Quote:
Originally Posted by LeoKa View Post
Take a look at this one. It handles two shore power connections, even at 50A. The price is around $600. From this one, the rest of the existing panels can be branched out.

https://www.go2marine.com/Paneltroni...ty=1&type=1240


I am just thinking out loud here. If this can take two 50A connections, all I need is two 50A receptacles and wiring. The description says that it can handle two individual hot and neutral bars. I suppose this will allow me to connect to either 30A or 50A pedestals. Unless I misunderstand the description.

That panel lets you select between two shore cords and a generator, but you can only use one at a time. There is no provision to combine anything.


You only have two choices:


1) Live with 30A/120V


2) Split up you power system into a 50A,120/240V split phase system. Then you can run off a 50A 120/240V shore outlet, or use a combiner to run off of two 30A 120V shore outlets. But if you have a generator you will need to consider how that fits, along with the isolation transformer. It's a big project.
__________________
MVTanglewood.com
twistedtree is offline   Reply With Quote
Old 11-22-2022, 05:32 AM   #22
Guru
 
City: Winthrop
Vessel Model: Pacific Trawler 40
Join Date: Mar 2020
Posts: 879
Quote:
Originally Posted by ranger58sb View Post
Ask the marina to change your pedestal?

Could be simple. Might not even charge you, but if they do, might not be much.

-Chris
Yep! You would be using one socket rather than two.
__________________
Iggy
Iggy is offline   Reply With Quote
Old 11-22-2022, 05:37 AM   #23
Guru
 
twistedtree's Avatar
 
City: Vermont
Join Date: Jan 2013
Posts: 10,099
Quote:
Originally Posted by SteveK View Post
I was suggesting one of these to plug into the 50 amp cord

But I see you have single 30 amp pedestals

These are incredibly dangerous, and illegal to use in any jurisdiction that required NEC compliance, which is pretty much everywhere.


The only safe way to combine two 30A power sources into a 120/240 power source is with some form of intelligent switch. That's why the Marinco or Furrion version of these combiners cost $600 or more. They only connect power through to the 120/240V side if both 30A supplies are present, and only if they are out pf phase.


A hard wired adapter like the one in this listing are dangerous in two ways:


1) If the two 30A power sources are in phase, then you can overload the neutral. When the power sources are out of phase, as they should be, the neutral current is the difference between the two phases. When they are in phase, the neutral current is the SUM of the two phases, so can run at 60A without any breakers tripping. That's a good way to start a fire.


2) If you plug in one of the 30A ends, and there are 240V loads connected on the boat side, the exposed plug prongs of the second 30A end will be live/hot. That's a good way to get electrocuted.


Oh, and it wouldn't help the OP anyway because his boat takes 50A 120V, not 120/240V.
__________________
MVTanglewood.com
twistedtree is offline   Reply With Quote
Old 11-22-2022, 05:43 AM   #24
Guru
 
City: Winthrop
Vessel Model: Pacific Trawler 40
Join Date: Mar 2020
Posts: 879
Quote:
Originally Posted by twistedtree View Post
These are incredibly dangerous, and illegal to use in any jurisdiction that required NEC compliance, which is pretty much everywhere.


The only safe way to combine two 30A power sources into a 120/240 power source is with some form of intelligent switch. That's why the Marinco or Furrion version of these combiners cost $600 or more. They only connect power through to the 120/240V side if both 30A supplies are present, and only if they are out pf phase.


A hard wired adapter like the one in this listing are dangerous in two ways:


1) If the two 30A power sources are in phase, then you can overload the neutral. When the power sources are out of phase, as they should be, the neutral current is the difference between the two phases. When they are in phase, the neutral current is the SUM of the two phases, so can run at 60A without any breakers tripping. That's a good way to start a fire.


2) If you plug in one of the 30A ends, and there are 240V loads connected on the boat side, the exposed plug prongs of the second 30A end will be live/hot. That's a good way to get electrocuted.


