We have been looking at trawlers as our next boat for long range cruising. We have pretty much settled on the 44 Defever as the one we want. I have found one that is a 2001 but it only has an 8 KW on it. I currently have a 10 on a smaller boat. I am thinking a 44 would be more suited with a 12 kw. Question is, is the 8 enough or would power management become a full time job?
__________________
Advertisement

soggy is offline   Reply With Quote
Old 08-06-2013, 08:43 AM   #2
Guru
 
swampu's Avatar


 
City: Biloxi, MS
Country: USA
Vessel Name: Cajun Rose
Vessel Model: Biloxi Lugger
Join Date: Jul 2011
Posts: 1,230
Does the boat have any gas appliances? If it was bult with a 8kw and all that does is run water pumps, ac's and lights than that would be enough. If it has to run a electric oven/range/fridge/heater.ect than it would probably not be enough.
__________________

swampu is offline   Reply With Quote
Old 08-06-2013, 08:54 AM   #3
Guru
 
Moonstruck's Avatar
 
City: Hailing Port: Charleston, SC
Country: USA
Vessel Name: Moonstruck
Vessel Model: Sabre 42 Hardtop Express
Join Date: Nov 2008
Posts: 7,972
An 8 kw will run a lot of stuff. If you have 3 A/Cs and electric cooking, you could have to do a little load management. I would look into adding a 3.5 to 5kw generator to bring on line when needed. Also, if doing island cruising it could serve as backup if the big one goes down. Battery charging and refrigeration are the essentials. A spare battery charger and/or inverter are also good ideas. Don't ask me how I know.

Plus you would have to be careful to keep about a 70% load on a 12kw. Much easier on an 8.
__________________
Don on Moonstruck
Sabre 42 Hardtop Express & Blackfin 25 CC
When cruising life is simpler, but on a grander scale (author unknown)
http://moonstruckblog.wordpress.com/
Moonstruck is offline   Reply With Quote
Old 08-06-2013, 08:57 AM   #4
TF Site Team
 
Larry M's Avatar
 
City: JAX, FL
Country: USA
Vessel Name: Hobo
Vessel Model: Krogen 42-120
Join Date: Nov 2008
Posts: 6,444
Total everything up on the boat you have now. How many amps full on? What does the 44 have over your current boat that would take an additional 3-3.5KW?

We have an 8KW now and we don't load it correctly. Our 2-16KW ACs draw 19 amps, add the charger, hot-water heater and we're less than 50 amps total. Add a toaster or microwave we're getting close, but only for a few minutes. We cook with propane.
Larry M is offline   Reply With Quote
Old 08-06-2013, 09:14 AM   #5
Guru
 
Phil Fill's Avatar
 
City: Everett Wa
Country: US
Vessel Name: Eagle
Vessel Model: Roughwater 58 pilot house
Join Date: Oct 2007
Posts: 2,919
A 8 KW# will produce 60 amps (8,000/120). Most boats are wired for 50 amps, so the 8 KW is sized the boat. The Eagle is wired for 50 amps, so what we did was load share, put timers on high demand items and convert things to DC, propane and diesel to reduce the total amp draw.
Phil Fill is offline   Reply With Quote
Old 08-06-2013, 09:24 AM   #6
TF Site Team
 
ksanders's Avatar
 
City: SEWARD ALASKA
Country: USA
Vessel Name: LISAS WAY
Vessel Model: BAYLINER 4788
Join Date: Feb 2011
Posts: 4,021
We have a 47' boat with all electric appliances including a clothes washer.

Since we are in the PACNW we do not have AC though.

We're running a 9 kw generator and never have to power manage.

consider this...

A 30 amp 120 volt dock connection is only 3.6KW

A 50 amp 120 volt dock connection is only 6KW
__________________
Kevin Sanders
Bayliner 4788
Seward, Alaska
www.mvlisasway.com
ksanders is offline   Reply With Quote
Old 08-06-2013, 10:06 AM   #7
Veteran Member
 
soggy's Avatar
 
City: GA
Country: USA
Vessel Name: Soggy Dollar
Vessel Model: 480 Sea Ray motor yacht
Join Date: Jan 2013
Posts: 38
Thank you all for he insight. I think we will go look at the 44 we found. We locked through this weekend next to a 44. They docked next to us and we got to meet them and see the boat. Great people and a really nice 44, she was a 1990.
soggy is offline   Reply With Quote
Old 08-06-2013, 10:08 AM   #8
Guru
 
djmarchand's Avatar
 
City: Litchfield, Ct and Punta Gorda, Fl
Country: USA
Join Date: Aug 2012
Posts: 3,308
Most boats have a generator that is too big to keep loaded properly.

