Battery chargers won't work on genset, work fine on SP

My boat suddenly has a strange issue. Both my Inverter (Xantrex SW3012) and my battery charger (Promariner 1250P) will not charge my batteries on 1992 Cummins Onan 8kw diesel genset power.



Every other 120V system on the boat works fine on genset power and both chargers work perfectly on shore power. The genset puts out a steady 118.3VAC (plus or minus .1V measured with a DMM using MIN and MAX function) at 61.25 Hz at the furthest outlet from the generator on the boat. An analog volt meter does not display any voltage fluctuations. The genset is running smoothly and works perfectly under heavy load (water heater and all three AC units running). I have not looked at the waveform yet with an oscilloscope, but that's the next step.


Any thoughts or ideas would be appreciated.


I called Xantrex tech support and they assured me that the inverter only looks at voltage, waveform, and frequency to qualify AC input power. It does not care about bonding, floating grounds, stray current, or any common issues like that one may find on a boat.


My gut says the genset os putting out a funky waveform that none of my other 120V devices care about or monitor. The genset has approximately 1240 hours.
__________________
Advertisement

Mischief Managed is offline   Reply With Quote
Old 07-09-2020, 06:55 AM   #2
Guru
 
City: Rochester, NY
Country: USA
Vessel Name: Hour Glass
Vessel Model: Chris Craft Catalina 381
Join Date: Aug 2019
Posts: 1,833
Check the brushes on the generator head and anything else that's mentioned in the manual and would be easy to check. Also, was that 61.25hz at no load, some load, or?
__________________

rslifkin is offline   Reply With Quote
Old 07-09-2020, 07:04 AM   #3
Senior Member
 
Mischief Managed's Avatar
 
City: Raymond NH
Country: USA
Vessel Name: Mischief Managed II
Vessel Model: 1992 Tollycraft 44 CPMY
Join Date: Oct 2018
Posts: 278
Quote:
Originally Posted by rslifkin View Post
Check the brushes on the generator head and anything else that's mentioned in the manual and would be easy to check. Also, was that 61.25hz at no load, some load, or?

Thanks, 61.25 Hz was with no load. I will check again under load, but I am certain it will be well within normal. Portable handheld oscilloscope is on the way; always wanted one and this is as good an excuse as any to add one to my tool kit.
Mischief Managed is offline   Reply With Quote
Old 07-09-2020, 07:06 AM   #4
Guru
 
City: Rochester, NY
Country: USA
Vessel Name: Hour Glass
Vessel Model: Chris Craft Catalina 381
Join Date: Aug 2019
Posts: 1,833
Definitely re-check with as much load as you can manage. Ideally, you'll be no more than 62 hz at no load, no less than 58 at full load. 63 - 57 is the outer end of the acceptable range.
rslifkin is offline   Reply With Quote
Old 07-09-2020, 07:13 AM   #5
Guru
 
fryedaze's Avatar
 
City: Solomons Island Md
Country: USA
Vessel Name: Fryedaze
Vessel Model: MC 42 (Overseas Co) Monk 42
Join Date: Sep 2011
Posts: 1,423
If the genset has an alternator it could be charging at a higher voltage than the battery charger causing the charger to back off.
__________________
Dave Frye
Fryedaze, MC 42 (Monk 42') 1989 Overseas Co
https://mvfryedaze.blogspot.com/
fryedaze is offline   Reply With Quote
Old 07-09-2020, 07:23 AM   #6
Guru
 
ranger42c's Avatar
 
City: Maryland
Country: USA
Vessel Model: 42' Sportfish
Join Date: Aug 2013
Posts: 5,216
Quote:
Originally Posted by Mischief Managed View Post
My boat suddenly has a strange issue. Both my Inverter (Xantrex SW3012) and my battery charger (Promariner 1250P) will not charge my batteries on 1992 Cummins Onan 8kw diesel genset power.

Is this a recent change?

If not... is the 1250P actually hooked up to charge 3 banks? (One being th genset battery?)

Is the 1250P properly charging other banks at the same time?

Is the generator's alternator charging the genset battery?

If so, is the genset battery fully charged, therefore not showing much current from the 1250P?

-Chris
__________________
South River, Chesapeake Bay
ranger42c is offline   Reply With Quote
Old 07-09-2020, 07:51 AM   #7
Senior Member
 
Mischief Managed's Avatar
 
City: Raymond NH
Country: USA
Vessel Name: Mischief Managed II
Vessel Model: 1992 Tollycraft 44 CPMY
Join Date: Oct 2018
Posts: 278
Quote:
Originally Posted by ranger42c View Post
Is this a recent change?

If not... is the 1250P actually hooked up to charge 3 banks? (One being th genset battery?)

Is the 1250P properly charging other banks at the same time?

Is the generator's alternator charging the genset battery?

If so, is the genset battery fully charged, therefore not showing much current from the 1250P?

-Chris

The 1250P does not charge the genset start battery and never has. It will eventually, but right now it charges the main starting battery, the house GC battery bank, and the Mathers Micro Controller (shifter/throttles) GC battery bank.



