Old 09-18-2021, 12:56 PM   #1
Member
 
City: North Channel / Canada
Vessel Name: M/V Change of Pace
Vessel Model: DeFever 40
Join Date: Sep 2021
Posts: 9
Low voltage Issues on N/L Generator

Thank you for letting us be a part of your group.
It was recommended by our DeFever Group to contact the Trawler Forum for help.
Our issue is we have a DF40 with a Northern Lights M643 generator that is going to low voltage in a Bulk state charge on our new Mastervolt Plus charger which was replaced once after it damaged $2200 of on board equipment.
Mastervolt have been very good to us by getting the replacement to us in a timely manor since we live on our boat in the North Channel here in Canada.
The replacement was a new version of the Plus with 10 dip switches instead of 8.
The M/V Plus replaced an aging Xantrex Freedom 2000 combo charger/inverter (the Link 1000 was acting up).
We have not had any issues with the N/L M643 generator with only a 1000 hrs on it.
The M/V charger works great on shore power and also works great on our backup Honda 2000e but goes to a low of 90.2 volts when using the N/L generator during the “bulk” charge state.
Note; if the hot water heater kicks in the voltage does go back up to its normal 122.3 volts…go figure
We can “baby sit” the monitor on the charger(EasyView 5)and change the current load setting form the factory setting of 16A to 8A to maintain the 122volts but amps in bulk charge goes to58 amps instead of the 75 amp rating that we payed for but the most important part of this is the damage and potentially a fire that good be created by this problem.
No wiring changes have been made other than the direct replacement of the Xantrex to the M/V.
The N/L folks have stated Since your generator set is wired for straight 120 VAC the issue can’t be due to imbalanced loads and is more than likely due to the excessive non-linear load of you charger. When your water heater energizes with purely resistive load it helps to mitigate the negative effects of the charger. I do not believe that it is caused by any problem with the generator but can’t say with a 100% assurance since your generator is older and I do not know the condition of the windings.
I have read that there are isolation transformers on the mart that are specifically designed to filter the effects of non-linear loads but I have not seen any in operation.

If anyone has experienced this problem we would love to find a resolution.
With thanks Paul
Small Change is offline   Reply With Quote
Old 09-18-2021, 01:08 PM   #2
Senior Member
 
fgarriso's Avatar
 
City: Blossom Village
Vessel Name: GOTCHA
Vessel Model: DeFever 59 PH
Join Date: Jun 2019
Posts: 491
What is the generator engine RPM at 122 VAC, and what is it at 90.2 VAC?
__________________
Captain F. Lee - R.P.E.
USCG 200 GT Master
fgarriso is offline   Reply With Quote
Old 09-18-2021, 01:24 PM   #3
Member
 
City: North Channel / Canada
Vessel Name: M/V Change of Pace
Vessel Model: DeFever 40
Join Date: Sep 2021
Posts: 9
I don’t have a rpm gauge but the generator doesn’t seem to change in sound compared to adding a different load to the gen set such as coffee maker or microwave.
Small Change is offline   Reply With Quote
Old 09-18-2021, 01:39 PM   #4
TF Site Team
 
Comodave's Avatar
 
City: Au Gres, MI
Vessel Name: Black Dog
Vessel Model: Formula 41PC
Join Date: Jul 2015
Posts: 13,028
Welcome aboard. You can get a photo tach on Amazon for less than $50 if you do need to check the RPMs.
__________________
Boat Nut:
If you are one there is no explanation necessary.
If you aren’t one, there is no explanation possible.
Comodave is online now   Reply With Quote
Old 09-18-2021, 01:42 PM   #5
Guru
 
twistedtree's Avatar
 
City: Walkabout Creek
Join Date: Jan 2013
Posts: 6,846
This does indeed have all the hallmarks of excessive non-linear loads. The fact that the problem goes away when you add a good resistive load is the big clue.


