Another power plug mishap.....

Well, it was bound to happen. In 30 years of boating, I have never had a power plug issue, until this weekend. I was overdue I guess. All we had on was one 12k btu Heat/AC unit and a 1500w bilge heater on that side. Ran all day just fine. Went in for dinner and came out to no power. This is what I found. Nice. Normally two heat/AC units would be on that side, plus microwave and one of the water heaters (plus battery chargers, plugs, etc).



Bought a full set of SmartPlugs to replace both connectors on both sides of the boat and on the cables. I have four total power input plug areas on the boat.


I was lucky. This could have been bad.
Attached Thumbnails
Click image for larger version

Name:	20200224_150806_resized.jpg
Views:	114
Size:	63.2 KB
ID:	99724   Click image for larger version

Name:	20200224_150845_resized.jpg
Views:	111
Size:	75.3 KB
ID:	99725   Click image for larger version

Name:	20200223_141054_resized.jpg
Views:	124
Size:	107.3 KB
ID:	99726  
__________________
Advertisement

__________________
"Everything on your boat is broken.... You just don't know it yet."
Redhook98 is offline   Reply With Quote
Old 02-24-2020, 05:21 PM   #2
Guru
 
City: Rochester, NY
Country: USA
Vessel Name: Hour Glass
Vessel Model: Chris Craft Catalina 381
Join Date: Aug 2019
Posts: 1,100
That looks like a 30A plug. Those things are total pieces of crap IMO. A 12k A/C unit on heat cycle plus a 1500w heater should be about 21 amps of load, so not overloaded. Anything over 24 amps on a 30A (80% rule) on a continuous basis would be considered overloaded, however. Short bursts up to 30A are fine though.

Personally, I'd say all inputs on any boat should be either Smartplugs or 50A twist locks. Personally, I prefer 50A shore power inlets in general as you get to use the much more robust 50A connector on the shore end unless they only have 30s available (and then you use an adapter). 50A lines are heavy to carry, but not much worse than 2x 30A (which is common). And IMO, the more robust connectors are worth it.
__________________

rslifkin is offline   Reply With Quote
Old 02-24-2020, 05:27 PM   #3
Guru
 
Comodave's Avatar
 
City: Au Gres, MI
Country: US
Vessel Name: Never Say Never
Vessel Model: President 41 DC
Join Date: Jul 2015
Posts: 6,845
Yes, you are very lucky that you caught it when you did. It could have happened overnight when you were sleeping.

We put Smart Plugs on our boat 2 years ago and have not had any issues since. I agree that about 24 amps is all you want to draw for any period of time on the 5-L30 plugs. Unfortunately when people see that it is rated for 30 amps, they think that 30 is ok all the time. The 5-L30 has very little contact area for 30 amps.
__________________
Boat Nut:
If you are one there is no explanation necessary.
If you arenít one, there is no explanation possible.
Comodave is offline   Reply With Quote
Old 02-24-2020, 06:33 PM   #4
Guru
 
psneeld's Avatar
 
City: AICW
Country: USA
Vessel Name: Freedom
Vessel Model: Albin 40
Join Date: Oct 2011
Posts: 20,744
I have to toss a red flag...does anyone have a reference that says a 30A boat circuit is not rated for 30A continuous?


And don't reference NEC stuff...unless there is a direct connection to boat shore power supplies.
psneeld is offline   Reply With Quote
Old 02-24-2020, 06:53 PM   #5
Guru
 
tiltrider1's Avatar
 
City: Seattle
Country: USA
Vessel Name: AZZURRA
Vessel Model: Ocean Alexander 54
Join Date: Aug 2017
Posts: 1,653
30 amp plugs can not handle 30 amp continuous. In fact anything over 24 amps will eventually end up like the pictures above. It doesn’t take much corrosion to cause excess heat. As the heat builds the female socket looses its grip, which creates more resistance which creates more heat which can lead to a boat on fire. The above pictures were close, lucky there is still a boat. If you are going to continue using these old style 30A plugs you need to inspect them every month. I bet if the above plug had been inspected a month earlier you would have seen discoloring around the positive prong on the male plug.