Oh, and it wouldn't help the OP anyway because his boat takes 50A 120V, not 120/240V.
If "When the power sources are out of phase" than you would have 203V? Yes?
__________________
Iggy
Iggy is offline   Reply With Quote
Old 11-22-2022, 06:18 AM   #25
Guru
 
twistedtree's Avatar
 
City: Vermont
Join Date: Jan 2013
Posts: 10,099
Quote:
Originally Posted by Iggy View Post
If "When the power sources are out of phase" than you would have 203V? Yes?

In this context, out of phase would give you 240V across L1 and L2. In phase would give you 0V across L1 and L2. Is that what you are asking, or are you asking about 240V vs 208V?
__________________
MVTanglewood.com
twistedtree is offline   Reply With Quote
Old 11-22-2022, 06:18 AM   #26
TF Site Team
 
Bacchus's Avatar
 
City: Seneca Lake NY
Vessel Name: Bacchus
Vessel Model: MS 34 HT Trawler
Join Date: Nov 2014
Posts: 7,831
Leoka
Now I understand your situation and what is desired.
You would need to check the 30A receptacles but if same phasing one of these should do what you want.
https://www.amazon.com/Adapter-30A-1.../dp/B0013HRJVM
__________________
Don
2008 MS 34 HT Trawler
"Bacchus"
Bacchus is offline   Reply With Quote
Old 11-22-2022, 07:04 AM   #27
Guru
 
City: Winthrop
Vessel Model: Pacific Trawler 40
Join Date: Mar 2020
Posts: 879
Quote:
Originally Posted by twistedtree View Post
In this context, out of phase would give you 240V across L1 and L2. In phase would give you 0V across L1 and L2. Is that what you are asking, or are you asking about 240V vs 208V?
It my club the have 3 phase. I was thinking that if you came off the 2 hot wire you would 208. But one one hot to natural you would have 120V due to there out of phase. I think by 45 degrees. OK, over thinking it.
__________________
Iggy
Iggy is offline   Reply With Quote
Old 11-22-2022, 09:39 AM   #28
Senior Member
 
Scottwb96's Avatar
 
City: Burien
Vessel Name: Star Weird
Vessel Model: Camargue
Join Date: Apr 2019
Posts: 381
Was just going to say the same thing as Ranger... Just convert the 30a pedestal to 50a and not have to worry about plugs/adapters/cables... Shouldn't be more than $500 to change you out...
Scottwb96 is offline   Reply With Quote
Old 11-22-2022, 11:23 AM   #29
Guru
 
twistedtree's Avatar
 
City: Vermont
Join Date: Jan 2013
Posts: 10,099
Quote:
Originally Posted by Bacchus View Post
Leoka
Now I understand your situation and what is desired.
You would need to check the 30A receptacles but if same phasing one of these should do what you want.
https://www.amazon.com/Adapter-30A-1.../dp/B0013HRJVM

That appears to be a splitter, taking a 50A 120V shore outlet and splitting it into two 30A 120V sources. He wants to do the reverse, and you can't do it without violating countless wiring and safety codes
__________________
MVTanglewood.com
twistedtree is offline   Reply With Quote
Old 11-22-2022, 11:25 AM   #30
Guru
 
twistedtree's Avatar
 
City: Vermont
Join Date: Jan 2013
Posts: 10,099
Quote:
Originally Posted by Scottwb96 View Post
Was just going to say the same thing as Ranger... Just convert the 30a pedestal to 50a and not have to worry about plugs/adapters/cables... Shouldn't be more than $500 to change you out...

Good idea if the marina will allow it.
__________________
MVTanglewood.com
twistedtree is offline   Reply With Quote
Old 11-22-2022, 11:31 AM   #31
Guru
 
LeoKa's Avatar
 
City: Vancouver
Vessel Name: Ironsides
Vessel Model: 54' Bruce Roberts steel sailboat hull, coastal LRC, 220HP CAT 3306.
Join Date: Apr 2017
Posts: 1,137
Quote:
Originally Posted by ranger58sb View Post
Ask the marina to change your pedestal?



Could be simple. Might not even charge you, but if they do, might not be much.



-Chris


I did. They have no plans to do it.

