Inverter in diesel engine room -- how bad?

I've been studying how/where/when/cost/etc. of a inverter installation. Easiest in this case is to replace an existing charger with an inverter/charger in the same location.

That location is in the engine room, very near but not directly above, the easiest supply battery bank, which is currently (and would continue to be) used for the bow thruster. Nearness to the supply bank addresses manufacturers' distance and fusing recommendations. That location would also simplify AC-side wiring from inverter/charger to the main panel.

Of course the installation manuals say as near the battery bank as possible, but not in an engine room or other hot location. Battery manuals say pretty much the same thing, as do charger manuals. Nor are batteries and chargers supposed to live together in the same location. (All this from a synthesis of Mastervolt, Victron Energy, and ProMariner charger and inverter/charger manuals.)

But then every boat we've ever owned, or even shopped on, has had batteries and chargers in the engine room, direct from the boat manufacturer.

(Our new ride, which is as originally built, currently has 4 battery banks and 3 chargers in our engine room. Not immediately next to the engines, not hugely far away from the genset.)

So, how horrible can it be, placing an inverter/charger in an engine room... along with those other chargers and batteries that aren't supposed to be there either?

Would we says it's:
A) Less optimal than it could be but would work OK
B) Not optimal, but better than nothing
C) really bad
D) dangerous and stupid

Or... maybe we could rate it on a scale of 1-10, with 1 being good enough and 10 being dangerous and stupid...

?????

-Chris
__________________
Chesapeake Bay, USA
ranger42c is offline   Reply With Quote
Old 09-27-2021, 03:48 PM   #2
Guru
 
City: Rochester, NY
Vessel Name: Hour Glass
Vessel Model: Chris Craft Catalina 381
Join Date: Aug 2019
Posts: 3,961
The only real issue with putting the inverter in the engine room is heat. As long as the engine room doesn't get hot enough to cause significant inverter de-rating or overheating, it's fine. Worst case, you could always build a box around an inverter or battery bank and vent it to the outside to keep things cooler. For batteries, unless you're running long travel day after long travel day, protecting them from radiant heat will help a lot.

My house bank, inverter, and solar controllers are outside of the engine room (although I'd have to move the house bank into the engine room if I ever make it bigger, mostly for weight distribution). The start batteries and charger are in the engine room, however, with no issues.

Batteries and inverters can live together, just don't put the inverter above the batteries (especially if they're flooded) where it'll receive all of the battery off-gassing. With some ventilation, the inverter off to the side and especially if you're using AGM, gel, or lithium batteries then having both in the same compartment is no problem.
rslifkin is offline   Reply With Quote
Old 09-27-2021, 06:30 PM   #3
Senior Member
 
City: St. Petersburg
Join Date: Oct 2007
Posts: 284
Victron publishes derating curves. For a 104F engine room, the maximum continuous power from a 3kW MultiPlus inverter/charger is 2.2kW.
__________________
Charlie Johnson
ABYC Master Technician
CharlieJ is offline   Reply With Quote
Old 09-27-2021, 06:41 PM   #4
Guru
 
dhays's Avatar
 
City: Gig Harbor
Vessel Name: Kinship
Vessel Model: North Pacific 43
Join Date: May 2015
Posts: 8,990
My Magnum 2800W inverter charger is in the ER. Not ideal but then I have a single engine boat and my engine coolant temp stays at a constant 174 degrees. So hot, but the ER doesn't get super hot.


When I'm under way, I'm not charging the battery with the charger. I'm also not typically running a lot of 120volt loads. The refer is running on 12v when under way and I'm not heating water.
__________________
Regards,

Dave
SPOT page
dhays is offline   Reply With Quote
Old 09-27-2021, 07:00 PM   #5
Guru
 
O C Diver's Avatar
 
City: Fort Myers, FL... Summers in Crisfield, MD
Vessel Name: Slow Hand
Vessel Model: Cherubini Independence 45
Join Date: Dec 2010
Posts: 10,058
My Magnum Energy inverter charger is in the engine room. During the refit process, I added exhaust ventilation to keep the temperature down. The thermometer is close to the ceiling and rarely shows temperature above 110 degrees. What the temperature is at the batteries and inverter is probably significantly less. If you plan to do what I did as far as added ventilation, remember to increase incoming air vents to prevent starving the engine or generator.

Ted
__________________
Blog: mvslowhand.com
I'm tired of fast moves, I've got a slow groove, on my mind.....
I want to spend some time, Not come and go in a heated rush.....
"Slow Hand" by The Pointer Sisters
O C Diver is offline   Reply With Quote
Old 09-27-2021, 07:13 PM   #6
TF Site Team
 
koliver's Avatar
 
City: Saltspring Island
Vessel Name: Retreat
Vessel Model: C&L 44
Join Date: Nov 2007
Posts: 4,416
Quote:
Originally Posted by dhays View Post
My Magnum 2800W inverter charger is in the ER. Not ideal but then I have a single engine boat and my engine coolant temp stays at a constant 174 degrees. So hot, but the ER doesn't get super hot.

