Old 04-08-2016, 06:20 AM   #21
FF
Guru
 
FF's Avatar
 
Join Date: Oct 2007
Posts: 22,553
"I'm still not clear on what the risks are to motors or other AC gear if the voltage is too low. Do they simply shut down or does it damage them?"

Modern AC motors demand a certain number of watts to operate.

V x A = W

So a 120v motor requiring 1200w to operate will draw 10A from the source.

The same motor at 100V will tale 12A from the supply.

AS the voltage drops the amp draw goes UP , yet the wires that make up the motor do not get thicker to handle the higher amps..

After a low enough voltage ,, a better grade motor will pop an overheat sensor , or an internal circuit breaker ,

but the chance is the feared "white smoke" will come out , and the motor will need a rewind or replacement.

IF you can,, always purchase any AC motor "universal wound" meaning it will have brushes in a brush holder.

Will be marked AC/DC.

These are fantastic as feeding them low voltage does not increase the amp draw, it simply makes the motor less powerful.

These are a great yard sale find for power tools for on board work with a non sine wave inverter or small gen set with a low power factor.

Also nice at home where 250 ft of extension cord will still operate a chain saw , just a bit slower.
FF is offline   Reply With Quote
Old 04-08-2016, 06:48 AM   #22
Veteran Member
 
seadogmike's Avatar
 
City: Charleston, SC
Vessel Name: Inspiration
Join Date: Nov 2015
Posts: 66
So here is my take...... A/C units.... even the most sophisticated newer models will accept voltages between 187 and 253 VAC for a 208-230 supply.
As mentioned earlier, when the voltage goes down, more current is drawn. When you are at the bottom of that range, a brownout/surge can have detrimental effects on not only HVAC/refrigeration equipment, but also any AC electronics.

One thing to take into consideration is how often you would be in this situation. Not all owners are subjected to a lot of different voltages, and in their case, I would not recommend the Iso-boost, unless they just wanted it to help with resale value later.
OTOH if they are coastal cruisers visiting many different marinas, I would recommend it.

There are ways to connect your isolation transformer to allow variable "taps". This is a more cost effective approach. That is if the isolation transformer has multiple taps for voltage adjustment. This setup would mean you would check the incoming voltage, set the tap to the proper incoming by a rotary switch prior to turning power on. IMHO this is as good an option as any.

Just my $.02
__________________
Seadogmike
Coastal, SC
ABYC Certified Marine Electrician
seadogmike is offline   Reply With Quote
Old 04-09-2016, 05:40 AM   #23
FF
Guru
 
FF's Avatar
 
Join Date: Oct 2007
Posts: 22,553
It is a shame that the isolation transformer folks do not add to their product line.

With little effort the unit could function as a great power supply.

Take DC from the alt , chop it up and reassemble as "house current" for any application'\

With a DC noisemaker the unit would work as well as the new Honda gas units ,
no fixed operating RPM, just enough to supply the load.

And of course they could operate as a boost inverter does , taking juice from the batts to help a rotten dock power source or a tiny noisemaker get that 2nd or 3rd air cond started.
FF is offline   Reply With Quote
Old 04-09-2016, 08:26 AM   #24
Moderator Emeritus
 
Bay Pelican's Avatar
 
City: Chicago, IL
Vessel Name: Bay Pelican
Vessel Model: Krogen 42
Join Date: Oct 2007
Posts: 2,993
Quote:
Originally Posted by caltexflanc View Post
If you are going to be spending a lot of time on a 208v dock with AC running, I'd advise doing something. Some sort of voltage booster will pay for itself over time in longer equipment life and usability of the boat. Find out if the isotransformer you getting a deal on can be tapped for switched boost. The manufacturer can tell you this and likely give instructions how. Or spring for the boost add on from Charles or Ward's (would be worth giving the latter a call and getting their advice).
I believe Charles sells a 50 amp Isoboost isolation transformer.
__________________
Marty
Bay Pelican is offline   Reply With Quote
Old 04-09-2016, 08:49 AM   #25
Guru
 
caltexflanc's Avatar
 
City: North Carolina for now
Join Date: Aug 2011
Posts: 6,348
Quote:
Originally Posted by Bay Pelican View Post
I believe Charles sells a 50 amp Isoboost isolation transformer.
Yes, I had two of them on my Hatteras. They also sell boost-only for those who already have an isolation transformer and can't, or don't want to, hassle with tapping and switching. Wards makes one too and sells all.
__________________
George

"There's the Right Way, the Wrong Way, and what some guy says he's gotten away with"
caltexflanc is offline   Reply With Quote
Old 04-09-2016, 01:35 PM   #26
Guru
 
angus99's Avatar
 
City: Signal Mtn., TN
Vessel Name: Stella Maris
Vessel Model: Defever 44
Join Date: Feb 2012
Posts: 2,741
Quote:
Originally Posted by seadogmike View Post
So here is my take...... A/C units.... even the most sophisticated newer models will accept voltages between 187 and 253 VAC for a 208-230 supply.
As mentioned earlier, when the voltage goes down, more current is drawn. When you are at the bottom of that range, a brownout/surge can have detrimental effects on not only HVAC/refrigeration equipment, but also any AC electronics.

There are ways to connect your isolation transformer to allow variable "taps". This is a more cost effective approach. That is if the isolation transformer has multiple taps for voltage adjustment. This setup would mean you would check the incoming voltage, set the tap to the proper incoming by a rotary switch prior to turning power on. IMHO this is as good an option as any.

Just my $.02
Thanks, Michael. Sounds like it's rolling the dice to assume shore power will be adequate and not damage equipment unless I have a boosting transformer.

Unfortunately, the unit that sounded like such a good deal doesn't allow variable taps. So I'm thinking I'll bide my time and ponder this some more.

I have also seen ACME buck and boost transformers advertised as "marine" units that are priced appealingly, but they don't mention ABYC compliance.
angus99 is offline   Reply With Quote
Reply

Thread Tools Search this Thread
Search this Thread:

Advanced Search
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


» Trawler Port Captains
Port Captains are TF volunteers who can serve as local guides or assist with local arrangements and information. Search below to locate Port Captains near your destination. To learn more about this program read here: TF Port Captain Program





All times are GMT -5. The time now is 02:17 AM.


Powered by vBulletin® Version 3.8.8 Beta 4
Copyright ©2000 - 2024, vBulletin Solutions, Inc.
Search Engine Optimization by vBSEO 3.6.0
Copyright 2006 - 2012