Boats that need to pull 30A continuous need to switch to 50A plugs.

Can’t answer Psneeld about a reference to 30A plugs being rated or not rated for 30A continuous. I can only reference people to a long list of boat fires that started at a 30A plug.
tiltrider1 is online now   Reply With Quote
Old 02-24-2020, 07:00 PM   #6
Guru
 
Lou_tribal's Avatar
 
City: Quebec
Country: Canada
Vessel Name: Bleuvet
Vessel Model: Custom Built
Join Date: Jan 2016
Posts: 3,715
Quote:
Originally Posted by rslifkin View Post
Personally, I'd say all inputs on any boat should be either Smartplugs or 50A twist locks. Personally, I prefer 50A shore power inlets in general as you get to use the much more robust 50A connector on the shore end unless they only have 30s available (and then you use an adapter). 50A lines are heavy to carry, but not much worse than 2x 30A (which is common). And IMO, the more robust connectors are worth it.
Why?
I have a 30 amps and that is far enough for what I need knowing that I never have more than 15 to 20amps load at any time. This all depends on how much energy hungry one is.

L
Lou_tribal is offline   Reply With Quote
Old 02-24-2020, 07:11 PM   #7
Guru
 
psneeld's Avatar
 
City: AICW
Country: USA
Vessel Name: Freedom
Vessel Model: Albin 40
Join Date: Oct 2011
Posts: 20,744
And 100% of every failure I have seen was probably corrosion/bad connection in the plugs, not because of their ratings...not the wires unless damaged and not the CBs.


Proof is worth a 1000 posts of dock talk....anyone have actual PROOF or some reliable recommendation?


If the setup is not foolproof...then what IS the acceptable continuous rating...as corrosion, looseness,etc could do the same at many different amp draws...why not limit them to 15A as safe?
psneeld is offline   Reply With Quote
Old 02-24-2020, 07:29 PM   #8
Guru
 
City: Rochester, NY
Country: USA
Vessel Name: Hour Glass
Vessel Model: Chris Craft Catalina 381
Join Date: Aug 2019
Posts: 1,100
Quote:
Originally Posted by Lou_tribal View Post
Why?
I have a 30 amps and that is far enough for what I need knowing that I never have more than 15 to 20amps load at any time. This all depends on how much energy hungry one is.

L
The 50a plugs have more contact area. And with the outer shell, they lock in much more securely, so there's less risk of the plug shifting and causing bad contact.

For the 80 percent rule, look at the circuit breaker specs. Most say 80 percent is the continuous rating. Most non marine electrical codes say the same. As a rule, that's the safe option unless the breakers and connectors are explicitly rated for 100 percent continuous load. Wiring is easy to size for the desired continuous load, so that part isn't much of a concern.
rslifkin is offline   Reply With Quote
Old 02-24-2020, 07:31 PM   #9
Guru
 
psneeld's Avatar
 
City: AICW
Country: USA
Vessel Name: Freedom
Vessel Model: Albin 40
Join Date: Oct 2011
Posts: 20,744
Agree the Smart plug for 30s and either for 50s is a quantum leap in terms of plug security.
psneeld is offline   Reply With Quote
Old 02-24-2020, 07:40 PM   #10
Senior Member
 
Capt. Jon's Avatar
 
City: Alabama
Country: USA
Vessel Name: Waypoint
Vessel Model: Californian 48' CPMY
Join Date: Dec 2013
Posts: 413
Appears psnead is correct. Nowhere in the installation literature does it say that the 30 amp marine cable cannot carry its rated load continuously. it actually says just the opposite. Below is a link to the installation paperwork. Refer to section 3. Its a short read and very informative.


https://hubbellcdn.com/installationm...NSTALLINST.pdf
__________________
Jon
------------------------------------------------
Waypoint's are abstract, often having no obvious relationship to any distinctive features of the real world.
Capt. Jon is offline   Reply With Quote
Old 02-24-2020, 08:04 PM   #11
Guru
 
syjos's Avatar
 
City: Gig Harbor
Country: USA
Vessel Name: Sandpiper
Vessel Model: Bluewater 40 Pilothouse Trawler
Join Date: Nov 2012
Posts: 1,280
I run 30 amps from shore power a lot and have never had a burnt or melted plug. No furnace so we run electric heaters during the winter.

