The suction pressure sounds within limits, it would be interesting to know the discharge pressure just to confirm. Is there a large temperature drop across the condenser with regard to gas in and liquid out?

I would check the compressor current draw and see if there is an internal problem with the motor. Check the air handler as well to see if the fan motor might be drawing too much current. It doesn't sound like a refrigeration issue per se.
I'm thinking controls or processer board somehow too...nothing is tripping a breaker...the compressor just stops compressing....everything else normal.