Copper fuel line to rubber fuel line ?

I'm about to install an electric fuel priming pump. Our fuel lines are copper but I'll use rubber fuel hose to splice in the pump.

What I'm wondering is if I need to put hose barbs on the copper line after cutting it or if I can simply slide the rubber hose onto the copper line and double-hose clamp it in place ?

Thanks.
__________________
Advertisement

Trawler_traveler is offline   Reply With Quote
Old 08-21-2019, 11:54 PM   #2
Guru
 
Comodave's Avatar
 
City: Au Gres, MI
Country: US
Vessel Name: Never Say Never
Vessel Model: President 41 DC
Join Date: Jul 2015
Posts: 5,016
I would not trust just putting the hose on the copper without a fitting and a barb fitting. Not sure what ABYC says about it but I would not do it.
__________________

__________________
Boat Nut:
If you are one there is no explanation necessary.
If you arenít one, there is no explanation possible.
Comodave is offline   Reply With Quote
Old 08-22-2019, 01:08 AM   #3
Guru
 
tiltrider1's Avatar
 
City: Seattle
Country: USA
Vessel Name: AZZURRA
Vessel Model: Ocean Alexander 54
Join Date: Aug 2017
Posts: 1,379
If you actually cut the copper tubing you will need to flare the end of the tube. You can buy a tube flaring tool at any automotive store. I recommend using a bubble or double flare.
tiltrider1 is offline   Reply With Quote
Old 08-22-2019, 06:29 AM   #4
Veteran Member
 
Trawler_traveler's Avatar
 
City: Currently Oxnard, Ca.
Country: Where the anchor is
Vessel Name: LAGOM
Vessel Model: Willard 40' Pilothouse
Join Date: Mar 2017
Posts: 36
Quote:
Originally Posted by Comodave View Post
I would not trust just putting the hose on the copper without a fitting and a barb fitting. Not sure what ABYC says about it but I would not do it.
Thanks, that was my thought too.

Quote:
Originally Posted by tiltrider1 View Post
If you actually cut the copper tubing you will need to flare the end of the tube. You can buy a tube flaring tool at any automotive store. I recommend using a bubble or double flare.
I have the bending and flaring tools and will look up how to do a bubble or double flare. Thanks.



-Sven
Trawler_traveler is offline   Reply With Quote
Old 08-22-2019, 07:44 AM   #5
Guru
 
Seevee's Avatar
 
City: st pete
Country: usa
Vessel Model: 400 Mainship
Join Date: Sep 2016
Posts: 2,130
Trawler traveler,


Agree with the others in that you need a fitting there. reverse (double flare) and AN fittings would be my choice.



ABYC has a bunch of specs on this but doesn't say you can use a barb.


Now if you don't have the tools and skills to make up hoses with AN fittings, there's a lot of good hose people that you can use. That's one job I farm out because one little mistake and you can have rubber bits in your fuel.



I don't like clamps on fuel hoses but ABYC permits them, however, must be double and have the properties of ~300 SS, min 1/2 in.
__________________
Seevee
Seevee is offline   Reply With Quote
Old 08-22-2019, 07:54 AM   #6
FF
Guru
 
FF's Avatar
 
Join Date: Oct 2007
Posts: 19,506
Just sliding the tubing into a rubber fuel hose , with 2 clamps works just fine.


A fuel transfer or priming is usually under 10PSI , do no big deal.
FF is offline   Reply With Quote
Old 08-22-2019, 08:01 AM   #7
Guru
 
kchace's Avatar
 
City: Brookline, NH
Country: USA
Vessel Name: Blue Heaven
Vessel Model: Albin 43 classic double cabin, twin 135 Lehmans
Join Date: Sep 2013
Posts: 1,527
If the ID of the hose is a close fit with the copper it will hold very well. Slide the hose on at least 3x the diameter of the copper and clamp it.

Ken
kchace is offline   Reply With Quote
Old 08-22-2019, 08:33 AM   #8
Senior Member
 
City: Rochester, NY
Country: USA
Vessel Name: Hour Glass
Vessel Model: Chris Craft Catalina 381
Join Date: Aug 2019
Posts: 108
If the line is very low pressure or a suction line, as long as it's slid far enough onto the copper and double clamped, I'd be ok with it. If it's under any meaningful pressure, I'd want something more to retain the hose.
rslifkin is online now   Reply With Quote
Old 08-22-2019, 09:17 AM   #9
Guru
 
tiltrider1's Avatar
 
City: Seattle
Country: USA
Vessel Name: AZZURRA
Vessel Model: Ocean Alexander 54
Join Date: Aug 2017
Posts: 1,379
Put a flare in it. That way the clamp has something to seal the hose to. Double clamping is fine as a get home solution but shouldn’t be a permanent fix.
tiltrider1 is offline   Reply With Quote
Old 08-22-2019, 10:45 AM   #10
Guru
 
syjos's Avatar
 
City: Gig Harbor
Country: USA
Vessel Name: Sandpiper
Vessel Model: Bluewater 40 Pilothouse Trawler
Join Date: Nov 2012
Posts: 687
Putting a small flare in the pipe will keep the hose from sliding off.

