Two breakers inline?

Why would the PO of the boat wire these two breakers "in-line"? The cabling on the bus-bar is labelled "capstan" which I presume is for the winches on the boat deck. One breaker is rated 100 amp and the other is rated 50 amps. The windlass has separate breaker.

Jim
Attached Thumbnails
Click image for larger version

Name:	Tandem Breakers for Capstan small.JPG
Views:	88
Size:	36.8 KB
ID:	35007  
__________________
Advertisement

JDCAVE is offline   Reply With Quote
Old 12-02-2014, 03:58 PM   #2
Guru
 
siestakey's Avatar
 
City: Sarasota,FL/Thomasville,GA
Country: USA
Vessel Name: Steppin Stone IV
Vessel Model: Marine Trader Kelly Trawler 46
Join Date: Jul 2013
Posts: 1,271
Send a message via Skype™ to siestakey
is there a chance you can get the pic straight on close like this and then one further back

maybe I am missing something
__________________

siestakey is offline   Reply With Quote
Old 12-02-2014, 04:12 PM   #3
Guru
 
JDCAVE's Avatar
 
City: Lions Bay, BC
Country: Canada
Vessel Name: Phoenix Hunter
Vessel Model: Kadey Krogen 42 (1985)
Join Date: Apr 2011
Posts: 1,610
This is another photo, further back. The breakers in question begin at the top of this photo.

Jim
Attached Thumbnails
Click image for larger version

Name:	Bus Bar DC Panel 2 Smaller.jpg
Views:	90
Size:	94.3 KB
ID:	35009  
JDCAVE is offline   Reply With Quote
Old 12-02-2014, 04:19 PM   #4
Guru
 
High Wire's Avatar
 
City: Cape May, NJ and Englewood, FL
Country: USA
Vessel Name: Irish Lady
Join Date: Dec 2007
Posts: 1,600
It appears that they are wired in parallel. The current to the load will be divided through both breakers. The lowest rated will trip first, shift all of the load to the second which will trip if above the setpoint . Go down to one breaker of the appropriate setpoint.
__________________
Archie
1984 Monk 36 Hull #46
Englewood, FL and Cape May, NJ
High Wire is offline   Reply With Quote
Old 12-02-2014, 04:22 PM   #5
Guru
 
psneeld's Avatar
 
City: Avalon, NJ
Country: USA
Vessel Name: Freedom
Vessel Model: Albin 40
Join Date: Oct 2011
Posts: 15,902
Maybe wanted 150 amp breaker, didn"t have one handy so that happened thinking in parallel you will probably get the necessary amps without tripping either. I don't know enough theory to say why it will of wouldn't work.
psneeld is online now   Reply With Quote
Old 12-02-2014, 04:22 PM   #6
Guru
 
siestakey's Avatar
 
City: Sarasota,FL/Thomasville,GA
Country: USA
Vessel Name: Steppin Stone IV
Vessel Model: Marine Trader Kelly Trawler 46
Join Date: Jul 2013
Posts: 1,271
Send a message via Skype™ to siestakey
Quote:
Originally Posted by High Wire View Post
It appears that they are wired in parallel. The current to the load will be divided through both breakers. The lowest rated will trip first, shift all of the load to the second which will trip if above the setpoint . Go down to one breaker of the appropriate setpoint.
That is what I am seeing
siestakey is offline   Reply With Quote
Old 12-02-2014, 04:25 PM   #7
Guru
 
psneeld's Avatar
 
City: Avalon, NJ
Country: USA
Vessel Name: Freedom
Vessel Model: Albin 40
Join Date: Oct 2011
Posts: 15,902
so what amps can you see at the windlass with that setup without tripping a breaker?
psneeld is online now   Reply With Quote
Old 12-02-2014, 04:32 PM   #8
Veteran Member
 
Cat Daddy's Avatar
 
City: Boyd, Texas
Country: USA
Vessel Name: Cat Daddy
Vessel Model: PDQ mv/34
Join Date: Jan 2014
Posts: 99
I agree with Archie, when the 50 amp trips the 100 amp will not be far behind. Seems like a lot of work to make those short connector pieces (crimp lugs & heat shrink), one breaker may have cost less.