When I'm under way, I'm not charging the battery with the charger. I'm also not typically running a lot of 120volt loads. The refer is running on 12v when under way and I'm not heating water.

My Xantrex manual says to try to keep the temp under 50C (122F).
Never been an issue.
I too can't use the charger while under way, rarely use the inverter feature.
__________________
Keith
koliver is offline   Reply With Quote
Old 09-27-2021, 07:41 PM   #7
Guru
 
tiltrider1's Avatar
 
City: Seattle
Vessel Name: AZZURRA
Vessel Model: Ocean Alexander 54
Join Date: Aug 2017
Posts: 2,803
Unless the engine room gets excessively hot, its no big deal to install an inverter/charger in the engine room. If it is a gas boat, DON'T DO IT.
tiltrider1 is offline   Reply With Quote
Old 09-27-2021, 09:03 PM   #8
Moderator Emeritus
 
ksanders's Avatar
 
City: SEWARD ALASKA
Vessel Name: LISAS WAY
Vessel Model: BAYLINER 4788
Join Date: Feb 2011
Posts: 5,227
I have a pair of stacked Victron multiplus 3KW inverter/chargers in the engine room, and they work just fine
__________________
Kevin Sanders
Bayliner 4788
Seward, Alaska
ksanders is offline   Reply With Quote
Old 09-27-2021, 09:48 PM   #9
Guru
 
Soo-Valley's Avatar
 
City: Gulf Islands, BC Canada
Vessel Name: Soo Valley
Vessel Model: Grand Banks 36
Join Date: Jul 2019
Posts: 1,892
My survey made me inverter/charger it out. It was installed in engine room when I n=bought the boat. Anyone have ABYC on this?
__________________
SteveK AKA Soo Valley
You only need one working engine. That is why I have two.
Soo-Valley is offline   Reply With Quote
Old 09-28-2021, 05:47 AM   #10
Guru
 
mvweebles's Avatar
 
City: Saint Petersburg
Vessel Name: Weebles
Vessel Model: 1970 Willard 36 Trawler
Join Date: Mar 2019
Posts: 2,853
I recently went with a LiFePO4 bank and moved my house bank and inverter from the ER to the aft lazarette. My goal was twofold: free-up ER space; and put the LFP batteries in an out-of-way place. Heat was not a concern - engine rooms I've been in have been hot but not overwhelmingly so, even in the tropics. I'd hazard a guess the OEM cautions were rooted in lawyers unsure of how people would configure their system. FLA batteries off-gas, inverters are generally NOT ignition protected so presence of gasoline would be a huge hazard.

Unless OP has a strong desire to move the batteries and inverter/charger, I'd keep it as-is. By far, biggest config issue remains long cable runs that foster voltage drop (and heat) so keeping them close to one another is a top priority.

Peter
__________________
M/V Weebles
1970 Willard 36 Sedan Trawler
Current Location: Ensenada MX
mvweebles is offline   Reply With Quote
Old 09-28-2021, 05:59 AM   #11
FF
Guru
 
FF's Avatar
 
Join Date: Oct 2007
Posts: 22,222
Besides derating for ER temperature , the inverter will have a hard life if directly over the charging batt set.
Not just hydrogen comes up out of a batt being heavily charged.
FF is offline   Reply With Quote
Old 09-28-2021, 07:48 AM   #12
Guru
 
ranger42c's Avatar
 
City: Annapolis
Vessel Model: 58' Sedan Bridge
Join Date: Aug 2013
Posts: 5,710
Thanks, all

Hadn't found Victron's de-rating charts, so seeing those helps. The fact they exist seems to confirm engine room temps not optimal but not dangerous. Check.

Diesel, not gas, check.

Not located directly over the batteries. Check.

Additional ventilation, hmmmmm... have to look further into that.

-Chris
__________________
Chesapeake Bay, USA
ranger42c is offline   Reply With Quote
Old 10-05-2021, 11:58 AM   #13
Guru
 
C lectric's Avatar
 
City: Gibsons, B.C., Canada
Vessel Name: Island Pride
Vessel Model: Palmer 32'
Join Date: Oct 2007
Posts: 3,573
Sometimes just increasing air circulation to the device will improve cooling. A couple of small fans aimed at the inverter would help. THey could be activated by a temp. sensitive switch.
The bilge is almost always much cooler than the top of the E.R. Set the fans low so they pick up that cooler air even if some small ducting is needed.
C lectric is offline   Reply With Quote
Old 10-05-2021, 12:18 PM   #14
Guru
 
syjos's Avatar


 
City: Gig Harbor
Vessel Name: Sandpiper
Vessel Model: Bluewater 40 Pilothouse Trawler
Join Date: Nov 2012
Posts: 2,055
I've sold 8 or 9 inverters and other electronic components to boaters whose electronics in the engine room was destroyed by an exhaust hose leak which sprayed salt spray or steam on everything. A few of those were from generator exhaust leaks.