If you just add up all of your AC loads and size your generator accordingly you will have a tough time keeping that generator loaded to 25% and at night when the A/C load drops off, it may be as low as 10%. That won't be very good for the genset's engine.

So size your generator to run those loads that absolutely have to run simultaneously and do some power management to keep it loaded like don't run the microwave and the hot water heater at the same time, etc.

David
djmarchand is online now   Reply With Quote
Old 08-06-2013, 10:41 AM   #9
TF Site Team
 
Baker's Avatar
 
City: League City, Tx
Country: Texas
Vessel Model: Carver 356
Join Date: Oct 2007
Posts: 5,813
8kw should be just fine!!!
Baker is offline   Reply With Quote
Old 08-06-2013, 10:43 AM   #10
Guru
 
Codger2's Avatar
 
City: San Diego
Country: US
Vessel Name: "Sandpiper"
Vessel Model: 2006 42' Ocean Alexander Sedan
Join Date: Oct 2007
Posts: 5,469
Quote:
Originally Posted by Baker View Post
8kw should be just fine!!
Couldn't agree more! You always have a management situation aboard, relative to your electrical needs, and if you don't, you have too big a boat!
__________________
Codger2

My passion for improving my boat(s) exceeds my desire to constantly cruise them.
Codger2 is online now   Reply With Quote
Old 08-06-2013, 10:44 AM   #11
Guru
 
Aquabelle's Avatar
 
City: sydney
Country: australia
Vessel Name: Aquabelle
Vessel Model: Ocean Alexander Flushdeck
Join Date: Jun 2012
Posts: 620
If you find that the genset is a little small for peak loads (eg running multiple air-con units simultaneously) you might find the best strategy is to invest in a load-sharing inverter/charger of the type made by Victron and MasterVolt. These are capable of adding to genset capacity for peak/surge loads & allow for a smaller genset to do the job. Also means the smaller genset is running better-loaded most of the time...as noted above by others, this is a good thing in its own right.
Aquabelle is online now   Reply With Quote
Old 08-06-2013, 06:13 PM   #12
Senior Member
 
IslandEagle's Avatar
 
City: Toronto & Nanaimo
Country: Canada
Vessel Name: Island Eagle
Vessel Model: DeFever
Join Date: Dec 2012
Posts: 232
Quote:
Originally Posted by Aquabelle View Post
If you find that the genset is a little small for peak loads (eg running multiple air-con units simultaneously) you might find the best strategy is to invest in a load-sharing inverter/charger of the type made by Victron and MasterVolt. These are capable of adding to genset capacity for peak/surge loads & allow for a smaller genset to do the job. Also means the smaller genset is running better-loaded most of the time...as noted above by others, this is a good thing in its own right.
I could not agree more. I have a 6KW and I run it through a Xantrex 4024MC, which has load sharing. It works like a charm.

Scott Welch
Island Eagle
IslandEagle is offline   Reply With Quote
Old 08-06-2013, 08:42 PM   #13
Guru
 
psneeld's Avatar
 
City: Avalon, NJ
Country: USA
Vessel Name: Freedom
Vessel Model: Albin 40
Join Date: Oct 2011
Posts: 16,887
wow...what understatements...8kw isn't nearly enough if you need it and WAYYYY too much if you don't.

People in this forum thought I was crazy for upgrading 2-30 amp services to a 50 amp 120/240 which produces 12,000 watts or 12 KW...and living aboard you can easily exceed that amount like the average house nowadays needs more than a 100 amp service.

Until you know what kind of "hotel services" you will be demanding at anchor or at no electric docks...you have no idea what king of genset you really need. Many boats with propane cooking can get by with a very small genset...mainly to heat water and run the batt charger. But if you like all electric (cooking included) and run a space heater or two during chilly weather...8KW is gonna run out fast.

The real trick is to find out what you need MOST of the time and size the genset to that. If you need more...maybe augment with an inverter or switch some appliances to other energy sources.

You don't want too big or too small..and what are your other options...

Kinda difficult to answer in a forum paragraph or two.
psneeld is offline   Reply With Quote
Old 08-06-2013, 10:50 PM   #14
Guru
 
koliver's Avatar
 
City: Saltspring Island
Country: BC, canada
Vessel Name: Retreat
Vessel Model: C&L 44
Join Date: Nov 2007
Posts: 2,450
Also note what the wiring in the boat will handle. If it comes with an 8KW and you want to upsize to 12, you may need to rewire to handle the extra amperage. Now THAT is a big job.
koliver is online now   Reply With Quote
Old 08-07-2013, 08:41 AM   #15
Guru
 
