Old 12-17-2013, 10:32 PM   #1
Member
 
Ray.Arwin's Avatar
 
City: Kuching
Country: Malaysia
Join Date: Dec 2013
Posts: 8
Westerbeke Transformer Regulator KVA

How to get transformer regulator KVA? i need to rewind the transformer, but the electrical workshop need this KVA to quote price. I'm new to this Westerbeke diesel generator. Model is 12 BTDC-514.
__________________
Advertisement

Ray.Arwin is offline   Reply With Quote
Old 12-17-2013, 11:20 PM   #2
Guru
 
Bob Cofer's Avatar
 
City: Bellingham
Country: US
Vessel Name: Ebbtide
Vessel Model: '72 Grand Banks
Join Date: Aug 2013
Posts: 1,028
Single phase is calculated:
Current in amps volts 1000 = kva

3 phase is calculated:
Current in amps line to line volts 1000 = kva
__________________

__________________
What kind of boat is that?
Bob Cofer is online now   Reply With Quote
Old 12-17-2013, 11:35 PM   #3
Member
 
Ray.Arwin's Avatar
 
City: Kuching
Country: Malaysia
Join Date: Dec 2013
Posts: 8
Quote:
Originally Posted by Bob Cofer View Post
Single phase is calculated:
Current in amps volts 1000 = kva

3 phase is calculated:
Current in amps line to line volts 1000 = kva
Is the outcome calculation result is for transformer regulator KVA? The generator is single phase, amps is 52.2 x 230volts 1000= 12kva. Find attached the transformer picture. Thank you very much.
Attached Thumbnails
Click image for larger version

Name:	IMG_0559.JPG
Views:	131
Size:	121.4 KB
ID:	25836  
Ray.Arwin is offline   Reply With Quote
Old 12-17-2013, 11:36 PM   #4
TF Site Team
 
ksanders's Avatar
 
City: SEWARD ALASKA
Country: USA
Vessel Name: LISAS WAY
Vessel Model: BAYLINER 4788
Join Date: Feb 2011
Posts: 3,952
Quote:
Originally Posted by Ray.Arwin View Post
How to get transformer regulator KVA? i need to rewind the transformer, but the electrical workshop need this KVA to quote price. I'm new to this Westerbeke diesel generator. Model is 12 BTDC-514.
A transformer regulator is a little thing. It can generally fit in the palm of your hand. Maybe a handful but about hand size.

If the transformer regulator in your generator has failed then buy a replacement unit. Its not something you would generally get rewound.

BTW, do you know its the transformer?
More often the bridge rectifier is what fails in a transformer regulator.

If you cannot find a replacement then goto a solid state voltage regulator. There are several off the shelf units that will work, but I really like the Marathon SE350. Basler also makes a great lineup of regulators.


Quote:
Originally Posted by Bob Cofer View Post
Single phase is calculated:
Current in amps volts 1000 = kva

3 phase is calculated:
Current in amps line to line volts 1000 = kva
3 phase power is calculated as:

Phase to phase volts * amps * the square root of three

In a wye connected system you can also use:

Line to neutral volts * phase A amps
+
Line to neutral volts * phase B amps
+
Line to neutral volts * phase C amps

These calculations result in Volt Amps

To convert volt amps to KVA or kilovolt amps divide by 1000

To convert volt amps to power multiply by the cosine of the phase angle.
__________________
Kevin Sanders
Bayliner 4788
Seward, Alaska
www.mvlisasway.com
ksanders is offline   Reply With Quote
Old 12-17-2013, 11:40 PM   #5
Guru
 
Bob Cofer's Avatar
 
City: Bellingham
Country: US
Vessel Name: Ebbtide
Vessel Model: '72 Grand Banks
Join Date: Aug 2013
Posts: 1,028
12 kva is correct. You may discover that the transformer is marked on the bottom or backside also. Let me do a bit of research and I will get back to you.

Bob
__________________
What kind of boat is that?
Bob Cofer is online now   Reply With Quote
Old 12-17-2013, 11:44 PM   #6
TF Site Team
 
ksanders's Avatar
 
City: SEWARD ALASKA
Country: USA
Vessel Name: LISAS WAY
Vessel Model: BAYLINER 4788
Join Date: Feb 2011
Posts: 3,952
Quote:
Originally Posted by Bob Cofer View Post
12 kva is correct. You may discover that the transformer is marked on the bottom or backside also. Let me do a bit of research and I will get back to you.

Bob
Bob, see my post above, and look at the photo the OP posted.