I examine and clean the prongs with electrical contact cleaner monthly. I also spray the cleaner into the female cord plug openings while holding the prong with the openings facing down to drain. A Scotchbrite pad is sometimes used for thorough cleaning of the male prongs.

The wiring from the shore inlet to the breaker and panel is #8 instead of the standard #10. In order to mitigate any possibility of the area around the inlet getting hot or burning, the inlet is mounted on a flush mount steel electrical box that is enclosed on the back side to contain any flames.

During the winter when we are away for couple months and heater use is high, I use a shore power cord with three ring terminals instead of the female plug and direct connect it to a terminal block inside the electrical box.

I'm in the process of installing a temperature sensor on the back side of the shore inlet wired to a solenoid that will open when the temperature gets to a certain point. I have to experiment and see what the high temperature open point will be.

The first generation Smart Plug had the safety feature of opening the circuit when the inlet became hot. That feature was discontinued since the breaker they used would reenergize automaticaly when the temperature dropped introducing a safety hazard.

The lack of a high temp cutoff on the newer Smart Plugs sort of reduces the safety aspects. It still has positive clamping and more contact surface area than standard plugs. But the contact area on Smart Plug still needs to be kept clean.
syjos is online now   Reply With Quote
Old 02-24-2020, 08:32 PM   #12
Guru
 
Comodave's Avatar
 
City: Au Gres, MI
Country: US
Vessel Name: Never Say Never
Vessel Model: President 41 DC
Join Date: Jul 2015
Posts: 6,845
Check CMS marine web site. He did an article about it. The contact area on twist lock connector is incredibly small.
__________________
Boat Nut:
If you are one there is no explanation necessary.
If you arenít one, there is no explanation possible.
Comodave is offline   Reply With Quote
Old 02-24-2020, 09:01 PM   #13
Guru
 
psneeld's Avatar
 
City: AICW
Country: USA
Vessel Name: Freedom
Vessel Model: Albin 40
Join Date: Oct 2011
Posts: 20,744
But they ARE adequate...like the Hubble link says...it's not the materials that are the problem...its the connection, corrosion, etc....


And thus why 30A standard are the most likely to overheat...because they are not easy to keep tight for a myriad of reasons.
psneeld is offline   Reply With Quote
Old 02-24-2020, 09:24 PM   #14
Guru
 
boathealer's Avatar
 
City: Out Cruisin'
Country: US
Vessel Name: SCOUT
Vessel Model: Great Harbour N37
Join Date: Aug 2017
Posts: 707
Agree with psneeld. I have never seen one of these melted contacts (including one of my own!) that was NOT due to corrosion. As I wrote in another post....

Corrosion on contacts equals resistance. Resistance on contacts means voltage drop and more current being drawn by onboard devices. Higher current through a resistance equals heat. Lots of heat equals melted plug. Guess which terminal had the corrosion?

Keep those shore power contacts CLEAN (both sides). Dielectric grease does help keep corrosion at bay.
__________________
--
Ray
m/v SCOUT Web Site
m/v SCOUT Projects Page
boathealer is online now   Reply With Quote
Old 02-25-2020, 06:23 AM   #15
FF
Guru
 
FF's Avatar
 
Join Date: Oct 2007
Posts: 20,267
By switching to the 240V 50A range plugs the copper contact area is increased 400% or more.

Yet to see the all electric live aboard folks melt one. Any Big Box store , priced right.

They are not "water proof" , never seems to matter.
FF is offline   Reply With Quote
Old 02-25-2020, 07:57 AM   #16
Guru
 
syjos's Avatar
 
City: Gig Harbor
Country: USA
Vessel Name: Sandpiper
Vessel Model: Bluewater 40 Pilothouse Trawler
Join Date: Nov 2012
Posts: 1,280
Quote:
Originally Posted by psneeld View Post
But they ARE adequate...like the Hubble link says...it's not the materials that are the problem...its the connection, corrosion, etc....


