Old 12-03-2014, 06:23 AM   #21
Guru
 
O C Diver's Avatar
 
City: Fort Myers, FL... Summers in Crisfield, MD
Country: USA
Vessel Name: Slow Hand
Vessel Model: Cherubini Independence 45
Join Date: Dec 2010
Posts: 4,820
While I have never done it, it would seem to me that with a 50 and a 100 amp breaker, both would trip around 110 amps. With parallel circuits of equal wire gauge size, the current would flow equally over each conductor (path of least resistance). When the 50 amp breaker saw 55 amps +/-, it would trip sheading its load to the 100 amp breaker which would now trip with a 110 amp load.

Ted
__________________
Advertisement

__________________
Blog: mvslowhand.com
I'm tired of fast moves, I've got a slow groove, on my mind.....
I want to spend some time, Not come and go in a heated rush.....
"Slow Hand" by The Pointer Sisters
O C Diver is offline   Reply With Quote
Old 12-03-2014, 08:15 AM   #22
TF Site Team
 
Larry M's Avatar
 
City: JAX, FL
Country: USA
Vessel Name: Hobo
Vessel Model: Krogen 42-120
Join Date: Nov 2008
Posts: 5,745
Our Warn DC1200 hoist lists max draw at 100 amps and 1200 lbf. It is part of a davit system, not the factory boom and mast from Krogen. Does your lifting system have 2 winches?
__________________

Larry M is online now   Reply With Quote
Old 12-03-2014, 09:14 AM   #23
Guru
 
windmill29130's Avatar
 
City: Little River SC
Vessel Name: JAZ
Vessel Model: Ta Chaio/CT35
Join Date: Jan 2011
Posts: 716
Per NEC 240.8: "Fuses and circuit breakers shall be permitted to be connected in parallel where they are factory assembled in parallel and listed as a unit. Individual fuses, circuit breakers, or combinations thereof shall not otherwise be connected in parallel."
__________________
Tracy & Susie Hellman 1985 Ta Chiao CT 35
Twin Lehman Super 90's Westerbeke 4.4kw
Lightkeepers Marina -Little River, SC
windmill29130 is offline   Reply With Quote
Old 12-03-2014, 11:08 AM   #24
Guru
 
JDCAVE's Avatar
 
City: Lions Bay, BC
Country: Canada
Vessel Name: Phoenix Hunter
Vessel Model: Kadey Krogen 42 (1985)
Join Date: Apr 2011
Posts: 1,612
Yes Larry, it has two winches. I only operate one at a time. These are the "Rule" winches.


Jim
Sent from my iPad using Trawler Forum
JDCAVE is offline   Reply With Quote
Old 12-03-2014, 11:35 AM   #25
Senior Member
 
greysailor's Avatar
 
City: Matagorda Bay
Country: Republic of Texas - USA
Vessel Name: Salty
Vessel Model: 2005 Defever 44
Join Date: May 2013
Posts: 100
Quote:
Originally Posted by High Wire View Post
We use series breakers in a nuclear power plant for motor loads that penetrate primary containment. One breaker is setup specifically to protect the motor. Because its a motor, there are design conditions that must be met and verified through periodic testing. The other breaker is sized specifically to prevent damage to the primary containment penetration and has completely different design and testing requirements. Neither breaker alone can meet both sets of requirements and both must operate independantly. Other than that, I can honestly say that in 40+ years in the electrical field, I've never seen 2 breakers used for one load that werent mechanically ganged together to trip at the same time until this post. Me thinks the installer was more of a mechanical guy.
Wow! Archie you sure brought back memories of an earlier life for me....countless hours sitting in front of an old SR76 or EPOCH test set shooting penetration breakers during refueling outages! Nice to know there are a few old power nukes still afloat.
Back OP's subject...I agree this was probably something configured by a "boatyard electrical expert", and lacks basis in both theory and application....Replace the two breakers with one that is properly sized for the load.
greysailor is offline   Reply With Quote
Old 12-03-2014, 12:35 PM   #26
Guru
 
JDCAVE's Avatar
 
City: Lions Bay, BC
Country: Canada
Vessel Name: Phoenix Hunter
Vessel Model: Kadey Krogen 42 (1985)
Join Date: Apr 2011
Posts: 1,612
Thanks all! I will go ahead and replace that breaker combination, but will wait until I replace the winches as the new ones may have a different requirement. They won't be used much in the next few months anyways.

The setup seemed odd, even for this electrical lightweight!

Jim
JDCAVE is offline   Reply With Quote
Old 12-03-2014, 03:37 PM   #27
FF
Guru
 
FF's Avatar
 
Join Date: Oct 2007
Posts: 16,531
>Thanks all! I will go ahead and replace that breaker combination, but will wait until I replace the winches as the new ones may have a different requirement.<

The CB are usually sized to protect the wiring , not the user.

A slow blow fuse works best for that.
__________________

FF is offline   Reply With Quote
Reply

Thread Tools
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off





All times are GMT -5. The time now is 05:15 PM.


Powered by vBulletin® Version 3.8.8 Beta 4
Copyright ©2000 - 2017, vBulletin Solutions, Inc.
Search Engine Optimization by vBSEO 3.6.0
Copyright 2006 - 2012