That IS NOT a 12KVA transformer.
__________________
Kevin Sanders
Bayliner 4788
Seward, Alaska
www.mvlisasway.com
ksanders is offline   Reply With Quote
Old 12-18-2013, 12:10 AM   #7
Guru
 
Bob Cofer's Avatar
 
City: Bellingham
Country: US
Vessel Name: Ebbtide
Vessel Model: '72 Grand Banks
Join Date: Aug 2013
Posts: 1,028
That part is called the compound transformer and does a couple of things. Provides a means of excitation voltage for the generator and through the magic of ohm's law give you the proper output voltage based on how the leads are connected. So it is not just a simple replacement part. Your genset output is indeed 12kva but that transformer is not. You will most likely need to get the OEM part in order to fix it. The information is on page 76 of the Westerbeke Manual but the page is too big to post on this site. Go to westerbeke, marine generators, engines, Official Site and you can download it for free.

Bob
__________________
What kind of boat is that?
Bob Cofer is online now   Reply With Quote
Old 12-18-2013, 12:12 AM   #8
Guru
 
Bob Cofer's Avatar
 
City: Bellingham
Country: US
Vessel Name: Ebbtide
Vessel Model: '72 Grand Banks
Join Date: Aug 2013
Posts: 1,028
Kevin,

See my post above, you are correct.

Bob
__________________
What kind of boat is that?
Bob Cofer is online now   Reply With Quote
Old 12-18-2013, 12:17 AM   #9
Member
 
Ray.Arwin's Avatar
 
City: Kuching
Country: Malaysia
Join Date: Dec 2013
Posts: 8
Quote:
Originally Posted by ksanders View Post
A transformer regulator is a little thing. It can generally fit in the palm of your hand. Maybe a handful but about hand size.

If the transformer regulator in your generator has failed then buy a replacement unit. Its not something you would generally get rewound.

BTW, do you know its the transformer?
More often the bridge rectifier is what fails in a transformer regulator.

If you cannot find a replacement then goto a solid state voltage regulator. There are several off the shelf units that will work, but I really like the Marathon SE350. Basler also makes a great lineup of regulators.




3 phase power is calculated as:

Phase to phase volts * amps * the square root of three

In a wye connected system you can also use:

Line to neutral volts * phase A amps
+
Line to neutral volts * phase B amps
+
Line to neutral volts * phase C amps

These calculations result in Volt Amps

To convert volt amps to KVA or kilovolt amps divide by 1000

To convert volt amps to power multiply by the cosine of the phase angle.
I'm not very sure if this is the transformer regulator failure, but i need to check the coil rewinding due to i found corrosion at the transformer steel bar, shims etc and this make me curious about the transformer regulator condition and performance. FYI, in Malaysia its difficult to get the parts and will be so expensive. So, i decided to rewound.

Renewed the bridge rectifier, rewound the main stator and check the fuel pump + governor (still in good condition). Now my problem is, the alternator itself unable to achieve the useable output voltage when loaded. Without load output is 230 volt, loaded only with 1 acu 24,000 btu, suddenly output will dropped to 202 volt. Installed and test with AVR, the output is very constant at 230 volt even loaded with 2 or more acu. But can't afford the AVR cost, hope this make everything clear and i really need some advice on this problem. Thank you.
Ray.Arwin is offline   Reply With Quote
Old 12-18-2013, 12:25 AM   #10
Guru
 
Bob Cofer's Avatar
 
City: Bellingham
Country: US
Vessel Name: Ebbtide
Vessel Model: '72 Grand Banks
Join Date: Aug 2013
Posts: 1,028
Download the Technical Manual from the above site. It gives detailed testing parameters and procedures that should help you. You may want to also check the governor for proper performance. Utility power is only required to be + or - ten percent of the nominal voltage and you are outside of that range so there is most likely a problem with the transformer. Did you reinstall the shims exactly as they were removed?

Bob
__________________
What kind of boat is that?
Bob Cofer is online now   Reply With Quote
Old 12-18-2013, 12:34 AM   #11
Member
 
Ray.Arwin's Avatar
 
City: Kuching
Country: Malaysia
Join Date: Dec 2013
Posts: 8
Quote:
Originally Posted by Bob Cofer View Post
Download the Technical Manual from the above site. It gives detailed testing parameters and procedures that should help you. You may want to also check the governor for proper performance. Utility power is only required to be + or - ten percent of the nominal voltage and you are outside of that range so there is most likely a problem with the transformer. Did you reinstall the shims exactly as they were removed?

