Which to me means that they could be different than "run" cables if the jumpers are less than 6 feet and the runs are longer...again...small patatoes but by suggesting that chart...then a series (jumper) cables of say 6 inches could be substantially smaller than ones at 6 feet.


That table really doesn't say much more than what I believe Kevin was saying and me that using loss and ampacity charts CAN be used to size jumpers...not arbitrarily using... "the same size as your "runs"" concept.....


But as has been said...do what you are gonna do....
__________________
Advertisement

psneeld is online now   Reply With Quote
Old 08-21-2015, 11:23 AM   #22
TF Site Team
 
ksanders's Avatar
 
City: SEWARD ALASKA
Country: USA
Vessel Name: LISAS WAY
Vessel Model: BAYLINER 4788
Join Date: Feb 2011
Posts: 3,956
Quote:
Originally Posted by psneeld View Post
Which to me means that they could be different than "run" cables if the jumpers are less than 6 feet and the runs are longer...again...small patatoes but by suggesting that chart...then a series (jumper) cables of say 6 inches could be substantially smaller than ones at 6 feet.


That table really doesn't say much more than what I believe Kevin was saying and me that using loss and ampacity charts CAN be used to size jumpers...not arbitrarily using... "the same size as your "runs"" concept.....


But as has been said...do what you are gonna do....
Exactly!

There is a huge difference between understanding the electrical and thermal properties of electrical conductors and quoting chapter and verse from a wire size table.

Again... I would probably not tend to undersize a battery jumper simply because I generally have the larger sizes and the crimpers on my boat all the time.

But It can be done and the loads would never know the difference.
__________________

__________________
Kevin Sanders
Bayliner 4788
Seward, Alaska
www.mvlisasway.com
ksanders is offline   Reply With Quote
Old 08-21-2015, 11:42 AM   #23
Guru
 
djmarchand's Avatar
 
City: East Greenwich, RI
Country: USA
Vessel Name: Bella
Vessel Model: Mainship Pilot 34
Join Date: Aug 2012
Posts: 2,883
Hmm! That Trojan table doesn't match other ampacity charts I have seen/used. Look at Ancor's table here: Conductor Sizes | Ancor Ancor makes marine, tinned wire and also should know a thing or two about ampacity. Their table is consistent with others I have seen so maybe Trojan's is based on different conditions/insulation.


But back to the conversation. Sure if I were going to order a new jumper for my recent dual 6V battery installation, I would choose 2/0. But because my house bank will never see more than 220 amps and 99.999% of the time less than 20 amps, I used a #1 jumper that I had on hand. It works, and it is safe.


David
djmarchand is online now   Reply With Quote
Old 08-21-2015, 02:57 PM   #24
QB
Senior Member
 
QB's Avatar
 
City: San Diego and Gabriola
Country: USA and Canada
Vessel Name: Skookum Maru
Vessel Model: Ed Monk design #1924
Join Date: Dec 2011
Posts: 215
Quote:
Originally Posted by ksanders View Post
Wire size tables are based on providing for a certain maximum voltage drop to the load.
Since wire size tables (as opposed to voltage drop calculators) typically do not reference the length of the wire run, that is not true.

Tables like the ones at Marine Wire and Cable: Voltage Drop Calculator are just based on the heat-dissipating capacity of the wire, which depends on its gauge, the temperature rating of the insulation, how many conductors are bundled together, and things like that -- all independent of length.

av8r and caltexflanc are correct about this.
QB is offline   Reply With Quote
Old 08-21-2015, 03:03 PM   #25
Guru
 
psneeld's Avatar
 
City: Avalon, NJ
Country: USA
Vessel Name: Freedom
Vessel Model: Albin 40
Join Date: Oct 2011
Posts: 15,920
Quote:
Originally Posted by QB View Post
Since wire size tables (as opposed to voltage drop calculators) typically do not reference the length of the wire run, that is not true.

