We had a similar problem. The digital display on the MarineAir unit read "CLF."
This means compressor load failure. We did what you did plus cleaning all the return air filters and vacuuming the evaporator coils. Could not fix it. Called in a repair company and they had to replace the circuit board. The one last thing I would investigate is to be sure the unit is getting proper voltage. Good luck, Howard