Rafe
Cat Daddy is offline   Reply With Quote
Old 12-02-2014, 04:39 PM   #9
Guru
 
JDCAVE's Avatar
 
City: Lions Bay, BC
Country: Canada
Vessel Name: Phoenix Hunter
Vessel Model: Kadey Krogen 42 (1985)
Join Date: Apr 2011
Posts: 1,610
I don't know what amps those winches draw/are rated at. One of them failed last summer and I managed to get it "remanned"...
Winch problem

So, what is the best approach? Go to a single breaker? One of these is 50 amp and the other is 100 amps?

I phoned "Blue Sea" and the tech I talked to said the expert on this topic was on his lunch break. I sent an email with the photo and hopefully they will get back to me.

Jim
JDCAVE is offline   Reply With Quote
Old 12-02-2014, 05:00 PM   #10
Guru
 
High Wire's Avatar
 
City: Cape May, NJ and Englewood, FL
Country: USA
Vessel Name: Irish Lady
Join Date: Dec 2007
Posts: 1,600
Quote:
Originally Posted by JDCAVE View Post
I don't know what amps those winches draw/are rated at. One of them failed last summer and I managed to get it "remanned"...
Winch problem

So, what is the best approach? Go to a single breaker? One of these is 50 amp and the other is 100 amps?

I phoned "Blue Sea" and the tech I talked to said the expert on this topic was on his lunch break. I sent an email with the photo and hopefully they will get back to me.

Jim
One breaker only. The winch installation guide should state the required amp value.
Putting 2 breakers in parallel (or series for that matter) has no value. 50 plus 100 does not equal 150 in the breaker world. I'll add that its worse than no value because you will have no idea what load current will finally trip the breakers. Best guess is somewhere north of 100 amps.
__________________
Archie
1984 Monk 36 Hull #46
Englewood, FL and Cape May, NJ
High Wire is offline   Reply With Quote
Old 12-02-2014, 05:07 PM   #11
Guru
 
psneeld's Avatar
 
City: Avalon, NJ
Country: USA
Vessel Name: Freedom
Vessel Model: Albin 40
Join Date: Oct 2011
Posts: 15,902
Quote:
Originally Posted by JDCAVE View Post
I don't know what amps those winches draw/are rated at. One of them failed last summer and I managed to get it "remanned"...
Winch problem

So, what is the best approach? Go to a single breaker? One of these is 50 amp and the other is 100 amps?

I phoned "Blue Sea" and the tech I talked to said the expert on this topic was on his lunch break. I sent an email with the photo and hopefully they will get back to me.

Jim
I would have and did just use one 150 amp breaker on my boat...but I'm not so sure that your current setup won't work and be just as safe.
psneeld is online now   Reply With Quote
Old 12-02-2014, 05:12 PM   #12
Guru
 
JDCAVE's Avatar
 
City: Lions Bay, BC
Country: Canada
Vessel Name: Phoenix Hunter
Vessel Model: Kadey Krogen 42 (1985)
Join Date: Apr 2011
Posts: 1,610
Thanks Archie. That can be a spring project. I intend to replace the winches this spring with a Warn model (DC 1200) as per the advice of S3 Systems (Seattle).

Jim
JDCAVE is offline   Reply With Quote
Old 12-02-2014, 05:22 PM   #13
Guru
 
twistedtree's Avatar
 
City: Gloucester, MA
Country: USA
Join Date: Jan 2013
Posts: 3,193
Agreed that what's there is a bad practice. It will completey open somewhere between 100 and 150A, but there is no way to know in advance exactly (or even approximately) where. And it's possible the 50A would trip, but the load continued by the 100A until it trips. Check the manual for the windless or whatever it powers and replace with a single properly sized breaker.
__________________
www.MVTanglewood.com
twistedtree is offline   Reply With Quote
Old 12-02-2014, 05:23 PM   #14
Veteran Member
 
Cat Daddy's Avatar
 
City: Boyd, Texas
Country: USA
Vessel Name: Cat Daddy
Vessel Model: PDQ mv/34
Join Date: Jan 2014
Posts: 99
One more thing to consider. The breaker also protects the wire and needs to be sized accordingly. If the winch needs a 150 amp but the wire is only rated for 100 amps, that's a problem.

