Solar Installation Guide

This is a presentation that I gave at the PSGBOA Rendezvous. It is basic but gives an idea of the process.

On Ebbtide 600w gives us a nice surplus and we can now make ice via the inverter while on the hook!

Safe travels,
Bob & Jill
Attached Files
File Type: pdf Solar Presentation.pdf (2.30 MB, 289 views)
__________________
Advertisement

__________________
What kind of boat is that?
Bob Cofer is offline   Reply With Quote
Old 06-15-2017, 11:48 AM   #2
TF Site Team
 
Larry M's Avatar
 
City: JAX, FL
Country: USA
Vessel Name: Hobo
Vessel Model: Krogen 42-120
Join Date: Nov 2008
Posts: 7,895
Bob: A nice write up. It would be a great addition to the Trawler Forum Library Systems Section.
__________________

Larry M is online now   Reply With Quote
Old 06-15-2017, 12:13 PM   #3
Guru
 
djmarchand's Avatar
 
City: Litchfield, Ct/Punta Gorda, Fl
Country: USA
Vessel Model: Atlas Pompano 23
Join Date: Aug 2012
Posts: 4,832
Bob and Jill:

Thanks for posting that presentation. How about posting it to the library section of this forum, so it won't get lost. Click on the icon in the upper right of this screen, pick the section and follow the directions.

Let me offer some clarification and comment, all in the spirit of positive feedback:

1. Often we don't know or even care whether a panel is mono or poly, just if it fits in the available space and gives the output we want.

2. Perhaps you could give more specifics about matching panel and controller specs, like making sure that your controller can deal with the Voc of the panel. I also have noticed that on-line panel vendors no longer advise upspecing the controller by 25% over panel wattage div 12. Have controllers gotten better, vendors less honest or what has changed.

3. For the life of me I can't see why you need overcurrent protection on the panel side of the controller. The wire should be sized to take the Isc current so what can go wrong?

4. I liked your explanation of series, paralles and series/parallel wiring.

5. I also liked your statement that for panels less than 200 watts, MPPT controllers were overkill and PWM controllers would uually do just fine. I just did a mental spec of a 300 watt system with either two 150 watt 12V nominal panels or one 300 watt 24V nominal panel. The single panel system obviously needed a MPPT controller to charge 12V batteries, but the controller cost more than the panel.

But today 24V nominal voltage panels have really gotten cheap. I just saw one for $.77 per watt, but since these big panels cannot be shipped UPS, motor freight charges can kill you if you are just buying one.

David
djmarchand is offline   Reply With Quote
Old 06-15-2017, 03:35 PM   #4
Scraping Paint
 
City: CT
Country: US
Join Date: Mar 2017
Posts: 963
Quote:
Originally Posted by djmarchand View Post
on-line panel vendors no longer advise upspecing the controller by 25% over panel wattage div 12. Have controllers gotten better, vendors less honest or what has changed.
The top-tier vendors are usually very clear which specs you can "push" and which are hard limits. I find most of the time the total voltage on MPPT units is strict, especially if you're tilting and might get cold clear days in winter.

Total amps is usually safe to exceed by a bit, increasing your average daily output but "wasting" some output in peak conditions.

For example, the two Bogart SC-2030s controlled by my Trimetric will accept up to 45A maximum each to avoid damage to the controller, but will never output more than 31A each.
john61ct is offline   Reply With Quote
Old 06-15-2017, 04:58 PM   #5
Guru
 
Bob Cofer's Avatar
 
City: Caimanera
Country: Cuba
Vessel Name: Seafarer
Vessel Model: 1926 56 Winslow RDMY
Join Date: Aug 2013
Posts: 1,183
Larry,

You can add it if you like.
__________________
What kind of boat is that?
Bob Cofer is offline   Reply With Quote
Old 06-15-2017, 05:06 PM   #6
TF Site Team
 
