I've had Victron Multi 3000's for over 10 years on two boats. I would buy another. A few comments:
- I'm "old school" and suspicious of automatic control. It only takes a second to switch something on and off at the panel. I don't need pretty colored graphics of where the electricity is going.
- They now have a 5 year warranty. Unheard of in marine electrical stuff.
- The Multi 3000 has been around for a decade. Very reliable and quite cheap ($1300). Conservative ratings. It can do 6000 watts momentarily for something like A/C motor startup surge.
- There's no way my 800ah Firefly batteries could be charged too fast by the alternator plus the Victron multi. And remember, about 50 amps is probably going to things on the boat. As the batteries reach absorption the amps automatically drop from both the Victron and the alternator with no intelligence between them.
- Be sure to use the included battery temp sensor so the charger is temperature compensated. Also, connect the voltage sensing wire for the charger directly to the batteries so it's getting a true voltage.
- I have Victron solar controllers on 600watts of solar panel. They work fine but I don't feel the need to "integrate" them with the charger/inverter. They rarely get above 30 amps so really don't impact what I'm doing with the other charging sources. I love the little bluetooth app that tells me how much solar I've gotten each day - but probably only look at it four times a year
- Programming the Victron is easy if you use the free software you can download on a laptop. I have one of the network plugs at the helm. I just plug in the laptop and tweak it (but frankly after setup, I probably only do this one a year).
- You are handling a lot of power so cables should be large. Don't skimp on cabling any 3000 watt inverter.
- The Victron has a ground relay that automatically switches the ground between genset and shore. This is really important at marinas that are upgrading their docks to ELCI breakers.
- Definitely get the remote panel. A knob let's you set the max amps from the AC source. In a marina I always turn this to 40 amps because I don't want to risk popping a marina breaker. Even on the genset, I use this to keep the genset below 80%. If the Victron hits 40 amps it will simply draw what it needs from the batteries. I won't know the difference.
- I have a 2nd Victron Multi for redundancy but did not wire them in parallel. They are completely independent. They can both charge (so 220 amps combined) but only one at a time can be an inverter. Frankly I try to limit the inverter draw to 15 amps by not running the microwave at the same moment as the toaster - easier on the batteries. I don't program this in the inverter but the AC out goes to a pair of breakers with lockout so only one can be turned on.
But really reliability is the most important thing to me. On the current boat the Victron has been on most of the time for six years with no repairs or problems.