Maybe I’ll ask how much it would be, if I pay for it?
Again, it is not life and death issue. I can manage as I am.
LeoKa is offline   Reply With Quote
Old 11-22-2022, 01:27 PM   #32
TF Site Team
 
Bacchus's Avatar
 
City: Seneca Lake NY
Vessel Name: Bacchus
Vessel Model: MS 34 HT Trawler
Join Date: Nov 2014
Posts: 7,831
Quote:
Originally Posted by twistedtree View Post
That appears to be a splitter, taking a 50A 120V shore outlet and splitting it into two 30A 120V sources. He wants to do the reverse, and you can't do it without violating countless wiring and safety codes
OK that might have been the wrong one but here is exactly what he is looking for -I believe unless I'm off again. This one does show the end contacts...
2 - 30A male to 50A female (3 wire - 120V)

https://www.amazon.com/Parkworld-Com...-8756842?psc=1
__________________
Don
2008 MS 34 HT Trawler
"Bacchus"
Bacchus is offline   Reply With Quote
Old 11-22-2022, 03:04 PM   #33
Guru
 
twistedtree's Avatar
 
City: Vermont
Join Date: Jan 2013
Posts: 10,099
Quote:
Originally Posted by Bacchus View Post
OK that might have been the wrong one but here is exactly what he is looking for -I believe unless I'm off again. This one does show the end contacts...
2 - 30A male to 50A female (3 wire - 120V)

https://www.amazon.com/Parkworld-Com...-8756842?psc=1

That combines two 30A 120V outlets into a single 50A 120/240V outlet. It won't get him any more 120V power, and it's the adapter that's really dangerous.
__________________
MVTanglewood.com
twistedtree is offline   Reply With Quote
Old 11-22-2022, 04:04 PM   #34
TF Site Team
 
Bacchus's Avatar
 
City: Seneca Lake NY
Vessel Name: Bacchus
Vessel Model: MS 34 HT Trawler
Join Date: Nov 2014
Posts: 7,831
Agree...
I'm wrong again! 0 for 3 and a strike out
Sorry for the confusion
__________________
Don
2008 MS 34 HT Trawler
"Bacchus"
Bacchus is offline   Reply With Quote
Old 11-22-2022, 04:53 PM   #35
Guru
 
tiltrider1's Avatar
 
City: Seattle
Vessel Name: AZZURRA
Vessel Model: Ocean Alexander 54
Join Date: Aug 2017
Posts: 4,312
As I mentioned in post #19. His best option is probably to run a second independent 30a line into the boat just for some heat.

It can be done very inexpensively as long as it’s kept independent of the primary system. He could put the heaters on a rotary switch that allows them to either source the 50a or 30a shore power. This would give him the best of both worlds.

The second line would not be on an isolation transformer. However, with just the heaters on the second line you could avoid the need to combine the grounds between this system and the rest of the boat. If you added a rotary switch make sure the grounds get switched as well.
tiltrider1 is online now   Reply With Quote
Old 11-22-2022, 04:54 PM   #36
Guru
 
LeoKa's Avatar
 
City: Vancouver
Vessel Name: Ironsides
Vessel Model: 54' Bruce Roberts steel sailboat hull, coastal LRC, 220HP CAT 3306.
Join Date: Apr 2017
Posts: 1,137
Quote:
Originally Posted by Scottwb96 View Post
Was just going to say the same thing as Ranger... Just convert the 30a pedestal to 50a and not have to worry about plugs/adapters/cables... Shouldn't be more than $500 to change you out...


I don’t know. If I spend my money, I’d rather improve my boat and not the marina. Besides, the marina is in the process of changing ownership, so nobody knows what is coming.
I am seriously considering the upgrade on my boat to two circuits, instead of one.
LeoKa is offline   Reply With Quote
Old 11-22-2022, 05:03 PM   #37
Guru
 
LeoKa's Avatar
 
City: Vancouver
Vessel Name: Ironsides
Vessel Model: 54' Bruce Roberts steel sailboat hull, coastal LRC, 220HP CAT 3306.
Join Date: Apr 2017
Posts: 1,137
[QUOTE=twistedtree;1137137]That panel lets you select between two shore cords and a generator, but you can only use one at a time. There is no provision to combine anything.