Here is some more info, and some pointers to filtering transformers.


https://eepower.com/technical-articl...ce-harmonics/#


If you find a transformer and it solves the problem, I'm sure the folks at NL would appreciate hearing about it.
__________________
MVTanglewood.com
twistedtree is offline   Reply With Quote
Old 09-18-2021, 01:47 PM   #6
Senior Member
 
fgarriso's Avatar
 
City: Blossom Village
Vessel Name: GOTCHA
Vessel Model: DeFever 59 PH
Join Date: Jun 2019
Posts: 491
It should be running at 1800 RPM for 120VAC @ 60Hrz. When the electrical load increases the RPM should stay the same, but the engine governor should open to hold the RPM. At the same time you should be able to hear the engine loading increase to maintain the RPM.
__________________
Captain F. Lee - R.P.E.
USCG 200 GT Master
fgarriso is offline   Reply With Quote
Old 09-18-2021, 03:16 PM   #7
TF Site Team
 
Larry M's Avatar
 
City: Jacksonville
Join Date: Nov 2008
Posts: 9,976
What is the frequency when the generator loads up? Your dvm should have a frequency function. There is a specification for frequency and voltage. At higher loads the frequency maybe lower but shouldn’t be below 58Hz and at zero load no more than about 62Hz. These are approximate.
Larry M is offline   Reply With Quote
Old 09-18-2021, 03:35 PM   #8
Guru
 
High Wire's Avatar
 
City: Cape May, NJ and Englewood, FL
Vessel Name: Irish Lady
Vessel Model: Monk 36
Join Date: Dec 2007
Posts: 4,200
1- Buy a Kill-A-Watts energy monitor and plug it into any onboard receptacle. It will monitor generator output voltage and frequency.
2- Buy a simple cube heater used at a thrift shop or <$20 new at Dollar General. Turn it on Low or High setting with an extension cord to outside to put a resistive load on the genny. Your gen will handle the extra load, plus it is good for the gen to run loaded anyway. Your batt charger is only using about 1200 watts on full charge. It drops fast after you reach Acceptance charge rates. Thats a long way from a healthy load.
BTW, Welcome Aboard.
__________________
Archie
Irish Lady
1984 Monk 36 Hull #46
Currently in Englewood, FL
High Wire is online now   Reply With Quote
Old 09-18-2021, 03:45 PM   #9
Member
 
City: North Channel / Canada
Vessel Name: M/V Change of Pace
Vessel Model: DeFever 40
Join Date: Sep 2021
Posts: 9
Thank you

Quote:
Originally Posted by twistedtree View Post
This does indeed have all the hallmarks of excessive non-linear loads. The fact that the problem goes away when you add a good resistive load is the big clue.


Here is some more info, and some pointers to filtering transformers.


https://eepower.com/technical-articl...ce-harmonics/#


If you find a transformer and it solves the problem, I'm sure the folks at NL would appreciate hearing about it.
thank you
Small Change is offline   Reply With Quote
Old 09-18-2021, 03:49 PM   #10
Member
 
City: North Channel / Canada
Vessel Name: M/V Change of Pace
Vessel Model: DeFever 40
Join Date: Sep 2021
Posts: 9
Quote:
Originally Posted by High Wire View Post
1- Buy a Kill-A-Watts energy monitor and plug it into any onboard receptacle. It will monitor generator output voltage and frequency.
2- Buy a simple cube heater used at a thrift shop or <$20 new at Dollar General. Turn it on Low or High setting with an extension cord to outside to put a resistive load on the genny. Your gen will handle the extra load, plus it is good for the gen to run loaded anyway. Your batt charger is only using about 1200 watts on full charge. It drops fast after you reach Acceptance charge rates. Thats a long way from a healthy load.
BTW, Welcome Aboard.
We’re you having the same issues and did this clear it and thanks for you input.
Small Change is offline   Reply With Quote
Old 09-18-2021, 04:33 PM   #11
Guru
 
