Hi all,

I'd like to set the wiring up so that my forward air conditioner can't run when either my stovetop or microwave/oven are in use.

In particular, I want to break the connection to the HVAC unit as soon as either device is turned on -- but delay by 5 or so minutes before turning it back on. This way, I don't short-cycle the HVAC unit as the thermostat turns the stove or oven on-and-off or as a human checks/stirs-and-resets the microwave.

I feel like others have solved this problem -- but the threads I was able to find didn't involve the time delay part.

Does anyone know of an appropriate relay to use?

Many thanks!

EDIT: I'd originally posted with one idea, but upon a more careful look at the spec sheet, I realized the time delay wouldn't work the way I want. I want the NC output to break immediately, but to delay coming back on. :-(
__________________
Advertisement

gkesden is offline   Reply With Quote
Old 06-27-2020, 07:16 PM   #2
Senior Member
 
KnotYet's Avatar
 
City: Los Angeles
Country: USA
Join Date: Feb 2020
Posts: 179
A medium current time delay relay from McMaster-Carr should do the trick.
They have a good selection and ship from various warehouses across the USA.
__________________

KnotYet is offline   Reply With Quote
Old 06-27-2020, 09:40 PM   #3
Guru
 
rgano's Avatar
 
City: Southport, Florida
Country: USA
Vessel Name: FROLIC
Vessel Model: Mainship 30 Pilot II since 2015. GB-42 1986-2015. Former Unlimited Tonnage Master
Join Date: Oct 2007
Posts: 1,700
Send a message via Skype™ to rgano
When I purchased my new dometic air conditioner a couple of years back, the dealer informed me that I should always turn it off via the air conditioner's control rather than the breaker because there are a number of subroutines which run in the electronics of the unit which need to shut down in an orderly fashion. The Micro-Air Easy Start in installed in this AC has a five minute delay built into the compressor start after a shutdown. I think a lot of AC units have compressor protection like that, but more expert opinion will soon chime in. IMHO, I would not attempt to install such a circuit as you discuss and would just handle the process manually.
__________________
Rich Gano
FROLIC (2005 MainShip 30 Pilot II)
Panama City area
rgano is offline   Reply With Quote
Old 06-27-2020, 10:38 PM   #4
Guru
 
City: Clearwater, FL
Country: United States
Vessel Name: Seas the Bay
Vessel Model: 1981 42' Hardin Europa
Join Date: Aug 2016
Posts: 964
rgano,

Thanks so much for the feedback!

And, as you know, you aren't telling any lies. My pump starts 5 seconds before the compressor and stops 5 seconds after.

It is just that, for right or for wrong, the post-shutdown 5-second delay is something I'm not super worried about. I don't think a critical amount of cooling happens in that time, especially for the 1-3 times/day, max, I cook.

For right or for wrong, the reality is that the HVAC panel for this unit is at the front of the boat, and the breaker panel is at the helm near the galley. So, the relay won't be doing any worse than I've done -- I've been shutting it off at the breaker for years. I have the same bad habit w.r.t. switching loads when transitioning between shore power and the genset and back. I suspect keeping up with my strainer baskets (or not) will more than make up for it over the long haul.

I am more concerned that I get the restart time delay right so that I don't end up with rapid start-stop-restart cycles that cause it to kick back on before the refrigerant gets to settle and pressures equalize. That'll eat the compressor really fast.

I guess if a bunch of people beat me with sticks on the thread, I can adjust my goal slightly. I really care about the compressor /starting/ while cooking. I can handle the running load. And, I can handle, be it barely, one compressor starting while cooking. But, cooking and having two compressors kick in at the same time puts me way over the top.

So, what I could do is put soft-start kits into both units and see where that gets me. It could easily mitigate the need to prevent the HVAC from starting while cooking -- and do it without disabling the HVAC.

That is probably an $800 solution, which would be excellent if I knew it would work. But, I'm not sure I trust the "specs". I'd hate to spend the $800, look at the current draw on my ammeter, and not be happy with the load in reality.

