Jim:


The voltage drop on each #10 from the panel to the "combiner" (I assume that is a junction box) is about a 1/4 volt. The voltage drop from the combiner to the solar controller (which I assume is about 15 feet) is about .45 volt.


So the net voltage to the MPPT controller will be approximately 18.5 -.25-.45 = 17.8 which is fine for the controller and represents a 4% loss to the controller.


The current from the controller to the batteries will be maybe 15% more than the input, because the voltage is lower, so the voltage drop will be about .55 volts. That is significant and I would consider increasing the wire gauge to the batteries. Or you can relocate the controller closer to the batteries.


David