High Wire's Avatar
 
City: Cape May, NJ and Englewood, FL
Vessel Name: Irish Lady
Vessel Model: Monk 36
Join Date: Dec 2007
Posts: 4,200
Not exactly. I bought the Kill A Watt monitor for my old generator as an easier way to monitor frequency/rpm than using a digital photo tach.
Since my old gen died from chronic under loading I have been very sensitive to monitor loading. On my boat after an hour, I can’t even hold 20% load. The battery charger tapers off and the water heater is hot and the AC units are cycling. I had two cube heaters to break in the new generator with both air conditioning units on heating mode with the doors and windows wide open. It’s the only way to reach 8 Kw on my boat.
As far as low voltage goes, there have been at least two similar threads within the last year where the cause was low frequency.
__________________
Archie
Irish Lady
1984 Monk 36 Hull #46
Currently in Englewood, FL
High Wire is online now   Reply With Quote
Old 09-19-2021, 08:43 AM   #12
Member
 
City: North Channel / Canada
Vessel Name: M/V Change of Pace
Vessel Model: DeFever 40
Join Date: Sep 2021
Posts: 9
Quote:
Originally Posted by High Wire View Post
Not exactly. I bought the Kill A Watt monitor for my old generator as an easier way to monitor frequency/rpm than using a digital photo tach.
Since my old gen died from chronic under loading I have been very sensitive to monitor loading. On my boat after an hour, I can’t even hold 20% load. The battery charger tapers off and the water heater is hot and the AC units are cycling. I had two cube heaters to break in the new generator with both air conditioning units on heating mode with the doors and windows wide open. It’s the only way to reach 8 Kw on my boat.
As far as low voltage goes, there have been at least two similar threads within the last year where the cause was low frequency.
Thanks Archie
Small Change is offline   Reply With Quote
Old 09-19-2021, 09:17 AM   #13
Member
 
City: North Channel / Canada
Vessel Name: M/V Change of Pace
Vessel Model: DeFever 40
Join Date: Sep 2021
Posts: 9
Thank you everyone for some good advice and I will follow up with the ideas and get back to the group.
Thanks again, Paul
Small Change is offline   Reply With Quote
Old 09-19-2021, 10:02 AM   #14
Moderator Emeritus
 
ksanders's Avatar
 
City: SEWARD ALASKA
Vessel Name: LISAS WAY
Vessel Model: BAYLINER 4788
Join Date: Feb 2011
Posts: 5,227
The folks that are recommending that you check the RPM are dead on correct.

I have seen this same problem many times with clients land based backup generators. They are a bit too high in frequency at low loading levels.

Add some load and the natural droop of the mechanical governor slows down the engine enough for the voltage regulator on the generator to stabilize the voltage.

One gauge you really want on your electrical panel is a frequency meter. That and make sure your onboard handheld DVM will also read frequency.

With no load you should have 61.5-62 hertz out of any mechanically governored generator. This will produce a fully loaded frequency of about 58HZ
__________________
Kevin Sanders
Bayliner 4788
Seward, Alaska
ksanders is offline   Reply With Quote
Old 09-19-2021, 10:58 AM   #15
Member
 
City: North Channel / Canada
Vessel Name: M/V Change of Pace
Vessel Model: DeFever 40
Join Date: Sep 2021
Posts: 9
Quote:
Originally Posted by ksanders View Post
The folks that are recommending that you check the RPM are dead on correct.

I have seen this same problem many times with clients land based backup generators. They are a bit too high in frequency at low loading levels.

Add some load and the natural droop of the mechanical governor slows down the engine enough for the voltage regulator on the generator to stabilize the voltage.

One gauge you really want on your electrical panel is a frequency meter. That and make sure your onboard handheld DVM will also read frequency.

With no load you should have 61.5-62 hertz out of any mechanically governored generator. This will produce a fully loaded frequency of about 58HZ
Thank you, would a Fluke117 be good replacement for my old meter( doesn’t read Htz) or could you recommend a affordable meter. Thanks
Small Change is offline   Reply With Quote
Old 09-19-2021, 12:11 PM   #16
Moderator Emeritus
 
ksanders's Avatar
 
City: SEWARD ALASKA
Vessel Name: LISAS WAY
Vessel Model: BAYLINER 4788
Join Date: Feb 2011
Posts: 5,227
Quote:
Originally Posted by Small Change View Post
Thank you, would a Fluke117 be good replacement for my old meter( doesn’t read Htz) or could you recommend a affordable meter. Thanks
Yes that one would work since it measures frequency.