Bob
Downloaded and many thanx for the info. The shim is in the correct position, i have added shims to increase the free run output voltage and its work. But still cant achieve the useable voltage. So, now i will rewind the compound transformer and see what is the end result. Back to the earlier question, i still cant get the transformer KVA. Any idea?
Ray.Arwin is offline   Reply With Quote
Old 12-18-2013, 12:41 AM   #12
Guru
 
Bob Cofer's Avatar
 
City: Bellingham
Country: US
Vessel Name: Ebbtide
Vessel Model: '72 Grand Banks
Join Date: Aug 2013
Posts: 1,028
Not really. It will be a fractional number at best. Take it in to your rewind shop and they will have to disassemble it and count the windings and wire sizes. Best of luck.

PS Perhaps give technical support a call and see if the information is available?

Bob
__________________
What kind of boat is that?
Bob Cofer is online now   Reply With Quote
Old 12-18-2013, 01:01 AM   #13
TF Site Team
 
ksanders's Avatar
 
City: SEWARD ALASKA
Country: USA
Vessel Name: LISAS WAY
Vessel Model: BAYLINER 4788
Join Date: Feb 2011
Posts: 3,952
Quote:
Originally Posted by Ray.Arwin View Post
I'm not very sure if this is the transformer regulator failure, but i need to check the coil rewinding due to i found corrosion at the transformer steel bar, shims etc and this make me curious about the transformer regulator condition and performance. FYI, in Malaysia its difficult to get the parts and will be so expensive. So, i decided to rewound.

Renewed the bridge rectifier, rewound the main stator and check the fuel pump + governor (still in good condition). Now my problem is, the alternator itself unable to achieve the useable output voltage when loaded. Without load output is 230 volt, loaded only with 1 acu 24,000 btu, suddenly output will dropped to 202 volt. Installed and test with AVR, the output is very constant at 230 volt even loaded with 2 or more acu. But can't afford the AVR cost, hope this make everything clear and i really need some advice on this problem. Thank you.
$50 you can buy a SE350 knock off on ebay.

Thats a pretty versitile regulator and will probably work fine. Download the instruction manual and compare it with the westerbeke spec.

I think the SE350 will do up to 73 volts DC and up to 3 amps

I'd check the spec on the westerbeke exciter and or the westerbeke avr to see if it'll work.

Or better yet research the westerbeke avr and buy a knockoff of that unit.
__________________
Kevin Sanders
Bayliner 4788
Seward, Alaska
www.mvlisasway.com
ksanders is offline   Reply With Quote
Old 12-18-2013, 06:43 AM   #14
Scraping Paint
 
City: Fort Lauderdale
Vessel Model: CHB 48 Zodiac YL 4.2
Join Date: Oct 2007
Posts: 3,804
Quote:
Originally Posted by ksanders View Post
$50 you can buy a SE350 knock off on ebay.
Or, try these guys:

online voltage regulator and static exciter catalog

They offer a huge range of AVRs and exciters, they also have some of the best tech support I have ever had the pleasure to contact and have pulled me out of generator regulation problems in the past. I recommend them without hesitation and suggest calling them for advice.
RickB is offline   Reply With Quote
Old 12-18-2013, 09:26 AM   #15
Scraping Paint
 
City: Fort Lauderdale
Vessel Model: CHB 48 Zodiac YL 4.2
Join Date: Oct 2007
Posts: 3,804
Forgot to add this link:

http://www.westerbeke.com/Troublesho...ing_manual.pdf
RickB is offline   Reply With Quote
Old 12-18-2013, 11:30 AM   #16
TF Site Team
 
ksanders's Avatar
 
City: SEWARD ALASKA
Country: USA
Vessel Name: LISAS WAY
Vessel Model: BAYLINER 4788
Join Date: Feb 2011
Posts: 3,952
Quote:
Originally Posted by RickB View Post
Yep, my first response when I get a call like this is generally RTFM
__________________
Kevin Sanders
Bayliner 4788
Seward, Alaska
www.mvlisasway.com
ksanders is offline   Reply With Quote
Old 12-19-2013, 07:08 AM   #17
Scraping Paint
 
City: Fort Lauderdale
Vessel Model: CHB 48 Zodiac YL 4.2
Join Date: Oct 2007
Posts: 3,804
Quote:
Originally Posted by ksanders View Post
Yep, my first response when I get a call like this is generally RTFM
I tried that the other day (RTFM on its own line followed by some links) and it got edited out by someone ... at least they didn't delete the entire post that time since it contained some good information.
__________________

RickB is offline   Reply With Quote
Reply

Thread Tools
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off





All times are GMT -5. The time now is 11:48 PM.


Powered by vBulletin® Version 3.8.8 Beta 4
Copyright ©2000 - 2017, vBulletin Solutions, Inc.
Search Engine Optimization by vBSEO 3.6.0
Copyright 2006 - 2012