Larry M's Avatar
 
City: JAX, FL
Country: USA
Vessel Name: Hobo
Vessel Model: Krogen 42-120
Join Date: Nov 2008
Posts: 7,895
Quote:
Originally Posted by Bob Cofer View Post
Larry,

You can add it if you like.
Done. Thanks again.
Larry M is online now   Reply With Quote
Old 06-15-2017, 08:30 PM   #7
Veteran Member
 
2geer's Avatar
 
City: South Hero, VT
Country: United States
Vessel Name: Stout
Vessel Model: Kadey Krogen 42-087
Join Date: Feb 2017
Posts: 29
We just completed a solar install using Victron Energy's MPPT charge controller technology. We used (2) SunPower X21-345 panels in series mounted on the pilothouse roof. With the help of Victron's calculator we were able to safely match the charge controller for the installation. The calculator is at:

https://www.victronenergy.com/blog/2...ge-regulators/

The above file allows you to enter the specific parameters of the panel(s) you plan to use.

Because of our existing investment in our (2) Victron's Multiplus units and Color GX display it made sense to go in this direction. With a recent test on anchor, we are very pleased with the results - no generator needed...

See attached pic...

Dave & Lisa Geer
M/V Stout KK42-087
Attached Thumbnails
Click image for larger version

Name:	IMG_4405.jpg
Views:	117
Size:	124.9 KB
ID:	65799  
2geer is offline   Reply With Quote
Old 06-15-2017, 08:50 PM   #8
Scraping Paint
 
City: CT
Country: US
Join Date: Mar 2017
Posts: 963
Very nice aesthetics for solar there!
john61ct is offline   Reply With Quote
Old 06-15-2017, 09:40 PM   #9
Guru
 
City: Satsuma FL/Daytona Beach Shores
Country: United States
Vessel Name: No Mo Trawla
Vessel Model: Hurricane SS188
Join Date: Jul 2014
Posts: 2,183
Quote:
Originally Posted by 2geer View Post
We just completed a solar install using Victron Energy's MPPT charge controller technology. We used (2) SunPower X21-345 panels in series mounted on the pilothouse roof. With the help of Victron's calculator we were able to safely match the charge controller for the installation. The calculator is at:

https://www.victronenergy.com/blog/2...ge-regulators/

The above file allows you to enter the specific parameters of the panel(s) you plan to use.

Because of our existing investment in our (2) Victron's Multiplus units and Color GX display it made sense to go in this direction. With a recent test on anchor, we are very pleased with the results - no generator needed...

See attached pic...
Are there any issues on the fly bridge of glare or heat from the panels in your setup?
__________________
Buffalo Bluff Light 28
Donsan is offline   Reply With Quote
Old 06-15-2017, 11:22 PM   #10
Veteran Member
 
2geer's Avatar
 
City: South Hero, VT
Country: United States
Vessel Name: Stout
Vessel Model: Kadey Krogen 42-087
Join Date: Feb 2017
Posts: 29
We have had them operational less than a month. No problems with glare or heat as of yet. Spent the day the pic was taken operating from the flybridge with no issue.

The view is taken looking south into Willsboro Bay on Lake Champlain approximately here:

https://www.google.com/maps/dir/44.4...73.4079684,14z

Dave Geer
2geer is offline   Reply With Quote
Old 06-16-2017, 04:15 AM   #11
Senior Member
 
Ex Sailor's Avatar
 
City: Toronto
Country: Canada
Join Date: Nov 2015
Posts: 271
Quote:
Originally Posted by Bob Cofer View Post
This is a presentation that I gave at the PSGBOA Rendezvous. It is basic but gives an idea of the process.

On Ebbtide 600w gives us a nice surplus and we can now make ice via the inverter while on the hook!

Safe travels,
Bob & Jill

Great presentation ! thanks for sharing.