And thus why 30A standard are the most likely to overheat...because they are not easy to keep tight for a myriad of reasons.
I agree that dirty contacts and corrosion is the cause of burnt inlet/outlet.

The inlet and the female plug should be cleaned and inspected regularly and at the first sign of corrosion or overheating, replaced.

If the locking ring doesn't tighten the plug, replace the ring.

Dielectric grease will reduce corrosion but it is not conductive.

I use MG Chemicals 846 Carbon Conductive Grease. It is a carbon-filled, electrically conductive grease. It lubricates, reduces contact resistance, repels moisture and inhibits corrosion.
syjos is online now   Reply With Quote
Old 02-25-2020, 07:58 AM   #17
Guru
 
City: Carefree, Arizona
Country: usa
Vessel Name: sunchaser V
Vessel Model: DeFever 48
Join Date: Apr 2008
Posts: 8,411
I have to agree with PSN and others on this. The 30 amp cord "scorched" issues I've seen are relegated to corrosion, abuse or old tired connectors. All bets are off when breakers on either side don't trip properly.

An all too common, and ignored, occurrence is running electric heaters and thinking that is the load. Then in the dark of night the wind blows down a tree somewhere kicking off power for several hours. Once power restored your big inverter charger kicks on overloading the already challenged cord set. Which is why I try to stay at less than 1/2 of 30 amps with electric heat during the winter.
sunchaser is online now   Reply With Quote
Old 02-25-2020, 10:00 AM   #18
Guru
 
Codger2's Avatar
 
City: San Diego
Country: US
Vessel Name: "Sandpiper"
Vessel Model: 2006 42' Ocean Alexander Sedan
Join Date: Oct 2007
Posts: 6,085
Quote:
Originally Posted by psneeld View Post
Agree the Smart plug for 30s and either for 50s is a quantum leap in terms of plug security.
I switched to the SmartPlugs when they first came out and have had both 30 & 50 amp plugs.
Attached Thumbnails
Click image for larger version

Name:	SmartPlug.jpg
Views:	70
Size:	104.5 KB
ID:	99761  
__________________
Codger 1941.. Constant pursuit of the ultimate SoCal Cruising boat.
Codger2 is online now   Reply With Quote
Old 02-25-2020, 10:10 AM   #19
Veteran Member
 
Redhook98's Avatar
 
City: Colonial Beach, VA
Country: US
Vessel Name: Tatoosh
Join Date: Jun 2019
Posts: 82
The funny thing is I do maintenance all the time. My years in the Navy has taught me to be pretty anal on this point. It was a fairly new cord (about 5 months old), I used dielectric grease and the rings were seemingly tight. My Portuguese Bridge door opens onto those two power connectors and I am wondering if someone on a recent cruise had opened it a little carelessly and hit them. It's a heavy door. Either way, it was a bad connection and somehow that got worse. Luckily it burned itself out. New SmartPlugs and cables on the way.
__________________
"Everything on your boat is broken.... You just don't know it yet."
Redhook98 is offline   Reply With Quote
Old 02-25-2020, 10:15 AM   #20
Guru
 
Gulf Comanche's Avatar
 
City: Baton Rouge, Louisiana
Country: U.S.A.
Vessel Name: Old School
Vessel Model: 38' Trawler custom built by Hike Metal Products
Join Date: Dec 2007
Posts: 955
Had a similar almost disaster as shown in the OP’s pics. Switched to Smartplug and both ends run cool to the touch. But, pulling the female side from the boat is no picnic, I thought it was supposed to be easy.
__________________

Gulf Comanche is offline   Reply With Quote
Reply

Thread Tools Search this Thread
Search this Thread:

Advanced Search
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off





All times are GMT -5. The time now is 10:42 AM.


Powered by vBulletin® Version 3.8.8 Beta 4
Copyright ©2000 - 2020, vBulletin Solutions, Inc.
Search Engine Optimization by vBSEO 3.6.0
Copyright 2006 - 2012
×