Generator Question

I have recently acquired a vessel in Australia that is fitted with a Lombardini LMG9000 genset.
Itís a 2 cylinder 3,000rpm setup that is meant to be good for 9kva.
It is 15 years old and has done 1,700 hours.
Down under we run AC power at 240v and circa 50hz.
It is producing the 50hz no problems but is only generating 195v.
On shore power the voltage gauge registers 240.
Nothing terrible happening yet however electrical appliances like the toaster arent getting to full heat.
Iíve got a couple questions if anyone can help.
In its current state do I run the risk of damaging any of the on board circuitry systems like the water heater, battery chargers, air conditioning etc?
Has anyone else addressed this and if so what was the fix?
Thanks in advance.
ABQLD is offline   Reply With Quote
Old 01-22-2022, 06:54 AM   #2
Guru
 
O C Diver's Avatar
 
City: Fort Myers, FL... Summers in the Great Lakes
Vessel Name: Slow Hand
Vessel Model: Cherubini Independence 45
Join Date: Dec 2010
Posts: 10,899
Always best to measure voltage, hertz, and RPM while you're at it, at the generator to eliminate boat wiring as an issue. I wouldn't be running anything until resolving the issue. While an induction heat element such as a water heater wouldn't be effected by low voltage, appliances with AC motors and electronics could seriously be damaged.

If you've verified low voltage with the correct hertz and RPM at the generator, probably time to call a professional familiar with that brand.

Ted
__________________
Blog: mvslowhand.com
I'm tired of fast moves, I've got a slow groove, on my mind.....
I want to spend some time, Not come and go in a heated rush.....
"Slow Hand" by The Pointer Sisters
O C Diver is offline   Reply With Quote
Old 01-23-2022, 12:54 AM   #3
Member
 
ABQLD's Avatar
 
City: Brisbane
Vessel Name: Placebo
Vessel Model: Fairway 36
Join Date: Sep 2021
Posts: 6
Quote:
Originally Posted by O C Diver View Post
Always best to measure voltage, hertz, and RPM while you're at it, at the generator to eliminate boat wiring as an issue. I wouldn't be running anything until resolving the issue. While an induction heat element such as a water heater wouldn't be effected by low voltage, appliances with AC motors and electronics could seriously be damaged.

If you've verified low voltage with the correct hertz and RPM at the generator, probably time to call a professional familiar with that brand.

Ted
Thanks Ted.
Iíll get a sparky out ASAP.
Hopefully an AVR adjustment is possible but probably a bit of wishful thinking to find 30-40V.
ABQLD is offline   Reply With Quote
Old 01-23-2022, 01:27 AM   #4
Senior Member
 
Brisyboy's Avatar
 
City: Brisbane
Vessel Name: Malagari
Vessel Model: Island Gypsy 36 Europa
Join Date: Mar 2015
Posts: 396
Hi AB

Perhaps a bit belated but welcome. We had use of a Fairway 36 (Bluegum) for a couple of years so we are a fan of Fairways.

Where are you - we are over at Wynnum Manly?
__________________
George
Brisbane
IG 36 Europa
Brisyboy is offline   Reply With Quote
Old 01-23-2022, 02:03 AM   #5
Member
 
ABQLD's Avatar
 
City: Brisbane
Vessel Name: Placebo
Vessel Model: Fairway 36
Join Date: Sep 2021
Posts: 6
Hi there Brisyboy.
I’ve got the boat at Manly.
20 years ago when I was getting g around the bay on trailer boats I used to see Fairway’s plodding around and always thought they looked like a great bay boat.
Wind the clock forward to an alignment of my retirement and a pandemic and my travel plans were somewhat curbed.
Some cruising seemed like a great alternative and the search began.
I found this one just before Xmas which is an 06 one owner boat.
Slowly working my way through some neglected issues but hope to be ready to hit the Sandy Straights and possibly the Bunker Group this winter.
Thanks for reaching out.
ABQLD is offline   Reply With Quote
Old 01-23-2022, 02:17 AM   #6
Guru
 
North Baltic sea's Avatar
 
Vessel Model: Nordic Tug 37
Join Date: Sep 2015
Posts: 1,005
Ted gave the best advice, take care to adjust the voltage and Hz to safety.

we have 230V / 50Hz here, the same as you have. my genny without load 240V and fully load 230V. Sometimes the ports have low electricity of about 215V and only the Victron charger can handle this low current, others are malfunctioning and may at worst overheat litle.