None were repairable due to the quick corrosion of the electronic components.

I have no electronics of any kind in the engineroom. If I experience an exhaust leak, I repair the leak, wash the entire engine room and can continue my cruise.

With electronics dead from salt water in the ER, the cruise may not be continued depending on whats installed down there.
syjos is offline   Reply With Quote
Old 10-06-2021, 02:27 AM   #15
Veteran Member
 
jgtrucking's Avatar
 
City: Camden, TN
Vessel Name: Toscana
Vessel Model: Island Gypsy 44 Flushdeck
Join Date: Jul 2019
Posts: 85
Anything in the seawater circuit should be replaced well in advance of failure underway. That being said sh#% sometimes happens even to the most dilligent. The ER may well be tge popular place for these components, heck on some boats, the only place. If you have another viable location, great. But most will still have to be in there.
jgtrucking is offline   Reply With Quote
Old 10-06-2021, 11:35 AM   #16
Moderator Emeritus
 
ksanders's Avatar
 
City: SEWARD ALASKA
Vessel Name: LISAS WAY
Vessel Model: BAYLINER 4788
Join Date: Feb 2011
Posts: 5,227
Quote:
Originally Posted by jgtrucking View Post
Anything in the seawater circuit should be replaced well in advance of failure underway. That being said sh#% sometimes happens even to the most dilligent. The ER may well be tge popular place for these components, heck on some boats, the only place. If you have another viable location, great. But most will still have to be in there.
That is the challenge for most boats in the size range generally found in recreational boats.

No dedicated space for electrical components.

That leaves little choice except for the engine room.
__________________
Kevin Sanders
Bayliner 4788
Seward, Alaska
ksanders is offline   Reply With Quote
Old 10-06-2021, 04:11 PM   #17
TF Site Team
 
Insequent's Avatar
 
City: Brisbane
Vessel Name: Insequent
Vessel Model: Ocean Alexander 50 Mk I
Join Date: Mar 2012
Posts: 3,372
For the OP, your box "A" is about right. If you can put inverter/charger elsewhere then do it. Of less concern is house bank, but likewise not in ER if possible.

My Victron Quattro 3000 and house bank are in the ER. I've had the Quattro de-rate to the point where the dryer trips it if I use it underway. Washing machine is ok.
Of course there are other AC loads underway, including my nav PC which takes 600W.
Unfortunate, as underway the large alternators can provide plenty of juice. I checked a couple of times and the Quattro was a bit over 50C
__________________
Brian
Insequent is offline   Reply With Quote
Old 10-06-2021, 05:54 PM   #18
Senior Member
 
DrissZougari's Avatar
 
City: (Cypress Landing) Chocowinity, NC
Vessel Name: BZ interlude
Vessel Model: MS390
Join Date: Mar 2019
Posts: 179
They do not recommend the installation in Gas engine room that is.
DrissZougari is offline   Reply With Quote
Old 10-08-2021, 01:53 PM   #19
Veteran Member
 
City: Key West
Vessel Name: Joe~lyn
Vessel Model: 46' Grand Banks CL
Join Date: May 2019
Posts: 43
Inverter in Engine Room

I have '89 Grand Banks. Original inverter was in the engine room (3208's). No problem. Have replaced it in same location....no problem.
tdomenech is offline   Reply With Quote
Old 10-08-2021, 02:28 PM   #20
Veteran Member
 
Patrick4002's Avatar
 
City: oostende
Vessel Name: Lady Penelope
Vessel Model: Trader 54 sunliner
Join Date: Nov 2019
Posts: 41
invertor in the engine room

Hello i had a 5kw victron invertor in the engine room, it was no problem so long we didt make a longer trip, during travel the engine room got 40gr C. but when we stoped the temp rise to 60 gr C.
then the invertors reduse the max output to 25% or shut down completly

the just stop working, when the engine room was cool again the started back working

So i replaced the invertor in the next room and no problem anny more.

If you have big engines (in size) the heat comes when you stop them the block have 70 or 80gr C and there is no extra airflow in the engine room, so it starts heating up.

measure the temp in your engine room , so you now if it could be a problem

Best regards,
Patrick

ps on my current boat i changed one shower room to elektrical room so all heavy electronic equipment can stay cool, i also put a temp controled fan to get rid af the warm air in the room
Patrick4002 is offline   Reply With Quote
Reply

Thread Tools Search this Thread
Search this Thread:

Advanced Search
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


» Trawler Port Captains
Port Captains are TF volunteers who can serve as local guides or assist with local arrangements and information. Search below to locate Port Captains near your destination. To learn more about this program read here: TF Port Captain Program





All times are GMT -5. The time now is 04:18 AM.


Powered by vBulletin® Version 3.8.8 Beta 4
Copyright ©2000 - 2021, vBulletin Solutions, Inc.
Search Engine Optimization by vBSEO 3.6.0
Copyright 2006 - 2012