AC condensation to bilge or shower sump?

My 36 MK II project is crawling along. I found an outfit that would do a complete refit over the 2 years I have to work with. However their price of well over $200,000 was just a bit outside of what I am willing to put into a 40 year old boat! It appears my best choice is finding and hiring individual contractors. First up was an HVAC guy I have used for years. $7k price estimate for two zone system with each unit installed in the hanging lockers forward and aft. The price seems reasonable since I am confident he will do a very good job. The only question he had was if Gulfstars have a wet bilge or not. If so the condensation can drain there and be dealt with by the pumps. If not then the condensation should drain to the shower sump (difficult to do with forward unit). The boat has been on the hard since I've owned it and the bilge is dry. Where do others have the condensation drain to?
__________________
Advertisement

__________________
--Kurt
2002 Motorcat MC30 "Deuce"
18 knot cruise at 7gph real-time rate.
Gulfstar 36 MKII - 1976 - Work in progress
mixman is offline   Reply With Quote
Old 09-17-2015, 08:49 AM   #2
Senior Member
 
ddalme's Avatar
 
City: LAFAYETTE,LA
Country: USA
Vessel Name: Relenti
Vessel Model: Atlantic 30, 1983
Join Date: Mar 2015
Posts: 406
Funny, I'm thinking about putting in a sump pump and connecting the drains from the condensers to it along with the shower. Everything drains into the bilge and its a mess. Just don't like a wet bilge.
__________________

ddalme is offline   Reply With Quote
Old 09-17-2015, 08:58 AM   #3
Guru
 
Ski in NC's Avatar
 
City: Wilmington, NC
Country: USA
Vessel Name: Louisa
Vessel Model: Custom Built 38
Join Date: Jan 2014
Posts: 3,884
I drain both of mine to the shower sump. Works fine, bilge is dry. There are also small sumps available that can pump from one AC to the shower sump if you can't get a reliable gravity drain to go that far.
Ski in NC is offline   Reply With Quote
Old 09-17-2015, 09:01 AM   #4
Guru
 
Capt.Bill11's Avatar
 
City: Sarasota/Ft. Lauderdale
Country: USA
Join Date: Apr 2014
Posts: 5,422
Pump or drain them over board. You don't want it in your bilge.

I'm kind of surprised you A/C guy would even suggest draining them into the bilge if there are other reasonable ways to route them over board.
Capt.Bill11 is offline   Reply With Quote
Old 09-17-2015, 09:09 AM   #5
Senior Member
 
Gabe n Em's Avatar
 
City: Savannah, GA
Country: USA
Vessel Name: In Sanity
Vessel Model: 1981 Mainship 40'
Join Date: Jan 2015
Posts: 279
Just to play the other side:
We have wet bilges. It got a little funky in the spring before we used the ac a lot but once they started up for the summer, the fresh, changing, water actually helped to keep the odor and funk down. Our bilge pump would go off about 3 or 4 times a day with the ac on so the water never really sat
Gabe n Em is offline   Reply With Quote
Old 09-17-2015, 09:10 AM   #6
Senior Member
 
Gabe n Em's Avatar
 
City: Savannah, GA
Country: USA
Vessel Name: In Sanity
Vessel Model: 1981 Mainship 40'
Join Date: Jan 2015
Posts: 279
That being said, I'd much prefer a completely dry bilge if it was possible
Gabe n Em is offline   Reply With Quote
Old 09-17-2015, 09:15 AM   #7
Guru
 
City: gulf coast
Country: pinellas
Join Date: Jun 2014
Posts: 2,198
Never in the bilge and direct outside via thru hull if at all possible unless you want to have a stinky boat.
bayview is offline   Reply With Quote
Old 09-17-2015, 09:46 AM   #8
Senior Member
 
City: Marathon
Country: Usa
Vessel Name: silver gift
Vessel Model: 45 jefferson
Join Date: Nov 2013
Posts: 202
Have a shower sump pump installed to catch the condensate then pump it overboard, I did this for my a/c and has worked fine. The amount of water in my bilge to activate the pump is a lot. That is a lot of water to have in a normally dry bilge. Water in the boat is a bad thing.
Deckape is offline   Reply With Quote
Old 09-17-2015, 09:56 AM   #9
Guru
 
City: Fort Myers
Country: USA
Join Date: Jul 2013
Posts: 954
I know at one time I saw they had this venturie device that would suck up condensation and discharge it within the raw water line, has anyone seen that or knows if it would work, I think I saw it on Mermaid Air website sometime ago, just a option, but also recommend sump as best method.
Marlinmike is offline   Reply With Quote
Old 09-17-2015, 10:04 AM   #10
Senior Member
 
Join Date: Sep 2015
Posts: 204
Quote:
Originally Posted by Marlinmike View Post
I know at one time I saw they had this venturie device that would suck up condensation and discharge it within the raw water line, has anyone seen that or knows if it would work, I think I saw it on Mermaid Air website sometime ago, just a option, but also recommend sump as best method.
Both of our Cruise Air units have the venturi/slurper device plumbed into the discharge line. Been working great for ten years.
go-planing is offline   Reply With Quote
Old 09-17-2015, 10:16 AM   #11
Guru
 
