Small (Quiet) GenSet recommendation

Hi,
I have an older 20kw genset which needs to be replaced but in the meantime I was thinking about getting something smaller (5kw range) in addition to a larger set. The larger is only needed to power the 3 AC units which rarely will get used so wondering if folks had done something similar. I heard NextGen units are good, compact and quiet?

Any thoughts or advice would be appreciated. I have a yard evaluating the space requirements, etc so its more a question of which units are best should they say we can do the auxiliary unit.

Thanks
Arthur
__________________
Advertisement

__________________
Kadey-Krogen 54
Arthurc is offline   Reply With Quote
Old 06-10-2017, 07:38 PM   #2
Scraping Paint
 
City: CT
Country: US
Join Date: Mar 2017
Posts: 963
Do you spend many days/hours per day on the hook without running the propulsion engine?

If not, retrofitting an Alt setup designed for high-amp charging of a large quality high-acceptance deep cycle bank gives the luxury of sitting in silence when not motoring. You still may want some solar to get maximum lifespan out of the bank.

If yes, then solar alone may be enough if you have enough surface area and sunshine relative to your average AH usage per day.

Finally, many can make do with the very quiet 2kW inverter suitcase gennies, like Honda or Yamaha.

To me buying, carrying and maintaining two bigger ones seems wasteful, but that's me.
__________________

john61ct is offline   Reply With Quote
Old 06-10-2017, 07:38 PM   #3
Guru
 
City: Carefree, Arizona
Country: usa
Vessel Name: sunchaser V
Vessel Model: DeFever 48
Join Date: Apr 2008
Posts: 8,020
You likely don't need 20 kW. On our vessel we have 3 ACs, water heater, inverter, washer and dryer, electric range, additional 50 amp charger, microwave and hair dryers as big loads. We have a 12.5 Westerbeke that with a little load management does fine.

Suggest you consider carefully what your ultimate needs are now, get that unit and forget the small and not inexpensive 5kW install.
sunchaser is offline   Reply With Quote
Old 06-10-2017, 08:19 PM   #4
Guru
 
Bigsfish's Avatar
 
City: Miami River
Country: USA
Vessel Name: Gotcha
Vessel Model: Grand Banks. Heritage. 54
Join Date: Aug 2016
Posts: 2,529
The newer generators are extremely quiet, my Onan 11kw I don't even know it is running.
Bigsfish is offline   Reply With Quote
Old 06-10-2017, 08:23 PM   #5
Guru
 
City: New Orleans
Country: USA
Vessel Name: Scot Free
Vessel Model: Cheoy Lee 53' Efficient
Join Date: Dec 2015
Posts: 725
I had a 3.5kW NexGen on my sailboat. It was a single cylinder 3,600 rpm unit. Noisy as all get out and lots of vibration. I have 16kW Northern Lights on the big boat. Much quieter and smoother. Been thinking of a 6-8kW as a backup. I have room in the machinery space. The Fischer Panda's were very quiet. But I dont know much about their reliability. I do not want a gas engine so that rules out the little Hondas.
McGillicuddy is offline   Reply With Quote
Old 06-10-2017, 08:24 PM   #6
Guru
 
Arthurc's Avatar
 
City: Seattle
Country: USA
Vessel Name: Sea Bear
Vessel Model: Kadey-Krogen 54
Join Date: Sep 2016
Posts: 522
Good feedback, I honestly don't know the exact draw yet as I just got her and she is in the yard (where they found several parts for the 20kw would be hard to get and expensive so hence this thread). She isn't small so I need to plan on the following.
AC fridge, AC washing machine (combo unit), AC dishwasher, hot water heater, plus running all her systems. Heat/cooling is currently designed Florida so likely never to stress it that much.

Im feeling a bit rushed into the decision since I haven't cruised on her yet and already need to make a call so may just see if the genset can make it through a summer then choose the right unit.

Anyone running two units? advice came from a very experienced boater but I guess in fairness I think he has a pretty large yacht where it might make sense.