The other thing I could do is to wire it with feedback so that, if the unit is already running, it stays running, but if not, it won't start. I fear that going that route would take me into the "I know something about electrical circuits so I'll make a contraption" space. And, when I've seen folks start down that slope, it has been a slippery one, and not often consistent with the KISS principle that I try to follow to keep things reliable, low maintenance, and easily debugged. Regardless, even if only for the thought experiment, I'd still need the time delay relay in this case.

Thanks again!
gkesden is offline   Reply With Quote
Old 06-27-2020, 10:39 PM   #5
Guru
 
City: Clearwater, FL
Country: United States
Vessel Name: Seas the Bay
Vessel Model: 1981 42' Hardin Europa
Join Date: Aug 2016
Posts: 964
KnotYet,

I don't think I'm seeing one that would work. I'm probably missing it. Any recommendations?

Many thanks!
-Greg
gkesden is offline   Reply With Quote
Old 06-28-2020, 02:10 AM   #6
Moderator Emeritus
 
ksanders's Avatar
 
City: SEWARD ALASKA
Country: USA
Vessel Name: LISAS WAY
Vessel Model: BAYLINER 4788
Join Date: Feb 2011
Posts: 4,622
This is not as easy as a time delay relay.

Remember that your stove top and microwave oven have power to them all the time.

You only want to turn off the HVAC when the stovetop or the microwave are operating.

In order to make this happen you are going to have to sense power flow and have that turn off your HVAC.
__________________
Kevin Sanders
Bayliner 4788
Seward, Alaska
ksanders is offline   Reply With Quote
Old 06-28-2020, 02:15 AM   #7
Guru
 
City: Clearwater, FL
Country: United States
Vessel Name: Seas the Bay
Vessel Model: 1981 42' Hardin Europa
Join Date: Aug 2016
Posts: 964
Hey Kevin,

I totally get that. But, just as a for example, the neutral line doesn't normally have current flowing through it, but does when the device is operating.

I could also use a coil or hall effect triggered circuit. But....still need the relay.
gkesden is offline   Reply With Quote
Old 06-28-2020, 02:27 AM   #8
Moderator Emeritus
 
ksanders's Avatar
 
City: SEWARD ALASKA
Country: USA
Vessel Name: LISAS WAY
Vessel Model: BAYLINER 4788
Join Date: Feb 2011
Posts: 4,622
Quote:
Originally Posted by gkesden View Post
Hey Kevin,

I totally get that. But, just as a for example, the neutral line doesn't normally have current flowing through it, but does when the device is operating.

I could also use a coil or field effect triggered circuit. But....still need the relay.
Grainger sells a good selection of time delay relays with a variety of trigger voltages.

My opinion is that you need to work out your trigger circuit challenges first.
__________________
Kevin Sanders
Bayliner 4788
Seward, Alaska
ksanders is offline   Reply With Quote
Old 06-28-2020, 02:55 AM   #9
Guru
 
City: Clearwater, FL
Country: United States
Vessel Name: Seas the Bay
Vessel Model: 1981 42' Hardin Europa
Join Date: Aug 2016
Posts: 964
Hey Kevin,

The trigger part isnt at all a concern to me. There are a lot of ways to do that. Like I said, the sensing can be based upon a coil sensor (or a hall effect sensor) or be directly switched off neutral. Everyone has familiar turf and less familiar space. That space is familiar to me.

There are already products out there that do most of that. A quick Google search turns up what might be an example:
-- https://www.dwyer-inst.com/Product/P...S/Google#specs

I did see some relays at Grainger's that might work. But, I'm a lot less rehearsed at reading time delay relay specs than other specs.

I was just hoping someone had done this already or played with relays more often and could quickly make a recommendation.

But, thanks for the feedback!
gkesden is offline   Reply With Quote
Old 06-28-2020, 04:05 AM   #10
Moderator Emeritus
 
ksanders's Avatar
 
City: SEWARD ALASKA
Country: USA
Vessel Name: LISAS WAY
Vessel Model: BAYLINER 4788
Join Date: Feb 2011
Posts: 4,622
Quote:
Originally Posted by gkesden View Post
Hey Kevin,

The trigger part isnt at all a concern to me. There are a lot of ways to do that. Like I said, the sensing can be based upon a coil sensor (or a hall effect sensor) or be directly switched off neutral. Everyone has familiar turf and less familiar space. That space is familiar to me.