Tables like the ones at Marine Wire and Cable: Voltage Drop Calculator are just based on the heat-dissipating capacity of the wire, which depends on its gauge, the temperature rating of the insulation, how many conductors are bundled together, and things like that -- all independent of length.

av8r and caltexflanc are correct about this.
OK....how do YOU base what wire size to use on a run?
psneeld is online now   Reply With Quote
Old 08-23-2015, 12:14 PM   #26
Guru
 
JDCAVE's Avatar
 
City: Lions Bay, BC
Country: Canada
Vessel Name: Phoenix Hunter
Vessel Model: Kadey Krogen 42 (1985)
Join Date: Apr 2011
Posts: 1,613
Wire size short/long run

I had his same discussion with my marine electrician. We will likely increase cable size in my house bank to 4/0 when we rewire the bank for a more optimal configuration this fall. The "optimal configuration" change is to ensure the batteries in the bank contribute equally to the loads on the system. The reason for 4/0 is because of the length of the cable run to the inverter charger and the associated voltage drop when under large loading. Since the current cable size is 2/0, I asked if the connectors between batteries could remain at 2/0 since the current between the individual batteries would be considerably less than that of the mail cables to the inverter charger. He indicated that while that could be done, he urged best practice would be to switch everything over to 4/0 all the way to the inverter charger.


Jim
Sent from my iPad using Trawler Forum
JDCAVE is offline   Reply With Quote
Old 08-23-2015, 05:25 PM   #27
Guru
 
Xsbank's Avatar
 
City: Pender Harbour, BC
Country: Canada
Vessel Name: Gwaii Haanas
Vessel Model: Vancouver Shipyards Custom Aluminum 52
Join Date: Sep 2013
Posts: 2,447
Interesting, this is one of the few things in boating where you don't have to guess, follow an old wive's tale, scatter chicken bones, listen to Bob who heard it from Sam who heard that somebody they heard of had a fire... More controversy than what quantity of bear spray you should pack in the bush. Cut and dried. Easy apps, good information in Calder etc.

Obviously, the only correct answer is to use only 4/0 cable, for everything. Everything, then there can be no problems.
__________________
Don't believe everything that you think.
Xsbank is offline   Reply With Quote
Old 08-24-2015, 07:17 AM   #28
FF
Guru
 
FF's Avatar
 
Join Date: Oct 2007
Posts: 16,534
Samr reasoning holds for a refit.

Buy a spool of #10 and most everything will be happy

Little downside in cost if you buy a big volume , same terminal ends for everything and with a set of stick on numbers from the Alarm folks , its easy to keep track, and create a schematic.

Only downside is #10 might weigh a bit more than #22 for a light.
FF is offline   Reply With Quote
Old 08-24-2015, 02:11 PM   #29
Guru
 
caltexflanc's Avatar
 
City: North Carolina for now
Country: USA
Vessel Name: Small Incentive
Vessel Model: Boston Whaler 130 Sport
Join Date: Aug 2011
Posts: 3,802
What's the old saying? "The nice thing about banging your head against a wall is that it feels so good when you stop!"

Quote:
I asked if the connectors between batteries could remain at 2/0 since the current between the individual batteries would be considerably less than that of the mail cables to the inverter charger.
Not so, current, which is measured in amperes, will be the same all across all the battery-related cables.

Quote:
But because my house bank will never see more than 220 amps and 99.999% of the time less than 20 amps, I used a #1 jumper that I had on hand. It works, and it is safe.
It is "safe" only if the battery bank is fused correctly to protect the #1. No big sustained surge items in your system? No inverter?
__________________
George

"There's the Right Way, the Wrong Way, and what some guy says he's gotten away with"
caltexflanc is online now   Reply With Quote
Old 08-24-2015, 02:39 PM   #30
Guru
 
psneeld's Avatar
 
City: Avalon, NJ
Country: USA
Vessel Name: Freedom
Vessel Model: Albin 40
Join Date: Oct 2011
Posts: 15,920
Who here puts circuit protection on their jumpers between 6 V batteries?


yep...that wall is hard.....
psneeld is online now   Reply With Quote
Old 08-24-2015, 03:27 PM   #31
TF Site Team
 
Larry M's Avatar
 
City: JAX, FL
Country: USA
Vessel Name: Hobo
Vessel Model: Krogen 42-120
Join Date: Nov 2008
Posts: 5,747
Quote:
Originally Posted by JDCAVE View Post
...The reason for 4/0 is because of the length of the cable run to the inverter charger and the associated voltage drop when under large loading. Since the current cable size is 2/0, I asked if the connectors between batteries could remain at 2/0 since the current between the individual batteries would be considerably less than that of the mail cables to the inverter charger. He indicated that while that could be done, he urged best practice would be to switch everything over to 4/0 all the way to the inverter charger...
Jim: We went 4/0 from the negative and positive of the battery bank to the inverter as per the manufacturer. I would have had a difficult time with the battery posts if I had done all the interconnecting with 4/0 because of the lug thickness. Check your post type and height. After 7 years with a 2800 watt invertor, the 2/0 interconnecting cables has worked with no issues.