However, too large a flare will cut into the hose. I put a really small flare on the end of the pipe and smooth the sharp edge with sandpaper. Double flare would be ideal but hard to do a small one.

I double clamp.
syjos is offline   Reply With Quote
Old 08-22-2019, 11:00 AM   #11
Guru
 
HopCar's Avatar
 
City: Miami Florida
Vessel Name: Possum
Vessel Model: Ellis 28
Join Date: Aug 2011
Posts: 4,340
I’m in the camp that would just clamp it on the copper. If you slide the hose on far enough to get two clamps on, it’s not going anywhere.
__________________
Parks Masterson
HopCar is offline   Reply With Quote
Old 08-22-2019, 12:54 PM   #12
Guru
 
Lou_tribal's Avatar
 
City: Quebec
Country: Canada
Vessel Name: Bleuvet
Vessel Model: Custom Built
Join Date: Jan 2016
Posts: 3,459
Quote:
Originally Posted by HopCar View Post
Iím in the camp that would just clamp it on the copper. If you slide the hose on far enough to get two clamps on, itís not going anywhere.


This is what I have. The coper tubing is 2 to 3 inches in the hose and never moved

L
Lou_tribal is offline   Reply With Quote
Old 08-22-2019, 01:51 PM   #13
Guru
 
OldDan1943's Avatar
 
City: Aventura FL
Country: USA
Vessel Name: Kinja
Vessel Model: American Tug 34 #116
Join Date: Oct 2017
Posts: 3,697
Over time diesel will soften the rubber and it may expand. IF you use a rubber hose, make sure it is fuel proof and use 2 clamps. Make a point to inspect the hose and connection.

I agree with Chace, slide the hose down at least 3x the diameter.
__________________
SPAM on a tacco? Pork favor.
OldDan1943 is offline   Reply With Quote
Old 08-22-2019, 03:34 PM   #14
Guru
 
City: Between Oregon and Alaska
Country: US
Vessel Name: Charlie Harper
Vessel Model: Wheeler Shipyard 83'
Join Date: Jun 2016
Posts: 1,524
Quote:
Originally Posted by FF View Post
Just sliding the tubing into a rubber fuel hose , with 2 clamps works just fine.

Ditto




Lepke is offline   Reply With Quote
Old 08-22-2019, 05:21 PM   #15
TG
Senior Member
 
TG's Avatar
 
City: Oceanside, CA
Country: USA
Vessel Name: Tera Grace
Vessel Model: Californian 42 LRC
Join Date: Oct 2012
Posts: 173
I'd use brass compression fittings on the copper and convert to male JIC then use Female JIC push-lok swivels for all the soft fuel line connections.
TG is offline   Reply With Quote
Old 08-22-2019, 06:03 PM   #16
Guru
 
psneeld's Avatar
 
City: AICW
Country: USA
Vessel Name: Freedom
Vessel Model: Albin 40
Join Date: Oct 2011
Posts: 19,594
While I agree that clamping the hose on the copper works fine and has been done on a lot of boats.... I like compression swivel connectors ...makes repairs so much easier.
psneeld is online now   Reply With Quote
Old 08-23-2019, 05:58 AM   #17
FF
Guru
 
FF's Avatar
 
Join Date: Oct 2007
Posts: 19,506
."makes repairs so much easier."

Its true that the rubber over time will become one with the copper tubing.A PIA.

But when purchasing the rubber if 3ft instead of 1 ft is bought, a sharp knife slid on the copper will reduce any take apart tine to near Zero.

The fuel style hose clamps can be reused almost forever., and can be found at most NAPA or auto shops.
FF is offline   Reply With Quote
Old 08-23-2019, 08:23 AM   #18
Senior Member
 
City: Texas
Country: USA
Vessel Model: 37' C&L Double Cabin
Join Date: Feb 2017
Posts: 160
Quote:
Originally Posted by FF View Post
Just sliding the tubing into a rubber fuel hose , with 2 clamps works just fine.