There are already products out there that do most of that. A quick Google search turns up what might be an example:
-- https://www.dwyer-inst.com/Product/P...S/Google#specs

I did see some relays at Grainger's that might work. But, I'm a lot less rehearsed at reading time delay relay specs than other specs.

I was just hoping someone had done this already or played with relays more often and could quickly make a recommendation.

But, thanks for the feedback!
very cool, I had not seen those!

Use an “off delay” relay. Pick your poison.

The concept is that the relay will delay opening/closing the contacts until the trigger is removed plus the timer runs out.

you will probably have to use a interposing relay to get the current rating you need for the HVAC system.
__________________
Kevin Sanders
Bayliner 4788
Seward, Alaska
ksanders is offline   Reply With Quote
Old 06-28-2020, 05:14 AM   #11
Guru
 
twistedtree's Avatar
 
City: Gloucester, MA
Country: USA
Join Date: Jan 2013
Posts: 5,627
Finder makes a line of time delay relays, and I think also current sense relays.


Good suppliers for stuff like this are:


Mouser - Top notch supplier. Usually the first place I try.



Factorymation - Generally better pricing on the things they carry.



AutomationDirect - Similar to FactoryMation



DigiKey - Good selection, but usually more expensive than other places.



Newark - Very wide selection, but I have had quite a few order issues with them and now avoid them unless they are the only supplier.



I'm not sure what you guys have found, but I find Grainger to be uniformly significantly more expensive than other sources. They are the West Marine of industrial supply. The good part is that they carry a lot of stuff and you can get it quickly, but otherwise they are last on my list, even after Newark.
__________________
MVTanglewood.com
twistedtree is offline   Reply With Quote
Old 06-28-2020, 09:28 AM   #12
Guru
 
rgano's Avatar
 
City: Southport, Florida
Country: USA
Vessel Name: FROLIC
Vessel Model: Mainship 30 Pilot II since 2015. GB-42 1986-2015. Former Unlimited Tonnage Master
Join Date: Oct 2007
Posts: 1,700
Send a message via Skype™ to rgano
Quote:
Originally Posted by gkesden View Post
rgano,

Thanks so much for the feedback!

.......

So, what I could do is put soft-start kits into both units and see where that gets me. It could easily mitigate the need to prevent the HVAC from starting while cooking -- and do it without disabling the HVAC.

That is probably an $800 solution, which would be excellent if I knew it would work. But, I'm not sure I trust the "specs". I'd hate to spend the $800, look at the current draw on my ammeter, and not be happy with the load in reality.


Thanks again!
OK. I can provide a bit more feedback about my real world experience. My little boat has two air conditioners, a rooftop (air-to-air) 13.5 kBtu unit and a marine 10 kBtu unit, both Dometic. The diesel gen is a mere 3.5 KW Nextgen. Prior to installation of the Easy Starts (by me with excellent support from Micro-Air), only one of these unit could be run at a time on the generator, and there was a hell of a thump whenever the compressor came on and noticeable change in rpm from the genny. Now they both run fine, and there is NO, repeat, NO indication anything has changed as the compressors come on. You have to really pay attention to tell. The Easy Starts are expensive, but the price comes down a lot if you just by the circuit board from them and get a plastic box to place them in. I got super lucky and got my two Easy Start CBs for a couple hundred dollars from a fellow boater who had bought but not installed them. These things DO work.
__________________
Rich Gano
FROLIC (2005 MainShip 30 Pilot II)
Panama City area
rgano is offline   Reply With Quote
Old 06-28-2020, 10:51 AM   #13
Senior Member
 
KnotYet's Avatar
 
City: Los Angeles
Country: USA
Join Date: Feb 2020
Posts: 179
Quote:
Originally Posted by gkesden View Post
KnotYet,

I don't think I'm seeing one that would work. I'm probably missing it. Any recommendations?