I'm surprised that no mention was made of RFI generated by some ( obscure or off shore made ) MPPT controllers. I have seen it first hand where it will CHOKE all your VHF / FM / TV etc. In the end, you get what you pay for. fb
Ex Sailor is offline   Reply With Quote
Old 06-17-2017, 09:46 PM   #12
Guru
 
foggysail's Avatar
 
City: Ashland, MA
Country: United States
Vessel Model: 1990 Silverton 40 aftcabin
Join Date: Jul 2016
Posts: 1,089
I read Bob Cofer's Solar Presentation pdf and found it informative although I do have an exception. That exception pertains to shading and how it affects an entire string. This topic got me into a discussion with John61ct in another forum.

There is a belief out there that alludes one to believe that series strings should be avoided because of the calamitous impact that results from shading. I say that the problems caused by shading are small compared to operating lower Vpp panels in parallel. Parallel operation imposes demands for heavier wiring from the the panels to the controller. If one skimps on the wire installation between the panels and the controller.....for this discussion I am focusing only on an MPPT....... there will be times of maximum sun that results in the controller operating off the Vpp resulting in lost power transfer. This can last for hours!

OK, now consider shading. Bob's pdf claims that shading of one cell kills the entire string of series panels. That was true before bypass diodes were introduced and most panels today have them. Panel bypass diodes allows current to flow as if that shaded panel was absent. Yes, there will be a performance hit although the hit will be less as the number of panels in series increases. There will still be a loss though.

But we are focusing on shading and most shading is not constant so the shading impact will only last for the length of time the panel is shaded. Not so with compromised wiring. OK, sure! Just increase the wire sizes and avoid the problem. Well, there again the shade problem is still there so you can still lose a panel. Also how many of you have pulled #6 or worse #4 wires from panels to a controller? On my boat I would need to enlarge.... no! make that drill new holes in the fiberglass for the heavy wires to pass through. Big PITA!

So although I acknowledge that shading is a problem, over all it is something that I can live with because the shade is not permanent...momentary in most cases.

I am in the process of upgrading my solar. I have so far installed a new Victron 150-70 controller (downgraded my earlier plan for 150-85) and am in the process of purchasing 4 new Canadian CS6K295MS panels. My intention is to wire them in either series/parallel or just series. I am leaning toward just going series so my Vpp will be in the 120-130 volt range, well within the new controllers 150 volt limit. And by the way, when operating at these higher voltages it behooves all to consider adding a panel disconnect switch. I recommend switches anyway even with lower voltages. Think what can happen to a finger or a wrist if ring or a wrist watch shorts out a panel's current especially if the current is high.

Anyway, just wanted to share my technical thoughts on this topic and I know many will still believe shading is a death knell to series strings.
foggysail is offline   Reply With Quote
Old 06-17-2017, 10:05 PM   #13
Guru
 
psneeld's Avatar
 
City: AICW
Country: USA
Vessel Name: Freedom
Vessel Model: Albin 40
Join Date: Oct 2011
Posts: 19,983
For newbies....yes a lot of good tech advice...

A lot of which is frogs hair.

I bought 4 100W panels, put them in parralel with adequate wiring and the give away PWM controller.

Works great, wired per diagrams, hinged install on 2 panels allows for maximum output, 2 moveable panels allows for even more flexibility.

Sure ..... read all the literature and expert advice....go that way if desired, but my system has all but eliminated my daily genset runs and does the trick without higher tier engineering.

No need for an engineering degree and worry about frogs hair, you can buy 400W of panels and be up and running in a day. Renology from Amazon for less than $600..

Not saying there isnt perfection in a solar system...just dont be afraid to jump in, as it is really pretty simple if you let it be.
psneeld is online now   Reply With Quote
Old 06-17-2017, 10:09 PM   #14
Scraping Paint
 
City: CT
Country: US
Join Date: Mar 2017
Posts: 963
I was never arguing S vs P.

I'm saying putting the panels on a greater number of smaller controllers

ideally, a 75/15 on each, or

next best, a 100/30 per pair

would give you significantly higher total power output per day in real life due to sail/rigging shadows passing over the panels

The extra expense is minimal if any

Yes the wiring a bit more trouble.

