Au Gres, MI
Vessel Name: Never Say Never
Vessel Model: President 41 DC
Join Date: Jul 2015
Posts: 11,815
In general, I like to have a separate battery for the thruster and windlass. Then you can run heavy (4/0) cables for a short run. Put a separate battery charger there. I donít care if you can get away with a smaller cable for the short run I like the big cables so that voltage is at the maximum that the batteries supply. The extra cost is a one time cost but the benefit is every time you use the thruster or windlass you get better voltage. I would not put the inverter in the engine room and especially above the batteries if they are LA batteries. I am going to Lithium batteries for the house bank but they are pricey. Check every connection for corrosion. I like to put a copper paste on the ends of the cables before the connector goes on. Helps with conductivity and helps prevent corrosion. Then use adhesive lined heat shrink on all the connectors. I always go larger on wiring so that I get the absolute best voltage I can. Cheap in the long run.
__________________

__________________
Boat Nut:
If you are one there is no explanation necessary.
If you arenít one, there is no explanation possible.
Comodave is offline   Reply With Quote
Old 12-06-2020, 08:04 PM   #3
Guru
 
Russell Clifton's Avatar
 
City: La Conner Wa.
Vessel Name: Sea Fever
Vessel Model: Defever 49 RPH
Join Date: Sep 2012
Posts: 813
Why are you worried about a gasoline engine. That Lehman is a diesel.
Russell Clifton is offline   Reply With Quote
Old 12-06-2020, 08:23 PM   #4
Senior Member
 
markbarendt's Avatar
 
City: Portland
Vessel Name: 42
Vessel Model: Ocean Marine
Join Date: Sep 2020
Posts: 193
Quote:
Originally Posted by Russell Clifton View Post
Why are you worried about a gasoline engine. That Lehman is a diesel.
Not worried about gasoline.

Just haven't found a definitive "yes an inverter is ok in a diesel engine room" yet.
markbarendt is offline   Reply With Quote
Old 12-06-2020, 08:38 PM   #5
Guru
 
psneeld's Avatar
 
City: Ft Pierce
Vessel Name: Freedom
Vessel Model: Albin 40
Join Date: Oct 2011
Posts: 23,675
Heat is a big killer for many inverters, plus battery fumes if too close, and finally soot/oil in the air even though it's not much most of the time


Engine room can be done, but not preferred.
psneeld is online now   Reply With Quote
Old 12-06-2020, 08:43 PM   #6
Senior Member
 
markbarendt's Avatar
 
City: Portland
Vessel Name: 42
Vessel Model: Ocean Marine
Join Date: Sep 2020
Posts: 193
Quote:
Originally Posted by Comodave View Post
In general, I like to have a separate battery for the thruster and windlass. Then you can run heavy (4/0) cables for a short run. Put a separate battery charger there. I donít care if you can get away with a smaller cable for the short run I like the big cables so that voltage is at the maximum that the batteries supply. The extra cost is a one time cost but the benefit is every time you use the thruster or windlass you get better voltage. I would not put the inverter in the engine room and especially above the batteries if they are LA batteries. I am going to Lithium batteries for the house bank but they are pricey. Check every connection for corrosion. I like to put a copper paste on the ends of the cables before the connector goes on. Helps with conductivity and helps prevent corrosion. Then use adhesive lined heat shrink on all the connectors. I always go larger on wiring so that I get the absolute best voltage I can. Cheap in the long run.
The concern that I have heard about putting an inverter above the L.A. batteries is two fold, hydrogen and caustic fumes. The consensus I'm seeing is that both dissipate very quickly with even a little venting. The recommendation is simply to mount the inverter lower.

Mounting low brings up a (code?) concern about having the inverter below waterline.
markbarendt is offline   Reply With Quote
Old 12-06-2020, 08:49 PM   #7
Guru
 
twistedtree's Avatar
 
City: Gloucester, MA
Join Date: Jan 2013
Posts: 6,537
I agree that the ER isn't a desirable location for the inverter.


Another approach to solving the problem would be to up-size the cables. There are lots of calculators for figuring the voltage drop through wires, and you could run that on your setup. 4/0 cable might do the trick, or perhaps even two in parallel. I think it's worth an hour to at least check it out.
__________________
MVTanglewood.com
twistedtree is online now   Reply With Quote
Old 12-06-2020, 08:50 PM   #8
Guru
 
rochepoint's Avatar
 
City: Sidney BC Canada
Vessel Name: RochePoint
Vessel Model: 1985 Cheer Men PT38 Sedan
Join Date: Apr 2009
Posts: 1,654
Quote:
Originally Posted by markbarendt View Post
Not worried about gasoline.

Just haven't found a definitive "yes an inverter is ok in a diesel engine room" yet.
That where our inverter has been for the last 30 years and just had another survey done last week and no problems with it there. We just have to change the chassis ground to 1/0 cable per the ABYC requirements for our inverter.
__________________
Cheers
Mike Barge
rochepoint is offline   Reply With Quote
Old 12-06-2020, 08:52 PM   #9
Senior Member
 
markbarendt's Avatar
 
City: Portland
Vessel Name: 42
Vessel Model: Ocean Marine
Join Date: Sep 2020
Posts: 193
Quote:
Originally Posted by psneeld View Post
Heat is a big killer for many inverters, plus battery fumes if too close, and finally soot/oil in the air even though it's not much most of the time


Engine room can be done, but not preferred.
Yep, all things on a boat are a compromise.