Many thanks!
-Greg
As I read your desired outcome, you require 2 relays.
The first is a basic 'normally on' that turns off whenever the listed appliances are on.
The second is the time delay relay that incorporates the 5 minute start-up delay.
As long as you don't mind waiting 5 minutes every time you start the HVAC, that is.

There are many such programable relays that will do this from many suppliers.
I only mention McMaster-Carr because I have ordered these relays from them before.
Please correct me if I misunderstand your requirements.
KnotYet is offline   Reply With Quote
Old 06-28-2020, 11:11 AM   #14
Guru
 
twistedtree's Avatar
 
City: Gloucester, MA
Country: USA
Join Date: Jan 2013
Posts: 5,627
I think you could also do it with a single time delay relay that has a NC contact. Wire the AC units to the NC contact, and have operation of the other appliances trigger the relay opening the AC circuit. When the appliance turns off, the delay will run out and the NC contact will close again.


For sensing the appliances, there are current sense relays that you could use. Run one of the wires from each of the appliances through the sense coil, and it will detect either of them running.
__________________
MVTanglewood.com
twistedtree is offline   Reply With Quote
Old 06-28-2020, 11:49 PM   #15
Guru
 
City: Clearwater, FL
Country: United States
Vessel Name: Seas the Bay
Vessel Model: 1981 42' Hardin Europa
Join Date: Aug 2016
Posts: 964
Hi all,

Thanks for the help!

Kevin, KnotYet, TwistedTree:

I may just have bum luck paging through relays specs not really knowing how to search them, but what seems to be throwing me is that I only want the delay on the make, not the break. I've found all sorts of relays, but not exactly that. I can piece it together, but I just have a feeling that what I want is out there and that I just need to learn how to ask for it.

If I can find what I want, I shouldn't have to wait the 3 minutes each time, only after cooking. But, that may be a big if.

I may just give up on this approach and do the sense, state switch, and time-delay in solid-state and reserve the relay for carrying the load. Triacs get messy.


rgano:

I think I'm going to call them this week. It sounds like it'll be money well spent in any case. Thanks for writing about your experience.

If the MicroAir gives me the headroom to cook with both ACs on, that is the best of all worlds. Having said that, I might build a similar controller for the hot water heater, but that doesn't require a time delay and is a pretty low priority since i only use it for a bit in the morning, anyway.

Still looking for suggestions on a specific relay, though!

Cheers!
-Greg
gkesden is offline   Reply With Quote
Old 06-29-2020, 09:35 AM   #16
Guru
 
twistedtree's Avatar
 
City: Gloucester, MA
Country: USA
Join Date: Jan 2013
Posts: 5,627
This is the reason to use a SPDT relay, and use the NC side of it. Then the AC is normally on, and is triggered by load to turn off and stay off for a delay after the load goes away.
__________________
MVTanglewood.com
twistedtree is offline   Reply With Quote
Old 06-29-2020, 10:06 AM   #17
Guru
 
City: Clearwater, FL
Country: United States
Vessel Name: Seas the Bay
Vessel Model: 1981 42' Hardin Europa
Join Date: Aug 2016
Posts: 964
Hey Tanglewood,

Thanks! Pretty please see the attached spec sheet. It is the one I originally thought would work, posted about, and then edited out.

I thought from the specs that it should work, but when I looked at the transition diagram at the bottom right of the spec sheet it seemed backward. It still looks like it should work with via the other terminal, but I dont understand why.
Attached Files
File Type: pdf RIBTD2401B.pdf (687.1 KB, 13 views)
gkesden is offline   Reply With Quote
Old 06-29-2020, 10:51 AM   #18
Guru
 
twistedtree's Avatar
 
City: Gloucester, MA
Country: USA
Join Date: Jan 2013
Posts: 5,627
Quote:
Originally Posted by gkesden View Post
Hey Tanglewood,



Thanks! Pretty please see the attached spec sheet. It is the one I originally thought would work, posted about, and then edited out.



I thought from the specs that it should work, but when I looked at the transition diagram at the bottom right of the spec sheet it seemed backward. It still looks like it should work with via the other terminal, but I dont understand why.


That doesnít look like it will do what you want. The timing diagrams tell the story.