The only normal charging for the genset battery is the generator alternator and it's never been a problem. My boat has a paralleling switch so that I can start the genset from the house bank and I use that once a month over the Winter to combine them for charging via the 1250P (which is also only used once a month in the Winter until all batteries are in float).



I do not think the genset starting battery can have anything to do with this. Even if the batteries are all fully charged, the inverter and 1250P will still turn on and simply go to float. In my situation, they will not turn on at all. The inverter just stays in inverter mode and the 1250P goes right into fault mode. As soon as connected to shore power, they act normally.
Mischief Managed is offline   Reply With Quote
Old 07-09-2020, 08:55 AM   #8
Senior Member
 
Mischief Managed's Avatar
 
City: Raymond NH
Country: USA
Vessel Name: Mischief Managed II
Vessel Model: 1992 Tollycraft 44 CPMY
Join Date: Oct 2018
Posts: 278
Quote:
Originally Posted by ranger42c View Post
Is this a recent change?

There have been no changes at all in wiring since it worked normally and now. It started on Sunday morning when I ran the genset to charge the batteries and do some cooking after an overnight at anchor. Fortunately, the FLA house batteries were still at 12.4V (75ish% SOC) so the alternators had no trouble topping them up on the 6 hour cruise back to the marina. The genset worked fine for cooking and coffee.
Mischief Managed is offline   Reply With Quote
Old 07-09-2020, 09:02 AM   #9
Guru
 
kchace's Avatar
 
City: Brookline, NH
Country: USA
Vessel Name: Blue Heaven
Vessel Model: Albin 43 classic double cabin, twin 135 Lehmans
Join Date: Sep 2013
Posts: 1,878
I assume the inputs to the inverter and charger are separate? If so, it’s unlikely either device is at fault. Is it possible you lost a leg that feeds both, perhaps through a switch or breaker?

I have a scope I can bring to the boat Monday if you’d like to borrow it.

Ken
kchace is online now   Reply With Quote
Old 07-09-2020, 09:04 AM   #10
Guru
 
tiltrider1's Avatar
 
City: Seattle
Country: USA
Vessel Name: AZZURRA
Vessel Model: Ocean Alexander 54
Join Date: Aug 2017
Posts: 1,945
I am going to suggest the obvious. Under generator did you measure voltage at the inverter Or battery charger. I’m just wondering if there is some way the power is not getting to the inverter. This is a long shot but I couldn’t tell if it had been ruled out.
tiltrider1 is offline   Reply With Quote
Old 07-09-2020, 09:24 AM   #11
Guru
 
ranger42c's Avatar
 
City: Maryland
Country: USA
Vessel Model: 42' Sportfish
Join Date: Aug 2013
Posts: 5,216
Quote:
Originally Posted by Mischief Managed View Post
The 1250P does not charge the genset start battery and never has. It will eventually, but right now it charges the main starting battery, the house GC battery bank, and the Mathers Micro Controller (shifter/throttles) GC battery bank.

The only normal charging for the genset battery is the generator alternator and it's never been a problem.

Quote:
Originally Posted by Mischief Managed View Post
There have been no changes at all in wiring since it worked normally and now. It started on Sunday morning when I ran the genset to charge the batteries and do some cooking after an overnight at anchor. Fortunately, the FLA house batteries were still at 12.4V (75ish% SOC) so the alternators had no trouble topping them up on the 6 hour cruise back to the marina. The genset worked fine for cooking and coffee.

I think I misunderstood; thought you meant the 1250P wasn't charging ONLY the genset battery.

Instead, you mean it's not charging any battery when being powered by the genset, yes?

-Chris
__________________
South River, Chesapeake Bay
ranger42c is offline   Reply With Quote
Old 07-09-2020, 09:44 AM   #12
Senior Member
 
Mischief Managed's Avatar
 
City: Raymond NH
Country: USA
Vessel Name: Mischief Managed II
Vessel Model: 1992 Tollycraft 44 CPMY
Join Date: Oct 2018
Posts: 278
Quote:
Originally Posted by ranger42c View Post
I think I misunderstood; thought you meant the 1250P wasn't charging ONLY the genset battery.

Instead, you mean it's not charging any battery when being powered by the genset, yes?

-Chris

That is correct. Both the inverter and 1250P seem to need to qualify the AC input before they will activate charging mode and neither of them will do so, so there is no charging at all, except for the alternator on the gen set charging the genset starting battery.
Mischief Managed is offline   Reply With Quote
Old 07-09-2020, 09:46 AM   #13
Senior Member
 
Mischief Managed's Avatar
 
City: Raymond NH
Country: USA
Vessel Name: Mischief Managed II
Vessel Model: 1992 Tollycraft 44 CPMY
Join Date: Oct 2018
Posts: 278
Quote:
Originally Posted by tiltrider1 View Post
I am going to suggest the obvious. Under generator did you measure voltage at the inverter Or battery charger. Iím just wondering if there is some way the power is not getting to the inverter. This is a long shot but I couldnít tell if it had been ruled out.