Actually though I thought that I read that the 117 auto selects AC or DC automatically. I did not read up on it to verify but I would greatly prefer a DMM that you choose AC or DC over one that auto selects. That way for example you could look at a AC component on a DC signal.
__________________
Kevin Sanders
Bayliner 4788
Seward, Alaska
ksanders is offline   Reply With Quote
Old 09-19-2021, 12:11 PM   #17
Senior Member
 
gsholz's Avatar
 
City: Out and About
Vessel Model: Sold-GB 52 Europa, Queenship 59, Tolly 45
Join Date: Nov 2016
Posts: 447
It is not an RPM issue. The charger is a highly non-linear load. It distorts the voltage/current waveforms. Your gauge will not read correctly (unless it is a true RMS meter). Adding meaningful resistive load fixes it.
gsholz is offline   Reply With Quote
Old 09-19-2021, 12:22 PM   #18
Member
 
City: North Channel / Canada
Vessel Name: M/V Change of Pace
Vessel Model: DeFever 40
Join Date: Sep 2021
Posts: 9
So you saying if I add a resistance load like the small micro heater(which was recommended by another boater) when starting the charger in the bulk stage, this will settle out the generator, much like the hot water system did to maintain the 122 volts?
Small Change is offline   Reply With Quote
Old 09-19-2021, 01:04 PM   #19
Senior Member
 
Jc180's Avatar
 
City: New Smyrna Beach, Fl. & Scottsboro, Al.
Vessel Name: Salty Dog & Last Dragon
Vessel Model: Gulfstar 47 Sailmaster & Mainship 34 MK 1
Join Date: Aug 2018
Posts: 108
Have carefully read all posts on this thread and agree with both schools of thought 1) Most common low voltage on the single phase 120V generators is caused by low rpms as the machine is loaded. I had this problem and adjusting rpms up solved. 2) That it is likely a non-linear load problem. Suspect so since you can’t audibly detect generator speed changes and goes away with addition of resistance load. Suspect shore power is immune due to robust nature of the power and Honda gen immune because it is actually inverter type output. That said, My thought is that your beef is with Master Volt and not Northern Lights. Think an isolation transformer as a remedy would cost more than scrapping the Master Volt. And big and heavy. And when at anchor, turning on resistance load doesn’t make sense. I have had very good luck with Iota chargers. Not ignition protected, but fine for diesel powered boats. You do need a separate battery monitoring system.
Jc180 is offline   Reply With Quote
Old 09-19-2021, 02:47 PM   #20
Member
 
City: North Channel / Canada
Vessel Name: M/V Change of Pace
Vessel Model: DeFever 40
Join Date: Sep 2021
Posts: 9
Thanks for all your advice and it does make sense.
It is a shame that when we had the folks from M/V spec out the charging system that they would of recommended a charger that was compatible with our M643 generator.
I guess I could find something with a residive load to run that is better then a micro heater during charging since the generator runs great on all other demands on the vessel.
Thanks again for all your help.
Small Change is offline   Reply With Quote
Reply

Tags
battery chargers, electrical, generator

Thread Tools Search this Thread
Search this Thread:

Advanced Search
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


» Trawler Port Captains
Port Captains are TF volunteers who can serve as local guides or assist with local arrangements and information. Search below to locate Port Captains near your destination. To learn more about this program read here: TF Port Captain Program





All times are GMT -5. The time now is 11:53 AM.


Powered by vBulletin® Version 3.8.8 Beta 4
Copyright ©2000 - 2021, vBulletin Solutions, Inc.
Search Engine Optimization by vBSEO 3.6.0
Copyright 2006 - 2012