I think you want something that:

1) activates on the leading edge of the loads turning on, and

2) stays on for a programmable time after the load turns off.

And Iím still not clear on how you plan to detect when the loads are on? It sounded like you had a plan, but I didnít follow it.
__________________
MVTanglewood.com
twistedtree is offline   Reply With Quote
Old 06-29-2020, 03:41 PM   #19
Guru
 
twistedtree's Avatar
 
City: Gloucester, MA
Country: USA
Join Date: Jan 2013
Posts: 5,627
I think something like those in this datasheet will work. I'm using the highlighted one for a timed bathroom vent fan, and I think it's pretty much what you need.
Attached Files
File Type: pdf FinderS80EN.pdf (3.23 MB, 9 views)
__________________
MVTanglewood.com
twistedtree is offline   Reply With Quote
Old 06-30-2020, 05:57 AM   #20
Guru
 
City: Clearwater, FL
Country: United States
Vessel Name: Seas the Bay
Vessel Model: 1981 42' Hardin Europa
Join Date: Aug 2016
Posts: 964
Twistedtree,

Thanks so much!

The two basic "non contact" ways of detecting current flow are via some type of coil via inductance or via electron deflection in a hall effect sensor.

The idea behind the coil is that an alternating current moving through a wire produces an alternating magnetic field. The flux from this, in turn, induces a current flow in a nearby coil of wire. It is the same principle that lets the two coils of a transformer transmit energy, where in a 1:1 isolation transformer, or a step-up or step-down transformer, or to wirelessly charge a toothbrush or phone, or to enable those "light up AC voltage detectors".

So, basically what one does is to wrap wire into a coil and wrap that around the wire in which one wants to sense current, and then builds a circuit around it to let it drive the relay. Depending upon the details this likely involves an integrator and/or amplifier.

Either might need power to be able to drive a relay and/or the support circuit -- there is only so much one can drive off of a small coil:wire interface. If one did need power, one might want to take it from the output side of the circuit off to avoid disturbing the wire being monitored.

One could also use a hall-effect sensor, which basically takes advantage of the fact that (magnetic) opposites attract -- and sames repel. As current flows, electrons, which are negatively charged move, which can repel electrons in a tiny piece of metal, generating a tiny voltage differential across it (the potential energy of them moving back). This can then be amplified and used as above. The big advantage of hall effect sensors is that since they don't require current flow, they can be used for DC voltages and to detect static magnetic fields. In this application they'd be useful -- but, because of the tiny differential, require more support to drive a relay.

In terms of

One could get past this if one wanted to disturb the wire being sensed to add a voltage transformer. This replaces the inefficient wire with a more efficient coil. This is basically what many traditional current-sense relay do.

In terms of "contact" ways of doing things, one could add a transformer to the circuit being monitored and use it as a more powerful coil-based sensor. One could also add a "shunt", e.g. a very-precise low-resistance link. One could then measure the voltage drop across this link to deduce the current flow via Ohm's law and, in any case, amplify that voltage to drive the switch circuit.

Lastly, although the "hot" wire going to a device always has power, the "neutral" wire, which serves as the return path, is only a current carrying part of the circuit when the circuit is carrying a load. So one could come off of the neutral wire with a high impedance device to ground and sense voltage that way. Something like a MOSFET, JFET, etc can have doens to hundreds of ohms of impedance, so would have a negligible impact on the circuit. But, tapping anything is less clean than a non-contact sensor, and tappping the negative is particularly ugly as it is very unexpected.

At any rate, one could use any of the techniques to build a load sensor. And, it isn't hard to do. But, when ti comes to the passive sensors, which are likely the best approach -- plenty of people already have. They can be bought off the shelf.

Cheers!
-Greg
__________________

gkesden is offline   Reply With Quote
Reply

Thread Tools Search this Thread
Search this Thread:

Advanced Search
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off





All times are GMT -5. The time now is 05:20 PM.


Powered by vBulletin® Version 3.8.8 Beta 4
Copyright ©2000 - 2020, vBulletin Solutions, Inc.
Search Engine Optimization by vBSEO 3.6.0
Copyright 2006 - 2012
×