Portuguese's Avatar
 
City: Salvador - BA
Country: Brazil
Vessel Name: Rainha Jannota
Vessel Model: Curruira 46
Join Date: Jun 2011
Posts: 665
Send a message via MSN to Portuguese
MY boat is 46' and we have a 7 KVA genset. By the way, we are in a tropical country where AC is paramount. We have total 24000 BTU in the boat, MW, charger, one domestic refrigerator and several lamps.
No need for bigger genset
__________________
Now retired and cruising in calm waters
https://www.flickr.com/photos/rainha_jannota/
Portuguese is offline   Reply With Quote
Old 08-07-2013, 11:40 AM   #16
Guru
 
psneeld's Avatar
 
City: Avalon, NJ
Country: USA
Vessel Name: Freedom
Vessel Model: Albin 40
Join Date: Oct 2011
Posts: 16,887
Quote:
Originally Posted by Portuguese View Post
MY boat is 46' and we have a 7 KVA genset. By the way, we are in a tropical country where AC is paramount. We have total 24000 BTU in the boat, MW, charger, one domestic refrigerator and several lamps.
No need for bigger genset
Wow...good deal on the Air Conditoning...

I'm in a relatively cool zone with 32000 BTUs of Air Conditioning on a relatively small 40 footer.

Either way I'm still only at 30 amps for the a ACs and would have enough (either with my 8kw or your 7kw) to run enough other stuff...especially with a propane range.

Most of the time at anchor...unless cooking , running electric heat or air conditioning....much above 5kw is hard to really work hard enough for it to be good for the genset.
psneeld is offline   Reply With Quote
Old 08-08-2013, 04:31 AM   #17
FF
Guru
 
FF's Avatar
 
Join Date: Oct 2007
Posts: 17,244
Question is, is the 8 enough or would power management become a full time job?

8KW is plenty , and at a very modest cost automatic LOAD SHEDDING is easy to install.

Once worked out life is very simple
FF is offline   Reply With Quote
Old 08-08-2013, 05:11 AM   #18
Guru
 
CaptTom's Avatar
 
City: Southern Maine
Country: USA
Vessel Name: Cygnus
Vessel Model: Prairie 36 Coastal Cruiser
Join Date: Dec 2012
Posts: 1,530
Quote:
Originally Posted by FF View Post
...and at a very modest cost automatic LOAD SHEDDING is easy to install.
I looked at this for my house genset once. The theory is very simple, and I'm sure it's easy to install. I'd like to hear more about the "very modest cost" part. As I recall, that's not what I found.
CaptTom is offline   Reply With Quote
Old 08-08-2013, 08:32 AM   #19
TF Site Team
 
ksanders's Avatar
 
City: SEWARD ALASKA
Country: USA
Vessel Name: LISAS WAY
Vessel Model: BAYLINER 4788
Join Date: Feb 2011
Posts: 4,021
Quote:
Originally Posted by FF View Post
Question is, is the 8 enough or would power management become a full time job?

8KW is plenty , and at a very modest cost automatic LOAD SHEDDING is easy to install.

Once worked out life is very simple
Actually I'm in the wholesale power switching business and I have not and cannot find a commercially available automatic load shedding device.

The units that are being deployed are one off devices built from a protective relay and contactors by the electrician. Nobody is happy with this but again nothing is available that works.

There are a couple of units that work in their specific brands of generators, but nobody elses, but there is nothing that I can find that does not utilize propritary signaling.

The concept is simple, but there is nothing is commercially available yet.
If you know of somethingthat is available, and is UL listed, please either post it or PM me, because I can and will add it to our product portfolio.
__________________
Kevin Sanders
Bayliner 4788
Seward, Alaska
www.mvlisasway.com
ksanders is offline   Reply With Quote
Old 08-08-2013, 08:41 AM   #20
Scraping Paint
 
City: Fort Lauderdale
Vessel Model: CHB 48 Zodiac YL 4.2
Join Date: Oct 2007
Posts: 3,804
Quote:
Originally Posted by koliver View Post
Also note what the wiring in the boat will handle. If it comes with an 8KW and you want to upsize to 12, you may need to rewire to handle the extra amperage. Now THAT is a big job.
Unless you increase the consumers (load) you can put a 500kW generator in and not have any problems with the wiring.

Amperage is not pushed down the wires, it is dragged.

With regard to load shedding, I have never used one of their products but Panbo makes a programmable load shedding controller for small boats that might serve the purpose very well.
__________________

RickB is offline   Reply With Quote
Reply

Thread Tools
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off





All times are GMT -5. The time now is 11:02 AM.


Powered by vBulletin® Version 3.8.8 Beta 4
Copyright ©2000 - 2018, vBulletin Solutions, Inc.
Search Engine Optimization by vBSEO 3.6.0
Copyright 2006 - 2012