A fuel transfer or priming is usually under 10PSI , do no big deal.
I've done this many times, no problem.
I just slide the rubber a foot or so over the copper and put 3 clamps of it makes you sleep better.
I've also done this with 60psi water piping with good results
Nopistn is offline   Reply With Quote
Old 09-06-2019, 01:35 PM   #19
Senior Member
 
Steve DAntonio's Avatar


 
City: Deltaville
Country: United States
Join Date: Dec 2015
Posts: 330
Quote:
Originally Posted by Comodave View Post
I would not trust just putting the hose on the copper without a fitting and a barb fitting. Not sure what ABYC says about it but I would not do it.
Agreed. ABYC is clear, you cannot place a fuel supply hose over a smooth pipe (there is an exception for fill hoses), it must include serrations, barbs or a bead. Only one clamp is required for fuel hoses other than fill lines.

The Standards say...

33.11 CONNECTIONS - FUEL HOSE
33.11.1 Flexible hose not equipped with permanently attached end fittings, such as swaged sleeve and threaded insert, shall be attached with corrosion resistant metallic clamps.

NOTE: Some USCG Type A hose is not designed to be clamped.

33.11.2 The ID of a hose and the OD of a connecting spud or fitting must meet the specification in H-33 Table II.

33.11.3 Hose shall not be installed on helical threading or knurling that provides a path for fuel leakage.

33.11.4 Clamps depending solely on the spring tension of the metal shall not be used.

33.11.5 Clamps shall be installed to impinge directly on the hose and shall not overlap each other.

33.11.6 Clamps shall be beyond the flare or bead, or fully on serrations where provided, and at least 1/4 inch (6mm) from the end of the hose.

33.11.7 Hose used in the fuel tank fill system shall be secured to pipes (smooth pipes acceptable), spuds or other fittings at each connection, by at least two corrosion resistant metallic clamps with nominal band widths of at least 1/2 inch (12mm).

33.11.8 Hose used in the fuel tank vent system, or the fuel distribution and return line system, shall be secured to a fitting that is formed or machined to provide serrations, barbs or a bead with a minimum height of at least 0.015 inches (0.038 mm)

33.11.9 Hose connections used in the fuel tank vent system or the fuel distribution and return line system shall have at least one corrosion resistant metallic clamp with a minimum nominal band width as indicated in H-33 Table III.

33.11.9.1 All components of hose clamps shall have a resistance to corrosion equal to or greater than 300 series stainless steel.

33.11.9.2 Hose clamps shall be reusable.
__________________
Steve D'Antonio Marine Consulting, Inc.
https://www.stevedmarineconsulting.com
Steve DAntonio is offline   Reply With Quote
Old 09-06-2019, 01:51 PM   #20
Senior Member
 
Steve DAntonio's Avatar


 
City: Deltaville
Country: United States
Join Date: Dec 2015
Posts: 330
Quote:
Originally Posted by TG View Post
I'd use brass compression fittings on the copper and convert to male JIC then use Female JIC push-lok swivels for all the soft fuel line connections.
Just an FYI, PushLoks are designed to NOT be used with clamps, using a clamp cuts into the inside membrane of the hose, as the barbs are very sharp, because they are designed to be used with...no clamps.

PushLok is a Parker product, it is only supposed to be used with PushLok hose, the hose is special designed, somewhat like a Chinese handcuff, to grip the barb.

There is no Type A1 PushLok hose, most installations I encounter use common A1 hose with PushLoks, which technically are incompatible, and most have clamps, which again violates Parker's installation guidelines.

From Parker, "Note: Push-Lok hose is recommended for vacuum applications but not for cooling lines in air conditioners and heat pumps, or for hydraulic applications where extreme pulsations are encountered. Push-Lok is not recommended for any fuel." https://www.parker.com/static_conten.../4281%20B1.pdf

Parker does make a PushLok fuel hose, but it's not labeled A1, and must be used with HY fittings, which must be crimped.

Having said all that, I'll admit that the PushLok fittings are very convenient and make disassembly a snap. If you can find a similar flare fitting with a conventional barb, that would be better. I've never been able to pull any hose off of a PushLok fititng.
__________________

__________________
Steve D'Antonio Marine Consulting, Inc.
https://www.stevedmarineconsulting.com
Steve DAntonio is offline   Reply With Quote
Reply

Thread Tools Search this Thread
Search this Thread:

Advanced Search
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off





All times are GMT -5. The time now is 09:29 AM.


Powered by vBulletin® Version 3.8.8 Beta 4
Copyright ©2000 - 2019, vBulletin Solutions, Inc.
Search Engine Optimization by vBSEO 3.6.0
Copyright 2006 - 2012