AC
__________________
Kadey-Krogen 54
Arthurc is offline   Reply With Quote
Old 06-10-2017, 08:43 PM   #7
Guru
 
Pgitug's Avatar
 
City: Punta Gorda, fl
Country: Usa
Vessel Name: Escapade
Vessel Model: Nordic Tug 37 2002
Join Date: Jan 2015
Posts: 1,147
Get a Northern Lights that is properly sized for your electrical load. We have three AC units, two 12K and a 16K, water heater and 80 amp three battery charger and an 8KW Northern Lights generator is hard to keep a proper load on it.
For reliability, economical parts, easy to work on and QUIET, get the Northern Lights. Click image for larger version

Name:	IMG_1274.jpg
Views:	122
Size:	152.3 KB
ID:	65641Click image for larger version

Name:	IMG_1273.JPG
Views:	122
Size:	35.5 KB
ID:	65642
Pgitug is offline   Reply With Quote
Old 06-10-2017, 09:00 PM   #8
Guru
 
City: Hampton, va
Country: USA
Vessel Name: Didi Mau
Vessel Model: 2003 Ocean Alexander 456
Join Date: Jul 2015
Posts: 915
Our 12kw Northern lights runs our five ACs and everything else. If we are running only two ACs,. We use the 6 kw northern lights.
Gordon J is offline   Reply With Quote
Old 06-10-2017, 09:04 PM   #9
Guru
 
Arthurc's Avatar
 
City: Seattle
Country: USA
Vessel Name: Sea Bear
Vessel Model: Kadey-Krogen 54
Join Date: Sep 2016
Posts: 522
Quote:
Originally Posted by Gordon J View Post
Our 12kw Northern lights runs our five ACs and everything else. If we are running only two ACs,. We use the 6 kw northern lights.
So you have dual gensets? Im hearing conflicting thoughts on two versus one generator.
__________________
Kadey-Krogen 54
Arthurc is offline   Reply With Quote
Old 06-10-2017, 09:12 PM   #10
Guru
 
City: Hampton, va
Country: USA
Vessel Name: Didi Mau
Vessel Model: 2003 Ocean Alexander 456
Join Date: Jul 2015
Posts: 915
The PO put a 6 kw in the boat when she was 7 years old. The smaller generator has 500 more hours than the 14 year old 12 kw. Ib find the smaller one enough for most things and it is cheaper to run.
Gordon J is offline   Reply With Quote
Old 06-10-2017, 09:15 PM   #11
Guru
 
Arthurc's Avatar
 
City: Seattle
Country: USA
Vessel Name: Sea Bear
Vessel Model: Kadey-Krogen 54
Join Date: Sep 2016
Posts: 522
Quote:
Originally Posted by Gordon J View Post
The PO put a 6 kw in the boat when she was 7 years old. The smaller generator has 500 more hours than the 14 year old 12 kw. Ib find the smaller one enough for most things and it is cheaper to run.
Thanks,
the yard is going to try and get a decent read on draw, but in the NW in the summer our heat/ac systems are not stressed at all so may have to go off of spec. I know that 20kw is way too big as the boat originally had an electric range.
AC
__________________
Kadey-Krogen 54
Arthurc is offline   Reply With Quote
Old 06-10-2017, 09:43 PM   #12
Guru
 
twistedtree's Avatar
 
City: Gloucester, MA
Country: USA
Join Date: Jan 2013
Posts: 4,891
Ideally I would get the 20kw running and get some time on the boat to see what your real needs are before dropping $$ on a second generator. Right now it would be an expensive guess.

Dual generators - one small and one large - are common on bigger boats. On most I'm aware of, the smaller gen gets much more use than the big gen. The small unit is typically sized to carry AC and other house loads over night. For bigger loads, the larger generator is run.

We have a 20kw as well and I don't think I've ever been able to get the loading up over 60-70%. I think a 16kw, or perhaps even 12kw with some load management would be plenty for a single generator if you wanted to replace the 20kw completely.

If you want to add a second smaller generator, I'd just make sure it can carry your base heating/cooling load. 5KW might be a bit low. 9kw might get you some more head room.

Before considering a Panda, google around and read about people's experience with them. It's not pretty.

BTW, how old is the 20kw and what brand? I'm surprised you are finding parts hard to get.
__________________
www.MVTanglewood.com
twistedtree is offline   Reply With Quote
Old 06-10-2017, 10:29 PM   #13
Guru
 
Arthurc's Avatar
 
City: Seattle
Country: USA
Vessel Name: Sea Bear
Vessel Model: Kadey-Krogen 54
Join Date: Sep 2016
Posts: 522
It's an Onan 20 mdl4-3cr, guessing 1988
__________________
Kadey-Krogen 54
Arthurc is offline   Reply With Quote
Old 06-10-2017, 11:45 PM   #14
Guru
 
City: Carefree, Arizona
Country: usa
Vessel Name: sunchaser V
Vessel Model: DeFever 48
Join Date: Apr 2008
Posts: 8,020
Arthur

In Seattle, if Sure or Gallery Marine can't find the parts then I'd agree they are hard to find.

