Restitution
Senior Member
Hello all,
Restitution has an Entec 4200b Gen set (Farymann?)
It will start, run for 10 minutes, then randomly shut off without coughing or shuddering.
This unit has a temp sending unit and oil sending unit that activates a solenoid to shut off fuel if either are not satisfied.
I tested the head and cooling temperature and it runs at 140 or so degrees, but shuts off anyway. I'm unsure how to test the oil sending unit?
Has anybody had this issue. I thought of shunting the temp sending unit while continuously checking the temp to see if perhaps this sending unit is defective. Perhaps do the same with oil sending unit, but I would need to assure that the engine is getting oil?
Other notes: Oil is full (15w 40), antifreeze is full, heat exchanger is working and cleaned out, I installed new raw water and antifreeze impellers.
Thoughts?
Sam
Restitution has an Entec 4200b Gen set (Farymann?)
It will start, run for 10 minutes, then randomly shut off without coughing or shuddering.
This unit has a temp sending unit and oil sending unit that activates a solenoid to shut off fuel if either are not satisfied.
I tested the head and cooling temperature and it runs at 140 or so degrees, but shuts off anyway. I'm unsure how to test the oil sending unit?
Has anybody had this issue. I thought of shunting the temp sending unit while continuously checking the temp to see if perhaps this sending unit is defective. Perhaps do the same with oil sending unit, but I would need to assure that the engine is getting oil?
Other notes: Oil is full (15w 40), antifreeze is full, heat exchanger is working and cleaned out, I installed new raw water and antifreeze impellers.
Thoughts?
Sam