Up to you if the difference is worth it, but please don't try to deny there is a difference.

In the old days you just couldn't get four excellent full-featured MPPT controllers for ~$400 delivered.

But now you can.
john61ct is offline   Reply With Quote
Old 06-17-2017, 10:36 PM   #15
Guru
 
dhays's Avatar
 
City: Gig Harbor
Country: United States
Vessel Name: Kinship
Vessel Model: North Pacific 43
Join Date: May 2015
Posts: 8,433
I appreciate reading these discussions because I learn a bit more each time. The presentation by Bob was very helpful.

Eventually, I want to do what Rebel did and put two panels on my PH roof (that is Pilothouse not Principle Home). Reading the information on solar is very helpful.
__________________
Regards,

Dave
SPOT page
dhays is offline   Reply With Quote
Old 06-18-2017, 12:14 AM   #16
Guru
 
twistedtree's Avatar
 
City: Gloucester, MA
Country: USA
Join Date: Jan 2013
Posts: 4,939
There has been a really good discussion on Cruisers Forum on serial vs parallel, including an excellent model run by a very competent electrical engineer. There are infinite shading scenarios to consider, and different panel cell layouts, so there are no absolutes. But assuming modern panels with bypass and blocking diodes, and assuming a good MPPT charge controller, series wiring almost always wins. Not always, but you have much better chances. How you physically arrange your panels matters too.

Per-panel charge controllers is probably the ultimate, if the costs etc work for you.
__________________
www.MVTanglewood.com
twistedtree is offline   Reply With Quote
Old 06-19-2017, 05:29 AM   #17
Guru
 
Pgitug's Avatar
 
City: Punta Gorda, fl
Country: Usa
Vessel Name: Escapade
Vessel Model: Nordic Tug 37 2002
Join Date: Jan 2015
Posts: 1,148
I just took two solar panels off my new to me tug. The controller had failed and cooked the house batteries with high voltage. Also the previous owner had no means to wash the boat section under the panels so The fiberglass now has black mold growth that has stained the gel coat. I am not a fan of what it takes to operate solar on a trawler.
Pgitug is offline   Reply With Quote
Old 06-19-2017, 06:00 AM   #18
Guru
 
psneeld's Avatar
 
City: AICW
Country: USA
Vessel Name: Freedom
Vessel Model: Albin 40
Join Date: Oct 2011
Posts: 19,983
Poor installs making maintenance difficult or an issue is bad for any system, not just solar.

Seems to be way more satisfied than dissatisfied solar users.
psneeld is online now   Reply With Quote
Old 06-19-2017, 06:43 AM   #19
Guru
 
City: Satsuma FL/Daytona Beach Shores
Country: United States
Vessel Name: No Mo Trawla
Vessel Model: Hurricane SS188
Join Date: Jul 2014
Posts: 2,183
Quote:
Originally Posted by psneeld View Post
Poor installs making maintenance difficult or an issue is bad for any system, not just solar.

Seems to be way more satisfied than dissatisfied solar users.
Do you have suggestions on how to clean under the panels?
__________________
Buffalo Bluff Light 28
Donsan is offline   Reply With Quote
Old 06-19-2017, 07:01 AM   #20
Guru
 
psneeld's Avatar
 
City: AICW
Country: USA
Vessel Name: Freedom
Vessel Model: Albin 40
Join Date: Oct 2011
Posts: 19,983
Quote:
Originally Posted by Donsan View Post
Do you have suggestions on how to clean under the panels?
If it was my install and they weren't high enough to get under, they would be hinged on one side and pinned on the other.

Even better, they would be pinned on both sides for easy removal and have leg supports to possibly be tilted for better sun angle.
__________________

psneeld is online now   Reply With Quote
Reply

Thread Tools Search this Thread
Search this Thread:

Advanced Search
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On