Isolation Transformers question

As part of my refit, I am looking at adding in an isolation transformer, rather than galvanic isolators.

Is it advisable to just have an isolation transformer?
Can you parallel isolation transformers?
Any recommendations on the brand/model/etc for the transformers or isolators?

I was looking at the victron isolation transformer, but need to have about 20kw of shore power.

Thank you
sndog is offline   Reply With Quote
Old 03-22-2023, 12:30 PM   #2
Valued Technical Contributor
 
DavidM's Avatar
 
City: Litchfield, Ct
Join Date: Aug 2012
Posts: 6,566
You want a single isolation transformer on the shorepower inlet.

20 kW? The maximum you can get out of a 50A/220V shorepower receptical is 50*220 = 11 kW.

David
DavidM is online now   Reply With Quote
Old 03-22-2023, 12:42 PM   #3
Senior Member
 
City: Corona Del Mar
Join Date: Nov 2022
Posts: 144
Quote:
Originally Posted by DavidM View Post
You want a single isolation transformer on the shorepower inlet.

20 kW? The maximum you can get out of a 50A/220V shorepower receptical is 50*220 = 11 kW.

David
Yes, but 100A x 220V = 22kw
sndog is offline   Reply With Quote
Old 03-22-2023, 12:45 PM   #4
Moderator Emeritus
 
ksanders's Avatar
 
City: SEWARD ALASKA
Vessel Name: DOS PECES
Vessel Model: BAYLINER 4788
Join Date: Feb 2011
Posts: 5,956
If you have a isolation transformer there is no need for galvanic isolators.

You want a isolation transformer to match the shore power line and isolation transformer standard sizes do just that.

Do not parallel isolation transformers, and there is not any reason to do so. Just buy the correct one for your shore power inlet.
__________________
Kevin Sanders
Bayliner 4788 Dos Peces
Seward, Alaska - La Paz, Baja California Sur
https://maps.findmespot.com/s/2R02#live/assets
ksanders is offline   Reply With Quote
Old 03-22-2023, 01:17 PM   #5
Guru
 
twistedtree's Avatar
 
City: Walkabout Creek
Join Date: Jan 2013
Posts: 9,114
Quote:
Originally Posted by sndog View Post
Yes, but 100A x 220V = 22kw


Is that two 50A cords, or a single 100A. If two cords, then on 12kva isolation transformer for each. If a single cord then a single 25kva.
__________________
MVTanglewood.com
twistedtree is offline   Reply With Quote
Old 03-22-2023, 01:19 PM   #6
Guru
 
twistedtree's Avatar
 
City: Walkabout Creek
Join Date: Jan 2013
Posts: 9,114
Quote:
Originally Posted by twistedtree View Post
Is that two 50A cords, or a single 100A. If two cords, then on 12kva isolation transformer for each. If a single cord then a single 25kva.


Acme/Hubble make good isolation transformers including taps so you can wire a selector switch to boost 208V shore power when needed. They also make an auto sensing and boosting model, but considerably more expensive.
__________________
MVTanglewood.com
twistedtree is offline   Reply With Quote
Old 03-22-2023, 01:21 PM   #7
Senior Member
 
City: Corona Del Mar
Join Date: Nov 2022
Posts: 144
Quote:
Originally Posted by twistedtree View Post
Acme/Hubble make good isolation transformers including taps so you can wire a selector switch to boost 208V shore power when needed. They also make an auto sensing and boosting model, but considerably more expensive.
Thank you
sndog is offline   Reply With Quote
Old 03-22-2023, 01:22 PM   #8
Senior Member
 
City: Corona Del Mar
Join Date: Nov 2022
Posts: 144
Quote:
Originally Posted by twistedtree View Post
Is that two 50A cords, or a single 100A. If two cords, then on 12kva isolation transformer for each. If a single cord then a single 25kva.
Still deciding between the two. Any pros/cons?
sndog is offline   Reply With Quote
Old 03-22-2023, 02:22 PM   #9
Guru
 
twistedtree's Avatar
 
City: Walkabout Creek
Join Date: Jan 2013
Posts: 9,114
Quote:
Originally Posted by sndog View Post
Still deciding between the two. Any pros/cons?

100A dock outlets will only be in places expecting big boats - say 70' or bigger, and probably more in the 100'+ range. 50A outlets will be MUCH more common So based on that I'd go with two 50s.


That said, if you have two 50s, then you need to split up your loads between the two. Dedicating one to HVAC, and the other to everything else is common, but certainly not the only way to do it. But it has the advantage of letting you run the boat off a single 50A outlet as long as you don't need HVAC.


Just as one example, I have three load panels in the boat; Inverter loads, which is pretty much everything, non-inverter loads which is only the hot water heater and shore chargers, and HVAC. Then I have two 50A shore cords, and I can any of my load panels to either shore cord. So I can run off one cord or two, with loads split up in a number of different ways. It's relatively easy to do in a new build, but could be a lot harder in a refit.
__________________
MVTanglewood.com
twistedtree is offline   Reply With Quote
Reply

Thread Tools Search this Thread
Search this Thread:

Advanced Search
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


» Trawler Port Captains
Port Captains are TF volunteers who can serve as local guides or assist with local arrangements and information. Search below to locate Port Captains near your destination. To learn more about this program read here: TF Port Captain Program





All times are GMT -5. The time now is 07:31 AM.


Powered by vBulletin® Version 3.8.8 Beta 4
Copyright ©2000 - 2023, vBulletin Solutions, Inc.
Search Engine Optimization by vBSEO 3.6.0
Copyright 2006 - 2012