If a yard can't find the parts maybe it's because they'd like to do a genset install.
sunchaser is offline   Reply With Quote
Old 06-11-2017, 01:35 AM   #15
Guru
 
Seevee's Avatar
 
City: st pete
Country: usa
Vessel Model: 400 Mainship
Join Date: Sep 2016
Posts: 2,178
I have a question for the generator experts......

How much more does a big generator work to provide XXX load vs a smaller generator carrying the exact same XXX load?

Kinda like a big and small engine propelling a boat the same speed.
__________________
Seevee
Seevee is offline   Reply With Quote
Old 06-11-2017, 02:05 AM   #16
Guru
 
twistedtree's Avatar
 
City: Gloucester, MA
Country: USA
Join Date: Jan 2013
Posts: 4,891
Quote:
Originally Posted by Seevee View Post
I have a question for the generator experts......

How much more does a big generator work to provide XXX load vs a smaller generator carrying the exact same XXX load?

Kinda like a big and small engine propelling a boat the same speed.
About the same in roughly the 20%-100% load range. Figure on 0.1 gph per kw of generated power. And that's actual generated power, NOT the capacity of the generator.

But a small generator running at 50% load will be more fuel efficient than a bigger set running at 10% load.

But is this even what you are asking? Maybe not as I re-read the question.
__________________
www.MVTanglewood.com
twistedtree is offline   Reply With Quote
Old 06-11-2017, 04:02 AM   #17
Guru
 
Join Date: Jun 2014
Posts: 1,274
We owned a Panda. Much of the negative chatter is not worth the time it takes to read. Like any system, so much depends upon a number of factors including installation and use. We all have seen the range of possibilities for either category.
Early Panda's had seawater cooled generator sections that were problematic so people had legitimate complaints there. Beyond that, they remind me of the European autos I spent my life maintaining. They are quiet, capable machines and are capable of very long life.
Bruce
Bruce B is offline   Reply With Quote
Old 06-11-2017, 04:57 AM   #18
Guru
 
Seevee's Avatar
 
City: st pete
Country: usa
Vessel Model: 400 Mainship
Join Date: Sep 2016
Posts: 2,178
Quote:
Originally Posted by twistedtree View Post
About the same in roughly the 20%-100% load range. Figure on 0.1 gph per kw of generated power. And that's actual generated power, NOT the capacity of the generator.

But a small generator running at 50% load will be more fuel efficient than a bigger set running at 10% load.

But is this even what you are asking? Maybe not as I re-read the question.
Twisted,
I'd bet the additional fuel burn for a bigger one would be relatively small overall. And even if it were double, it wouldn't make much economic sense unless Arthurc was full time, long term with the boat.

Arthurc: What are your goals with the boat?
__________________
Seevee
Seevee is offline   Reply With Quote
Old 06-11-2017, 05:17 AM   #19
Moderator Emeritus
 
ksanders's Avatar
 
City: SEWARD ALASKA
Country: USA
Vessel Name: LISAS WAY
Vessel Model: BAYLINER 4788
Join Date: Feb 2011
Posts: 4,410
Regarding fuel burn Vs engine loading...

My Northern Lights 9KW generator is rated at...

.93GPH at full load of 9KW

.51GPH at 1/2 load or 4.5KW

What that means is that you'll burn a little less than 10% more fuel per KW produced if you load the generator to 1/2 load Vs if you load it to full load.

Not bad...
__________________
Kevin Sanders
Bayliner 4788
Seward, Alaska
ksanders is offline   Reply With Quote
Old 06-11-2017, 06:01 AM   #20
Guru
 
City: Hampton, va
Country: USA
Vessel Name: Didi Mau
Vessel Model: 2003 Ocean Alexander 456
Join Date: Jul 2015
Posts: 915
One thing to remember its that generators like to be loaded. Running a 12kw worth one AC and a charger could result in glazed cylinders.

Regarding panda....I had one on last boat. I was generally happy with it. It was a 6 kw. I had no real issues, other than an intermittent issue of it shutting down for now reason that I could discover. I would start it right back up and she would run for hours. The 6kw panda appears to me to be smaller than our 6 kw northern lights. Both equally quiet.

Gordon
__________________

Gordon J is offline   Reply With Quote
Reply

Thread Tools Search this Thread
Search this Thread:

Advanced Search
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off





All times are GMT -5. The time now is 12:11 AM.


Powered by vBulletin® Version 3.8.8 Beta 4
Copyright ©2000 - 2019, vBulletin Solutions, Inc.
Search Engine Optimization by vBSEO 3.6.0
Copyright 2006 - 2012
×