You only have two choices:







What if there is 3rd choice? More money, but my boat will benefit from it.

I spoke to Paneltronics and I have the answers. If I buy their panel for dual shorepower, I can connect two individual pedestals. This will require me to do some work on the existing switch board and split the present AC sub panel into two. This way, each connection on the Paneltronics can supply a partial AC branch. Optional 50A breakers can be chosen at ordering. I will need to buy and install another 50A/125V inlet and do the wirings.
This setup should not violate any codes and will give me more flexibility.
The panel in question also has a parallel switch, which allows to share one connection between the two AC branches, if only one connection is available from the dock.

What do you think?
LeoKa is offline   Reply With Quote
Old 11-22-2022, 05:14 PM   #38
Guru
 
LeoKa's Avatar
 
City: Vancouver
Vessel Name: Ironsides
Vessel Model: 54' Bruce Roberts steel sailboat hull, coastal LRC, 220HP CAT 3306.
Join Date: Apr 2017
Posts: 1,137
Quote:
Originally Posted by tiltrider1 View Post
As I mentioned in post #19. His best option is probably to run a second independent 30a line into the boat just for some.
The second line would not be on an isolation transformer. However, with just the heaters on the second line you could avoid.


Your suggestion is valid and it could be a solution. However, this is not just about the heaters. I have a water maker, portable ac, other appliances. Those draw enough to dim the lights, or flip the breakers, if multiple are on.
I am thinking long term. I might not be at the present marina forever, and flexibility or extra load options would be nice to have. You will never know when it is needed, and it would be more pricey to do upgrades like this in another country. Yes, it is not cheap to upgrade, but it can pay off sometimes in the future.
LeoKa is offline   Reply With Quote
Old 11-22-2022, 05:21 PM   #39
Guru
 
SteveK's Avatar
 
City: Gulf Islands, BC Canada
Vessel Name: Sea Sanctuary
Vessel Model: Bayliner 4588
Join Date: Jul 2019
Posts: 5,023
Quote:
Originally Posted by tiltrider1 View Post
As I mentioned in post #19. His best option is probably to run a second independent 30a line into the boat just for some heat.

It can be done very inexpensively as long as it’s kept independent of the primary system. He could put the heaters on a rotary switch that allows them to either source the 50a or 30a shore power. This would give him the best of both worlds.

The second line would not be on an isolation transformer. However, with just the heaters on the second line you could avoid the need to combine the grounds between this system and the rest of the boat. If you added a rotary switch make sure the grounds get switched as well.
Respectfully wish to ask does your suggestion pass ABYC.
You said the splitters that stayed outside the boat were against the rules, how possibly can a bypass of the isolation transformer panel and reverse polarity be acceptable.
__________________
SteveK
You only need one working engine. That is why I have two.
Sea Sanctuary-new to me 1992 Bayliner 4588
SteveK is online now   Reply With Quote
Old 11-22-2022, 05:35 PM   #40
Guru
 
twistedtree's Avatar
 
City: Vermont
Join Date: Jan 2013
Posts: 10,099
Quote:
Originally Posted by Bacchus View Post
Agree...
I'm wrong again! 0 for 3 and a strike out
Sorry for the confusion

No worries. None of the product descriptions for adapters make it easy, and ParkWorld selling a product that violates all North American electric codes doesn't help either.
__________________
MVTanglewood.com
twistedtree is offline   Reply With Quote
Reply

Thread Tools Search this Thread
Search this Thread:

Advanced Search
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


» Trawler Port Captains
Port Captains are TF volunteers who can serve as local guides or assist with local arrangements and information. Search below to locate Port Captains near your destination. To learn more about this program read here: TF Port Captain Program





All times are GMT -5. The time now is 12:02 AM.


Powered by vBulletin® Version 3.8.8 Beta 4
Copyright ©2000 - 2024, vBulletin Solutions, Inc.
Search Engine Optimization by vBSEO 3.6.0
Copyright 2006 - 2012