I did not, only because it's a pain and they both work fine on shore power, so know the wiring from the AC breaker panel to the inverter and to the charger has to be OK.
Mischief Managed is offline   Reply With Quote
Old 07-09-2020, 09:53 AM   #14
Senior Member
 
Mischief Managed's Avatar
 
City: Raymond NH
Country: USA
Vessel Name: Mischief Managed II
Vessel Model: 1992 Tollycraft 44 CPMY
Join Date: Oct 2018
Posts: 278
Quote:
Originally Posted by kchace View Post
I assume the inputs to the inverter and charger are separate? If so, itís unlikely either device is at fault. Is it possible you lost a leg that feeds both, perhaps through a switch or breaker?

I have a scope I can bring to the boat Monday if youíd like to borrow it.

Ken

The inputs to both devices are indeed separate and are also on opposite legs in the AC panel. FWIW, the previous owner did a good job keeping the two charger circuits as separate and redundant as possible. I normally just run one charger but now I can't run any...



I should see if the 1250P will run on the sine wave output of the Inverter, not because it would solve my problem, just to see if the sine wave output is truly clean, since it seems to picky...
Mischief Managed is offline   Reply With Quote
Old 07-09-2020, 10:21 AM   #15
DDW
Guru
 
City: San Francisco
Country: USA
Join Date: Apr 2018
Posts: 1,233
Small gensets can have really horrible wave forms, many inverter type chargers will operate at reduced capacity or not at all on them. I don't have any idea why it would have changed, but looking at it with the o'scope is a good plan. The voltage output should be 110 - 120V RMS, so the peak waveform should be around 165V. If your meter was really measuring peak-to-peak, your voltage is low.
DDW is offline   Reply With Quote
Old 07-09-2020, 10:42 AM   #16
Guru
 
City: Carefree, Arizona
Country: usa
Vessel Name: sunchaser V
Vessel Model: DeFever 48
Join Date: Apr 2008
Posts: 8,740
MM
Unplug the Pro mariner and see if inverter charger does any better. Can you then bypass the inverter charger to see if PM then works better?

Do you have a BMK for the house bank? They are great tell alls if hooked up correctly. Also consider a dead battery cell somewhere. But, given it all works fine on shore power it points to a genset sending a bad wave form. 30+ years degrades electrical components just when sitting.
sunchaser is offline   Reply With Quote
Old 07-09-2020, 01:42 PM   #17
TF Site Team
 
Bacchus's Avatar
 
City: Seneca Lake NY
Country: US
Vessel Name: Bacchus
Vessel Model: MS 34 HT Trawler
Join Date: Nov 2014
Posts: 3,871
Quote:
Originally Posted by ranger42c View Post
Is this a recent change?

If not... is the 1250P actually hooked up to charge 3 banks? (One being th genset battery?)

Is the 1250P properly charging other banks at the same time?

Is the generator's alternator charging the genset battery?

If so, is the genset battery fully charged, therefore not showing much current from the 1250P?

-Chris
This raises a related question for me but I'll that a separate thread re Multi Bank Charger Operation to avoid hijacking this interesting thread.
__________________
Don
2008 MS 34 HT Trawler
"Bacchus"
Bacchus is offline   Reply With Quote
Old 07-09-2020, 03:13 PM   #18
Guru
 
twistedtree's Avatar
 
City: Gloucester, MA
Country: USA
Join Date: Jan 2013
Posts: 5,697
Have you metered the input voltage right at the terminals to the two devices?


Also, I think the SW "Meters" menu will let you see what it's seeing at the input.
__________________
MVTanglewood.com
twistedtree is offline   Reply With Quote
Old 07-09-2020, 03:25 PM   #19
Guru
 
kchace's Avatar
 
City: Brookline, NH
Country: USA
Vessel Name: Blue Heaven
Vessel Model: Albin 43 classic double cabin, twin 135 Lehmans
Join Date: Sep 2013
Posts: 1,878
Quote:
Originally Posted by Mischief Managed View Post
Portable handheld oscilloscope is on the way; always wanted one and this is as good an excuse as any to add one to my tool kit.

That's awesome. Now you have me thinking, I keep a lot of tools and spares on board but even *I* don't carry one of those! Should I? (I already own one)

Ken
kchace is online now   Reply With Quote
Old 07-09-2020, 05:29 PM   #20
Senior Member
 
City: St. Petersburg
Country: USA
Join Date: Oct 2007
Posts: 158
Just to be sure, recommend you check the ACIn settings on the SCP. These units will accept 85VAC to 135VAC and 45 to 70Hz. It is possible that the acceptance band was tightened for this installation and the genset freq or voltage has wandered out of the tighter band.
__________________

__________________
Charlie Johnson
ABYC Master Technician
CharlieJ is offline   Reply With Quote
Reply

Thread Tools Search this Thread
Search this Thread:

Advanced Search
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off





All times are GMT -5. The time now is 06:38 PM.


Powered by vBulletin® Version 3.8.8 Beta 4
Copyright ©2000 - 2020, vBulletin Solutions, Inc.
Search Engine Optimization by vBSEO 3.6.0
Copyright 2006 - 2012
×