AC Issues

I have a King Air AC unit on board. I was away from the boat for 2 weeks and when I returned there was no water flow, power was on and the fan was running. I secured the system and found the strainer plugged with debris. I cleaned and established water flow to the system.

When I turned on the AC back on, the fan comes on, the water pump comes on and has flow, but no compressor.

If the system ran for days without cooling water, where should I be looking for issues or would that have fried the compressor?

Thanks

Bill
__________________
Advertisement

captwill is offline   Reply With Quote
Old 07-22-2017, 12:35 PM   #2
Guru
 
Heron's Avatar
 
City: Cypress Landing Marina (NC)
Country: USA
Vessel Name: Heron (2)
Vessel Model: '88 Cape Dory 28 Flybridge #115
Join Date: Nov 2014
Posts: 1,303
Is there a reset button? Mine would occasionally kick off in those circumstances.
__________________

__________________
Steve
Heron is offline   Reply With Quote
Old 07-22-2017, 12:57 PM   #3
Technical Guru
 
Ski in NC's Avatar
 
City: Wilmington, NC
Country: USA
Vessel Name: Louisa
Vessel Model: Custom Built 38
Join Date: Jan 2014
Posts: 5,654
Look for a reset button on the refrigerant lines. My Mermaid units will trip the button if water flow is lost.
Ski in NC is online now   Reply With Quote
Old 07-23-2017, 11:32 AM   #4
Veteran Member
 
City: New Bern
Country: USA
Join Date: Jun 2016
Posts: 60
I couldn't find a reset button...found an overheated connection on what appears to be an overload protector. How would I check to see if this has failed? Put a meter across the terminals and check for continuity?

Thanks

Bill
Attached Thumbnails
Click image for larger version

Name:	pic 2.jpg
Views:	72
Size:	74.8 KB
ID:	67015   Click image for larger version

Name:	IMG_0511[6736].jpg
Views:	67
Size:	77.1 KB
ID:	67016  
captwill is offline   Reply With Quote
Old 07-23-2017, 01:45 PM   #5
Senior Member
 
City: Marathon
Country: Usa
Vessel Name: silver gift
Vessel Model: 45 jefferson
Join Date: Nov 2013
Posts: 258
Hgh pressure cut out.

Most units have a high pressure cut out control that will open the compressor circuits when you have no water flow. Look over unit carefully and somewhere on the smaller line set you will find a control with two wires going to control box. Should be a red button on top to reset it. Some unit also have a reset in t-stat ,off then on. Look at wiring diagram for h/ p control.
Deckape is offline   Reply With Quote
Old 07-23-2017, 07:36 PM   #6
Senior Member
 
City: Marathon
Country: Usa
Vessel Name: silver gift
Vessel Model: 45 jefferson
Join Date: Nov 2013
Posts: 258
Bymetal kixson

Your pictures are of the compressors by metal kixson. This opens the common wire to the compressor when it gets overloaded or high temp. You can om across the terminals to see if it is open. If it is open ,put jumper across and see if unit will start. Maybe able to pickup one at an appliance parts supplier.
Deckape is offline   Reply With Quote
Old 07-23-2017, 07:45 PM   #7
Guru
 
menzies's Avatar
 
City: Jacksonville
Country: USA
Vessel Name: SONAS
Vessel Model: Grand Alaskan 53
Join Date: May 2014
Posts: 5,836
You may have also drawn air into the system, that will give you a HI PR reading. Check to see if you have a bleed hose or valve just before the RW pump. If so turn on the system and quickly bleed the air. It may mean sucking on a hose until you get running water!
menzies is online now   Reply With Quote
Old 09-30-2017, 12:42 PM   #8
Veteran Member
 
City: Baltimore
Country: US
Join Date: Sep 2017
Posts: 31
It is not good for the compressor to repeatedly cycle on the thermal overload. Those Klixon overloads are often available on Amazon or elsewhere online. Make sure the new one matches the old. There should be a manual reset high pressure switch to protect the system in the event of water failure in cooling or fan failure in heating. Make sure the pressure rating is correct for the refrigerant in your unit.

Daniel
__________________

dvarholy is offline   Reply With Quote
Reply

Thread Tools Search this Thread
Search this Thread:

Advanced Search
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off





All times are GMT -5. The time now is 10:35 PM.


Powered by vBulletin® Version 3.8.8 Beta 4
Copyright ©2000 - 2020, vBulletin Solutions, Inc.
Search Engine Optimization by vBSEO 3.6.0
Copyright 2006 - 2012
×