BobH's Avatar
 
City: Montgomery, TX
Country: USA
Vessel Model: None, but looking
Join Date: Feb 2012
Posts: 778
If the units are above the waterline just put in a small thru hull fitting and drain overboard. We have one for the aft unit but the forward unit sits below the water line and drains into the bilge. I understand the venturi units make a slurping noise which could be annoying.
BobH is offline   Reply With Quote
Old 09-17-2015, 10:53 AM   #12
Senior Member
 
Join Date: Sep 2015
Posts: 204
Quote:
Originally Posted by BobH View Post
I understand the venturi units make a slurping noise which could be annoying.
The salon AC unit on our boat is under the built-in seating. Zero sound from the slurper...ever. Same for the one in the aft cabin as long as the closet door is closed (unit is on the floor of the closet)....and even then only if the unit is turned off while the salon unit is on. (Both units are supplied by one cooling pump, so water circulates when the salon unit is on and the aft cabin unit is off). The slurp sometimes occurs when the condensation tray is out of water. If the unit is on, the hum from the compressor and fan cover it up. In any event, keep the closet door closed and it's undetectable. Noise is a total non-issue unless the AC unit is installed out in the open. Unlikely.
go-planing is offline   Reply With Quote
Old 09-17-2015, 11:09 AM   #13
Guru
 
ranger42c's Avatar
 
City: Maryland
Country: USA
Vessel Model: 42' Sportfish
Join Date: Aug 2013
Posts: 3,157
Our forward AC is plumbed to the shower sump in the forward bilge (which is dry, as is our mid-bilge). Our saloon AC is plumbed directly overboard.


-Chris
__________________
South River, Chesapeake Bay
ranger42c is offline   Reply With Quote
Old 09-17-2015, 08:01 PM   #14
Senior Member
 
mixman's Avatar
 
City: Baltimore
Country: USA
Vessel Name: Deuce
Vessel Model: Motorcat MC30
Join Date: May 2014
Posts: 100
Quote:
Originally Posted by Capt.Bill11 View Post
Pump or drain them over board. You don't want it in your bilge.

I'm kind of surprised you A/C guy would even suggest draining them into the bilge if there are other reasonable ways to route them over board.
Bill, I've been dealing with this guy for years. He will work me in next day when I have need so I trust him. His preference is not bilge but he has a Marine Trader and says they are so wet in the bilge it makes no difference. But he wasn't sure if Gulfstars had the same wet bilge issues. He recommended shower sump but I thought I'd check here. I'm leaning towards direct overboard discharge thanks to all the replies/feedback.
__________________
--Kurt
2002 Motorcat MC30 "Deuce"
18 knot cruise at 7gph real-time rate.
Gulfstar 36 MKII - 1976 - Work in progress
mixman is offline   Reply With Quote
Old 09-17-2015, 08:28 PM   #15
Guru
 
City: Carefree, Arizona
Country: usa
Vessel Name: sunchaser V
Vessel Model: DeFever 48
Join Date: Apr 2008
Posts: 6,361
For those on the thread who have wet bilges, where is the water emanating?
sunchaser is offline   Reply With Quote
Old 09-17-2015, 08:34 PM   #16
Senior Member
 
Gulfstar 36's Avatar
 
City: Kent Island
Country: USA
Vessel Name: Sundowner
Vessel Model: Gulfstar 36 MrkII
Join Date: Jul 2012
Posts: 226
My bilge is dry until I turn on my secondary 10k BTW unit that dumps into the bilge. I do really like the setup on my 36 and I welcome your guy to meet me to see how it is installed. I have a VERY old cruisair 16k split system that sits in the engine room and a 10k all in one Marine Air that is is a saloon locker on the port side. The split has an evaporator up forward and one that divides between the saloon and aft stateroom. Each have their own overboard drains.
Attached Thumbnails
Click image for larger version

Name:	20141021_161641.jpg
Views:	76
Size:	106.5 KB
ID:	44685   Click image for larger version

Name:	20141021_161709.jpg
Views:	92
Size:	90.6 KB
ID:	44686   Click image for larger version

Name:	20141021_161513.jpg
Views:	87
Size:	100.5 KB
ID:	44687  
Gulfstar 36 is offline   Reply With Quote
Old 09-17-2015, 08:47 PM   #17
Senior Member
 
mixman's Avatar
 
City: Baltimore
Country: USA
Vessel Name: Deuce
Vessel Model: Motorcat MC30
Join Date: May 2014
Posts: 100
Hank, his installation ideas off the top of his head were quite similar to how your boat is set up. When you get on my boat tomorrow you'll notice that other than me having twin beds in the aft cabin they are almost identical. He suggested two all in one units. 16000 btu in the hanging locker in the aft cabin vented similar to yours. Then a 12000 btu combi in the locker in the forward birth. The vent for that one will be where yours is as well as one for the forward cabin. Both units will have "Smart Start" so my 4.4kw generator can handle them.
__________________

__________________
--Kurt
2002 Motorcat MC30 "Deuce"
18 knot cruise at 7gph real-time rate.
Gulfstar 36 MKII - 1976 - Work in progress
mixman is offline   Reply With Quote
Reply

Thread Tools
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off





All times are GMT -5. The time now is 12:46 AM.


Powered by vBulletin® Version 3.8.8 Beta 4
Copyright ©2000 - 2017, vBulletin Solutions, Inc.
Search Engine Optimization by vBSEO 3.6.0
Copyright 2006 - 2012