Rafe
Cat Daddy is offline   Reply With Quote
Old 12-02-2014, 05:35 PM   #15
Guru
 
twistedtree's Avatar
 
City: Gloucester, MA
Country: USA
Join Date: Jan 2013
Posts: 3,193
Quote:
Originally Posted by Cat Daddy View Post
One more thing to consider. The breaker also protects the wire and needs to be sized accordingly. If the winch needs a 150 amp but the wire is only rated for 100 amps, that's a problem.

Rafe
Yes, good reminder
__________________
www.MVTanglewood.com
twistedtree is offline   Reply With Quote
Old 12-02-2014, 05:37 PM   #16
Guru
 
City: gulf coast
Country: pinellas
Join Date: Jun 2014
Posts: 2,199
You have to get into some high theory to guess the results of breakers in parallel but it is not going to yield the sum of two ratings.
bayview is offline   Reply With Quote
Old 12-02-2014, 05:54 PM   #17
Senior Member
 
Sealife's Avatar
 
City: In transit
Country: From USA
Vessel Name: Sea life
Vessel Model: Krogen 42 #61
Join Date: Nov 2013
Posts: 378
Jim,
What was the thought for the DC1200? I believe the KK42 was engineered around a 500# lift for mast/boom rigging and stability. Just curious because I am currently installing DC800 on my KK42.

Scott
Sealife is offline   Reply With Quote
Old 12-02-2014, 06:08 PM   #18
Guru
 
JDCAVE's Avatar
 
City: Lions Bay, BC
Country: Canada
Vessel Name: Phoenix Hunter
Vessel Model: Kadey Krogen 42 (1985)
Join Date: Apr 2011
Posts: 1,610
Scott: Good point. I'm not certain. I have a KK42 and my skiff is probably only 350 lbs, max. I will contact S3 before I proceed. They came to our "Krogin" in Anacortes. They do all the commissioning for new KK's on the west coast. They probably recommended the Warn 1200 because that's what they put on for the new builds, which are typically bigger vessels than mine.

Jim
JDCAVE is offline   Reply With Quote
Old 12-02-2014, 06:19 PM   #19
Guru
 
psneeld's Avatar
 
City: Avalon, NJ
Country: USA
Vessel Name: Freedom
Vessel Model: Albin 40
Join Date: Oct 2011
Posts: 15,902
Quote:
Originally Posted by bayview View Post
You have to get into some high theory to guess the results of breakers in parallel but it is not going to yield the sum of two ratings.
After researching several electrical engineering websites/forums...

Seems that....

1. Parallel fusing in the US is not allowed for circuit protection but OK in devices.

2. Parallel fusing is fairly common in some devices and works great if the fuses are the same size.

3. Using different sized fused can result in all kinds of tripping sequences...but as long as the largest fuse is smaller than the ampacity of the wire... and the combined total is smaller also...there isn't a lot "danger" involved that a quick read showed.

So I guess if the setup has been working so far...other than following standards it seems to be a crapshoot.


Parallel fusing with equal fuses CBs doesn't seem complicated but there are efficiency issues that need to be addressed and what appears to be another constant or so if you really want perfection. Not the same size...well...it's rarely discussed.
psneeld is online now   Reply With Quote
Old 12-02-2014, 07:06 PM   #20
Guru
 
High Wire's Avatar
 
City: Cape May, NJ and Englewood, FL
Country: USA
Vessel Name: Irish Lady
Join Date: Dec 2007
Posts: 1,600
We use series breakers in a nuclear power plant for motor loads that penetrate primary containment. One breaker is setup specifically to protect the motor. Because its a motor, there are design conditions that must be met and verified through periodic testing. The other breaker is sized specifically to prevent damage to the primary containment penetration and has completely different design and testing requirements. Neither breaker alone can meet both sets of requirements and both must operate independantly. Other than that, I can honestly say that in 40+ years in the electrical field, I've never seen 2 breakers used for one load that werent mechanically ganged together to trip at the same time until this post. Me thinks the installer was more of a mechanical guy.
__________________

__________________
Archie
1984 Monk 36 Hull #46
Englewood, FL and Cape May, NJ
High Wire is offline   Reply With Quote
Reply

Thread Tools
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off





All times are GMT -5. The time now is 06:01 PM.


Powered by vBulletin® Version 3.8.8 Beta 4
Copyright ©2000 - 2017, vBulletin Solutions, Inc.
Search Engine Optimization by vBSEO 3.6.0
Copyright 2006 - 2012