120v Surge Protection - AC control transformer failure

I have just finished troubleshooting our Salon AC unit. It is a 16000 btu unit, 120v AC. It is only 3 years old, Ocean Breeze unit.

It turns out the 120/24 vac control power transformer was bad. I contacted PO and he said he had that happen also.

We just finished a few days at anchor over the 4th and were running our generator for quite a bit of time. So I am guessing that some sort of power surge blew the control transformer.

Anyone ever deal with this? I am contemplating the installation of some sort of surge protection.
kurt.reynolds is offline   Reply With Quote
Old 07-07-2017, 07:05 PM   #2
Senior Member
 
City: Hampton Bays, N.Y.
Vessel Name: Grand Yankee
Vessel Model: 1981 49' Grand Banks Classic
Join Date: Oct 2007
Posts: 328
Have you Allen the manufacturer and asked a teak rep his opinion?
Ron T is offline   Reply With Quote
Old 07-07-2017, 07:08 PM   #3
Senior Member
 
City: Hampton Bays, N.Y.
Vessel Name: Grand Yankee
Vessel Model: 1981 49' Grand Banks Classic
Join Date: Oct 2007
Posts: 328
Ok I put the beer down, have you called the manufacturer and asked a technical representative him opinion?
Ron T is offline   Reply With Quote
Old 07-07-2017, 07:35 PM   #4
Guru
 
twistedtree's Avatar
 
City: Vermont
Join Date: Jan 2013
Posts: 10,092
I think "power surges" are one of the industries great excuses for brushing off failures.

Transformers are generally very robust. I would look closely at the loading on it. What is it powering and is it overloaded? It shouldn't be an expensive part, so before installing any sort of surge protector, I would just buy a second one and carry a spare.
__________________
MVTanglewood.com
twistedtree is online now   Reply With Quote
Old 07-07-2017, 07:56 PM   #5
Guru
 
Maerin's Avatar
 
City: East Coast
Vessel Name: M/V Maerin (Sold)
Vessel Model: Solo 4303
Join Date: Jun 2013
Posts: 886
Which side opened? Check with a VOM/continuity on the 120V side and the 24V side to see which one doesn't read continuity. That's the side that opened. If it's the 24V side, chances are a surge protector won't help much, I'd expect the connected load may be at the VA limit of the transformer. Conversely, if the 120V side opened, a surge protector may help. But being the load side is lighter gauge wiring, it's what usually fails. You could use a higher VA rated transformer. 40VA is an industry standard for control circuits.
You can check the amp draw of your 24V control circuit if you have an amprobe, take a couple of wraps around the jaws to get the reading to scale better - divide the reading by the # of wraps. You should read less than 1.6A (AC amps- VA=Volts * Amps). If you're close, you could be overloading the transformer. If that's the case, you could go to a 70VA transformer, I'd put a 3A inline slo-blo fuse in the 24V supply just to be on the safe side.
Don't overlook the possibility that there may be a component over-drawing current intermittently, that could pop the transformer.
Since this is a repeat event, you need to find the why in the equation in order to solve the problem. Don't use a higher VA rated transformer simply to bypass the troubleshooting process- only if you determine that the connected load exceeds the transformer's capacity!
As a preventive measure, you could insert a resettable 1.5A circuit breaker in the 24V supply, could prevent a breakdown situation when you're not near parts and it's hot!
__________________
Steve Sipe

https://maerin.net
Maerin is offline   Reply With Quote
Old 07-08-2017, 07:23 AM   #6
Guru
 
City: kemah
Join Date: May 2015
Posts: 1,135
Quote:
Originally Posted by Maerin View Post
Which side opened? Check with a VOM/continuity on the 120V side and the 24V side to see which one doesn't read continuity. That's the side that opened. If it's the 24V side, chances are a surge protector won't help much, I'd expect the connected load may be at the VA limit of the transformer. Conversely, if the 120V side opened, a surge protector may help. But being the load side is lighter gauge wiring, it's what usually fails. You could use a higher VA rated transformer. 40VA is an industry standard for control circuits.
You can check the amp draw of your 24V control circuit if you have an amprobe, take a couple of wraps around the jaws to get the reading to scale better - divide the reading by the # of wraps. You should read less than 1.6A (AC amps- VA=Volts * Amps). If you're close, you could be overloading the transformer. If that's the case, you could go to a 70VA transformer, I'd put a 3A inline slo-blo fuse in the 24V supply just to be on the safe side.
Don't overlook the possibility that there may be a component over-drawing current intermittently, that could pop the transformer.
Since this is a repeat event, you need to find the why in the equation in order to solve the problem. Don't use a higher VA rated transformer simply to bypass the troubleshooting process- only if you determine that the connected load exceeds the transformer's capacity!
As a preventive measure, you could insert a resettable 1.5A circuit breaker in the 24V supply, could prevent a breakdown situation when you're not near parts and it's hot!
Or....

You could assume the ac unit has a electrical design flaw and buy one from westabo, or marinaire or whomever to alleviate the risk of fire that popping transformers bring with them. No offense against Maerin, but you shouldnt have to redesign their unit.
what_barnacles is offline   Reply With Quote
Old 07-08-2017, 08:13 AM   #7
Guru
 
diver dave's Avatar
 
City: Palm Coast, FL
Vessel Name: Coquina
Vessel Model: Lagoon 380
Join Date: Jan 2017
Posts: 2,570
Quote:
Originally Posted by twistedtree View Post
I think "power surges" are one of the industries great excuses for brushing off failures.

Transformers are generally very robust. I would look closely at the loading on it. What is it powering and is it overloaded? It shouldn't be an expensive part, so before installing any sort of surge protector, I would just buy a second one and carry a spare.
Agree totally. I design industrial surge resistant systems and frequently test transformers, power supplies, and other circuits to 4 and 5kV levels. I've never seen surge take out a transformer. They could run hot, corrode or have insulation failures. I would likely simply find a better quality transformer. Does it run too hot to touch? There are tons of 120 to 24V control transformers out there. But, look for Class 2 (safer) device.
Now, if a semiconductor failure took out the transformer, then the conversation will be different. Is the xfrmr the only defect?
diver dave is offline   Reply With Quote
Old 07-09-2017, 08:39 AM   #8
Guru
 
Maerin's Avatar
 
City: East Coast
Vessel Name: M/V Maerin (Sold)
Vessel Model: Solo 4303
Join Date: Jun 2013
Posts: 886
Quote:
Originally Posted by what_barnacles View Post
Or....

You could assume the ac unit has a electrical design flaw and buy one from westabo, or marinaire or whomever to alleviate the risk of fire that popping transformers bring with them. No offense against Maerin, but you shouldnt have to redesign their unit.
Absolutely no offense taken, you're exactly on the money. I would have been more appropriate to stress that a failed transformer is not normal, more important is to find WHY it failed. Once could be a fluke, twice is an undiagnosed fault.

Thanks for keeping me on point.
Steve
__________________
Steve Sipe

https://maerin.net
Maerin is offline   Reply With Quote
Reply

Thread Tools Search this Thread
Search this Thread:

Advanced Search
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


» Trawler Port Captains
Port Captains are TF volunteers who can serve as local guides or assist with local arrangements and information. Search below to locate Port Captains near your destination. To learn more about this program read here: TF Port Captain Program





All times are GMT -5. The time now is 09:40 PM.


Powered by vBulletin® Version 3.8.8 Beta 4
Copyright ©2000 - 2024, vBulletin Solutions, Inc.
Search Engine Optimization by vBSEO 3.6.0
Copyright 2006 - 2012