I'm thinking that if I ensure good ventilation, then the engine room (and under V-berth battery is probably a lot less risky, and easier on the equipment.
markbarendt is offline   Reply With Quote
Old 12-06-2020, 08:54 PM   #10
Senior Member
 
markbarendt's Avatar
 
City: Portland
Vessel Name: 42
Vessel Model: Ocean Marine
Join Date: Sep 2020
Posts: 193
Quote:
Originally Posted by rochepoint View Post
That where our inverter has been for the last 30 years and just had another survey done last week and no problems with it there. We just have to change the chassis ground to 1/0 cable per the ABYC requirements for our inverter.
I like that.
markbarendt is offline   Reply With Quote
Old 12-06-2020, 08:58 PM   #11
Senior Member
 
DrissZougari's Avatar
 
City: (Cypress Landing) Chocowinity, NC
Vessel Name: BZ interlude
Vessel Model: MS390
Join Date: Mar 2019
Posts: 161
I will assume that you do have house batteries separate from the starter and aux batteries.
Moving the Aux battery forward is a good idea (closer to the windlass & Thruster), as log as you can provide Eng. charging capability.
Why a timer switch while you can use a standard switches to activate the Aux battery to run the windlass or Thruster separately when needed (of course still driven by the ignition switch). you timer switch will put the Aux and the Start battery in parallels after 10min and you will loose both batteries if the alternator goes bad.
good luck.

The inverter in the Eng Room should just fine and you can also add ventilation if you heat any concerns.
DrissZougari is offline   Reply With Quote
Old 12-06-2020, 08:58 PM   #12
Senior Member
 
markbarendt's Avatar
 
City: Portland
Vessel Name: 42
Vessel Model: Ocean Marine
Join Date: Sep 2020
Posts: 193
Quote:
Originally Posted by twistedtree View Post
I agree that the ER isn't a desirable location for the inverter.


Another approach to solving the problem would be to up-size the cables. There are lots of calculators for figuring the voltage drop through wires, and you could run that on your setup. 4/0 cable might do the trick, or perhaps even two in parallel. I think it's worth an hour to at least check it out.
I did try 2 calculators and according to both there simply isn't a normal cable size that is big enough.
markbarendt is offline   Reply With Quote
Old 12-06-2020, 09:38 PM   #13
Guru
 
Pau Hana's Avatar


 
City: Seattle, WA
Vessel Name: Pau Hana
Vessel Model: 1989 PT52 Overseas Yachtfisher
Join Date: Aug 2012
Posts: 2,534
Quote:
Originally Posted by Comodave View Post
In general, I like to have a separate battery for the thruster and windlass. Then you can run heavy (4/0) cables for a short run. Put a separate battery charger there. I donít care if you can get away with a smaller cable for the short run I like the big cables so that voltage is at the maximum that the batteries supply. The extra cost is a one time cost but the benefit is every time you use the thruster or windlass you get better voltage. I would not put the inverter in the engine room and especially above the batteries if they are LA batteries. I am going to Lithium batteries for the house bank but they are pricey. Check every connection for corrosion. I like to put a copper paste on the ends of the cables before the connector goes on. Helps with conductivity and helps prevent corrosion. Then use adhesive lined heat shrink on all the connectors. I always go larger on wiring so that I get the absolute best voltage I can. Cheap in the long run.
^^^This.

We have 2 group 31 AGM on a standalone charger under the forward berth for the thruster. Short cable runs so max power is drivers to the thruster.

For the house bank, I went with doubled 4/0 cable from the bank to the inverter, and 3/0 to feed the main DC distribution panel.
__________________
Peter- Marine Insurance Guru & tuna fishing addict!

1989 52' PT Overseas yachtfisher
Pau Hana is offline   Reply With Quote
Old 12-06-2020, 09:54 PM   #14
Senior Member
 
markbarendt's Avatar
 
City: Portland
Vessel Name: 42
Vessel Model: Ocean Marine
Join Date: Sep 2020
Posts: 193
Quote:
Originally Posted by DrissZougari View Post
I will assume that you do have house batteries separate from the starter and aux batteries.
Moving the Aux battery forward is a good idea (closer to the windlass & Thruster), as log as you can provide Eng. charging capability.
Why a timer switch while you can use a standard switches to activate the Aux battery to run the windlass or Thruster separately when needed (of course still driven by the ignition switch). you timer switch will put the Aux and the Start battery in parallels after 10min and you will loose both batteries if the alternator goes bad.
good luck.
The length of time idea is good, I may consider a shorter duration.

The idea of the timer is to avoid a problem like what you describe. With the old school, manual switch on 'both' position, there is no automatic protection of the starter battery from overuse.

