Generator issues

My 4.4 kw Westerbeke is acting strangely.
When first started up, it will charge the batteries at the maximum that the charger, Xantrex MS2000 will permit. As the batteries get charged, dropping from Bulk to Acceptance, to Float, the generator will drop voltage, from the 125v that it starts with, to around 100v, which the Xantrex rejects, as that is too low. When that happens, charging stops altogether.

I notice this a few tries in, and then started adding other loads as the charger reduced loads. That kept the voltage up and allowed the charging to continue. Now, with a space heater drawing furiously, out on the foredeck, it works. Until the heater turns itself off. I might have one at home I can substitute, without an automatic overheat shutoff, but I digress.

I need to get this fixed, but I have already taken it in, which I did 2 years ago, but the tech, armed with test equipment, couldn't make it misbehave, so nothing was accomplished. Then I added solar, so the generator saw almost no use last year. This year I added significantly to electrical loads, so needed the generator, so now I have more incentive to get it fixed.

Which part of the genset is malfunctioning, to allow the voltage to drop as the load drops?
__________________
Keith
koliver is online now   Reply With Quote
Old 08-05-2021, 06:49 PM   #2
Senior Member
 
Wood's Avatar
 
City: Portsmouth, NH
Vessel Name: Irony
Vessel Model: Bayliner 4588
Join Date: Mar 2016
Posts: 117
If you start the generator without the charger under low load - what is the voltage?
__________________
Irony
Bayliner 4588
Portsmouth, NH
Wood is offline   Reply With Quote
Old 08-05-2021, 07:42 PM   #3
Guru
 
High Wire's Avatar
 
City: Cape May, NJ and Englewood, FL
Vessel Name: Irish Lady
Vessel Model: Monk 36
Join Date: Dec 2007
Posts: 4,126
Buy a Kill-A-Watt power monitor (about $25) and plug it into a wall outlet. It allows you to easily monitor output voltage on one leg and generator frequency from an accessible location.
Low frequency (engine speed) will lower the voltage as well as a voltage regulator problem.
Check your generator manual for generator output voltage troubleshooting.
__________________
Archie
Irish Lady
1984 Monk 36 Hull #46
Currently in Cape May NJ
High Wire is offline   Reply With Quote
Old 08-05-2021, 08:01 PM   #4
STB
Guru
 
City: .
Join Date: Aug 2016
Posts: 1,646
We need to do some more tests to get a better idea.

My first guess would that the problem is on the engine side of things with the governor.

Can you check the RPMs if the engine, e.g. with a tach gauge or phototach instrument? Do they go up and down with the voltage?

Can you check the AC output voltage frequency, for example with a multimeter frequency scale, a frequency counter instrument, or with an oscilloscope? Does it go up and down with the voltage?

If you happen to have an oscilloscope, does the waveform look right or change?

If it isn't on the mechanical side of things, it could be in the voltage regulator or regulator-exciter circuit. The answer could be as easy as a bad capacitor.

But, to make any real guess, I'd need to see the schematic for your generator or know the /exact/ model to see if I can find it online. Different generators work very differently in this respect, especially generationally.
STB is offline   Reply With Quote
Old 08-06-2021, 01:03 AM   #5
Guru
 
syjos's Avatar


 
City: Gig Harbor
Vessel Name: Sandpiper
Vessel Model: Bluewater 40 Pilothouse Trawler
Join Date: Nov 2012
Posts: 2,030
Test the capacitor(s). Westerbekes come with one or two.

You'll need a multimeter with capacity measurement capabilities.
syjos is offline   Reply With Quote
Old 08-06-2021, 12:01 PM   #6
Senior Member
 
City: NEW PORT RICHEY
Vessel Name: M/V Intrigue
Vessel Model: 1985 Tung Hwa Senator
Join Date: Dec 2019
Posts: 192
I had this issue on my Westerbeke 4.4 when I purchased it. The Xantrex rejected the power and the voltage was low. I set my multimeter to hertz and plugged it in the nearest socket. I was getting low frequency. I cant remember exactly what it was but maybe high 40s. Come to find out, sometime in the recent past, someone had changed the stop solenoid. The stop solenoid is obviously connected to the fuel lever. Changing the stop solenoid requires a check and adjustment of the frequency to ensure it has not been altered during the R&R. This is also where the RPM is set. RPM= generator frequency. Just a few quick turns of the adjustment turnbuckle and I had it set to around 60.5 I think under no load. Then tested at high load to ensure it was around 59.9 to 60 hertz. Been fine ever since. Either the kilowatt mentioned above or a digital multimeter set to hertz and this check takes about 30 second. Adjusting takes a few minutes. I think you should rule this out before going down the line.
Barking Sands is online now   Reply With Quote
Reply

Thread Tools Search this Thread
Search this Thread:

Advanced Search
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


» Trawler Port Captains
Port Captains are TF volunteers who can serve as local guides or assist with local arrangements and information. Search below to locate Port Captains near your destination. To learn more about this program read here: TF Port Captain Program





All times are GMT -5. The time now is 08:06 PM.


Powered by vBulletin® Version 3.8.8 Beta 4
Copyright ©2000 - 2021, vBulletin Solutions, Inc.
Search Engine Optimization by vBSEO 3.6.0
Copyright 2006 - 2012