230V/50hz the current variation in the mains is +/- 10% limit values, I think it is a matter of small adjustment of your genny.

NBs
North Baltic sea is offline   Reply With Quote
Old 01-30-2022, 05:34 PM   #7
Veteran Member
 
City: Duvall, WA
Join Date: Aug 2020
Posts: 60
Decade ago, installing a new UPS in a school to power a new rack of switches. Had the school district electricians onsite for the activation, had 208V at the disconnect but dropped to 165V when energized. Two hours later, a bunch of corroded fittings were replaced and 208V stayed 208V. I don't think the cafeteria had a spatula big enough to scrape the egg off the electrician's faces, but we were all amazing that it had dipped that low (UPS went into battery charge as soon as it was activated and had quite a draw).
pjtemplin is offline   Reply With Quote
Old 01-30-2022, 06:04 PM   #8
TF Site Team
 
Comodave's Avatar
 
City: Au Gres, MI
Vessel Name: Black Dog
Vessel Model: Formula 41PC
Join Date: Jul 2015
Posts: 15,356
It can be quite surprising how much voltage can be dropped on a bad connection, also the heat generated.
__________________
Boat Nut:
If you are one there is no explanation necessary.
If you arenít one, there is no explanation possible.
Comodave is online now   Reply With Quote
Old 01-30-2022, 09:21 PM   #9
Senior Member
 
TowLou's Avatar
 
City: Flanders, NJ
Vessel Name: Bassey
Vessel Model: 17' Bass
Join Date: Aug 2016
Posts: 268
You should have a adjustment on your voltage regulator, or front panel for the voltage output. 3k rpm is good for 50 hhz as you want.
TowLou is offline   Reply With Quote
Old 01-30-2022, 10:27 PM   #10
Guru
 
BruceK's Avatar
 
City: Sydney
Vessel Name: Sojourn
Vessel Model: Integrity 386
Join Date: Oct 2011
Posts: 12,218
Great admirer of the Fairway 36. Now built in Taiwan, ABQLD`s is good old Queensland Aussie built. A boat on my marina is currently fitting a low hour second hand Lombardini, seems to be contained in a plastic suitcase ? sound shield. Looked a nice piece of kit.
__________________
BruceK
2005 Integrity 386 "Sojourn"
Sydney Australia
BruceK is online now   Reply With Quote
Old 01-31-2022, 02:01 AM   #11
Member
 
City: Wasilla
Vessel Name: Sea Surgeon
Join Date: Nov 2019
Posts: 11
Quote:
Originally Posted by ABQLD View Post
I have recently acquired a vessel in Australia that is fitted with a Lombardini LMG9000 genset.
Itís a 2 cylinder 3,000rpm setup that is meant to be good for 9kva.
It is 15 years old and has done 1,700 hours.
Down under we run AC power at 240vand circa 50hz.
It is producing the 50hz no problems but is only g enerating 195v.
On shore power the voltage gauge registers 240.
Nothing terrible happening yet however electrical appliances like the toaster arent getting to full heat.
Iíve got a couple questions if anyone can help.
In its current state do I run the risk of damaging any of the on board circuitry systems like the water heater, battery chargers, air conditioning etc?
Has anyone else addressed this and if so what was the fix?
Thanks in advance.
Yes it can hurt electronics. There is a term called brown out which refers to low voltage outside of equipment standard operating range. Each electrical an electronic manufacture has separate low and ranges for acceptable voltage input. If you drop below that, there is significant risk of damage and/or reduced lifespan of the equipment.
Alaska Californian 37 is offline   Reply With Quote
Old 01-31-2022, 07:01 AM   #12
FF
Guru
 
FF's Avatar
 
Join Date: Oct 2007
Posts: 22,553
"It can be quite surprising how much voltage can be dropped on a bad connection, also the heat generated."


However a special set of pans is not required to use the heat.
FF is offline   Reply With Quote
Reply

Thread Tools Search this Thread
Search this Thread:

Advanced Search
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


» Trawler Port Captains
Port Captains are TF volunteers who can serve as local guides or assist with local arrangements and information. Search below to locate Port Captains near your destination. To learn more about this program read here: TF Port Captain Program





All times are GMT -5. The time now is 01:11 AM.


Powered by vBulletin® Version 3.8.8 Beta 4
Copyright ©2000 - 2022, vBulletin Solutions, Inc.
Search Engine Optimization by vBSEO 3.6.0
Copyright 2006 - 2012