The time for the 'both' relay, is only there to allow the aux battery some time to 'jump charge' the starter battery.

While 'both' could be used the other way to help the bow thruster that is not the intent.

Your thought there got me thinking and I do think that I will change what I call that relay/switch to 'start assist' or 'jump start' so that other people better understand the intent.
markbarendt is offline   Reply With Quote
Old 12-06-2020, 10:03 PM   #15
Guru
 
porman's Avatar
 
City: Duvall, Wa. USA
Vessel Name: Beach Music II
Vessel Model: 2003 Mainship 430 Trawler
Join Date: Aug 2014
Posts: 750
Peter, so nothing is charging the thruster batteries when you're underway?
porman is offline   Reply With Quote
Old 12-06-2020, 10:08 PM   #16
Senior Member
 
markbarendt's Avatar
 
City: Portland
Vessel Name: 42
Vessel Model: Ocean Marine
Join Date: Sep 2020
Posts: 193
Quote:
Originally Posted by Pau Hana View Post
^^^This.

We have 2 group 31 AGM on a standalone charger under the forward berth for the thruster. Short cable runs so max power is drivers to the thruster.

For the house bank, I went with doubled 4/0 cable from the bank to the inverter, and 3/0 to feed the main DC distribution panel.
I like big cables too.

The charging system is a whole 'nuther monster.

I guess I don't understand the advantage of a stand alone charger up front.

What I'm getting at is that when using the thruster I'll either be coming or going from a dock or mooring ball; the only practical charging device that I'll have available in that moment will be the alternator.

What am I missing?
markbarendt is offline   Reply With Quote
Old 12-06-2020, 10:13 PM   #17
Guru
 
Pau Hana's Avatar


 
City: Seattle, WA
Vessel Name: Pau Hana
Vessel Model: 1989 PT52 Overseas Yachtfisher
Join Date: Aug 2012
Posts: 2,534
Quote:
Originally Posted by porman View Post
Peter, so nothing is charging the thruster batteries when you're underway?
Weíve generally run the genset while underway, so the thruster batteries are being charged. With the revised setup, Iíll be charging the forward bank via the DC-DC charger.
__________________
Peter- Marine Insurance Guru & tuna fishing addict!

1989 52' PT Overseas yachtfisher
Pau Hana is offline   Reply With Quote
Old 12-06-2020, 10:20 PM   #18
Senior Member
 
markbarendt's Avatar
 
City: Portland
Vessel Name: 42
Vessel Model: Ocean Marine
Join Date: Sep 2020
Posts: 193
Quote:
Originally Posted by Pau Hana View Post
Weíve generally run the genset while underway, so the thruster batteries are being charged. With the revised setup, Iíll be charging the forward bank via the DC-DC charger.
That explains it.
markbarendt is offline   Reply With Quote
Old 12-06-2020, 10:30 PM   #19
TF Site Team
 
Comodave's Avatar
 
City: Au Gres, MI
Vessel Name: Never Say Never
Vessel Model: President 41 DC
Join Date: Jul 2015
Posts: 11,815
Quote:
Originally Posted by Pau Hana View Post
Weíve generally run the genset while underway, so the thruster batteries are being charged. With the revised setup, Iíll be charging the forward bank via the DC-DC charger.
I donít charge the thruster battery while underway. Only on shore power since we usually donít run the genset underway. Never had any issues that way.
__________________
Boat Nut:
If you are one there is no explanation necessary.
If you arenít one, there is no explanation possible.
Comodave is offline   Reply With Quote
Old 12-06-2020, 10:47 PM   #20
Guru
 
Pau Hana's Avatar


 
City: Seattle, WA
Vessel Name: Pau Hana
Vessel Model: 1989 PT52 Overseas Yachtfisher
Join Date: Aug 2012
Posts: 2,534
Quote:
Originally Posted by markbarendt View Post
I like big cables too.

The charging system is a whole 'nuther monster.

I guess I don't understand the advantage of a stand alone charger up front.

What I'm getting at is that when using the thruster I'll either be coming or going from a dock or mooring ball; the only practical charging device that I'll have available in that moment will be the alternator.

What am I missing?
The standalone charger eliminates a long, heavy DC cable run from the engine room to the thruster. 12v DC is best served by short runs, while 24v or 48v can get away with longer runs without much loss.
__________________

__________________
Peter- Marine Insurance Guru & tuna fishing addict!

1989 52' PT Overseas yachtfisher
Pau Hana is offline   Reply With Quote
Reply

Thread Tools Search this Thread
Search this Thread:

Advanced Search
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off



» Trawler Port Captains
Port Captains are TF volunteers who can serve as local guides or assist with local arrangements and information. Search below to locate Port Captains near your destination. To learn more about this program read here: TF Port Captain Program





All times are GMT -5. The time now is 05:35 PM.


Powered by vBulletin® Version 3.8.8 Beta 4
Copyright ©2000 - 2021, vBulletin Solutions, Inc.
Search Engine Optimization by vBSEO 3.6.0
Copyright 2006 - 2012
×