side note: Our T-105's had ELPT (embedded low profile) posts. If our batteries had the EHPT (embedded high profile) posts, I would have been OK.
Attached Thumbnails
Click image for larger version

Name:	Battery Cables 002.jpg
Views:	35
Size:	122.0 KB
ID:	43507  
Larry M is offline   Reply With Quote
Old 08-24-2015, 08:24 PM   #32
QB
Senior Member
 
QB's Avatar
 
City: San Diego and Gabriola
Country: USA and Canada
Vessel Name: Skookum Maru
Vessel Model: Ed Monk design #1924
Join Date: Dec 2011
Posts: 215
Quote:
Originally Posted by psneeld View Post
OK....how do YOU base what wire size to use on a run?
Use the tables to determine a minimum wire size. Use a voltage drop calculator to see if you need to go larger, not to try to get away with smaller.
QB is offline   Reply With Quote
Old 08-24-2015, 08:40 PM   #33
Guru
 
psneeld's Avatar
 
City: Avalon, NJ
Country: USA
Vessel Name: Freedom
Vessel Model: Albin 40
Join Date: Oct 2011
Posts: 15,920
Quote:
Originally Posted by QB View Post
Use the tables to determine a minimum wire size. Use a voltage drop calculator to see if you need to go larger, not to try to get away with smaller.
Right...so we all use the same tables...not sure what your point was to Kevin.
psneeld is online now   Reply With Quote
Old 08-25-2015, 11:49 AM   #34
Guru
 
JDCAVE's Avatar
 
City: Lions Bay, BC
Country: Canada
Vessel Name: Phoenix Hunter
Vessel Model: Kadey Krogen 42 (1985)
Join Date: Apr 2011
Posts: 1,613
Quote:
Originally Posted by caltexflanc View Post
What's the old saying? "The nice thing about banging your head against a wall is that it feels so good when you stop!"

Not so, current, which is measured in amperes, will be the same all across all the battery-related cables.

Clearly my electrician agrees with you!

Larry I'm not sure what posts I have. Probably the low ones I think. I guess I'll cross that bridge when I get to it!

For now I have the 2/0 cabling, but we need to do the load tests to see what the voltage drop is with higher inverter loads. I've only run the microwave occasionally and for a maximum of 3 minutes at a time. It's a 1000 watt model I believe so we haven't gone to the full potential of the inverter. The cables remain cool with the full charger load.


Jim
Sent from my iPad using Trawler Forum
JDCAVE is offline   Reply With Quote
Old 08-25-2015, 12:12 PM   #35
TF Site Team
 
ksanders's Avatar
 
City: SEWARD ALASKA
Country: USA
Vessel Name: LISAS WAY
Vessel Model: BAYLINER 4788
Join Date: Feb 2011
Posts: 3,956
Guys this is not really worth arguing to me.

No, I generally would not choose to use a smaller size inter cell jumper than my load cables.

I reserve the right to do so, simply because from a technical standpoint I can.

I am an old man and have spent a lifetime making a living thinking about among other things wire size and battery banks so I'm not too worried about my decisions in this area.

For the laymen out there... Use a wire size table. That way you will always get the right size cable for the job.
__________________
Kevin Sanders
Bayliner 4788
Seward, Alaska
www.mvlisasway.com
ksanders is offline   Reply With Quote
Old 08-26-2015, 06:47 AM   #36
FF
Guru
 
FF's Avatar
 
Join Date: Oct 2007
Posts: 16,534
To keep the heat down on those terminals , you might consider using copper nuts ,

as their ampacity is far better than SS.

Harder to find tho,,,,
__________________

FF is offline   Reply With Quote
Reply

Thread Tools
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off





All times are GMT -5. The time now is 10:55 AM.


Powered by vBulletin® Version 3.8.8 Beta 4
Copyright ©2000 - 2017, vBulletin Solutions, Inc.
Search Engine Optimization by vBSEO 3.6.0
Copyright 2006 - 2012