My new to me Taiwanese Trawler has two 30amp power receptacles. One feeds the main (original) panel and the other feeds an added panel. The 5 months I have owned the boat I have had 2 cords plugged into the shore power pedestal and all has been well. I just moved to a larger slip which has a single 50amp outlet instead of the double 30amp my old slip had. I purchased a new Marinco splitter that plugs into the 50 and y's into two 30's. When I plug my boat in and flip the breaker on it immediately trips the breaker, tried the next pedestal over and same thing. Using only one cord in ANY position ( either side of splitter or either boat receptacle or either cord) all in well. Plug the 2nd cord in and immediate breaker trip when powered on. Once I tried to plug in the 2nd cord to the boat while the breaker was on and huge bang!&pop!. This is not some quirky gfci issue.
ANY IDEAS ?
__________________
Advertisement

BigTime is offline   Reply With Quote
Old 04-30-2019, 09:05 PM   #2
Guru
 
Ski in NC's Avatar
 
City: Wilmington, NC
Country: USA
Vessel Name: Louisa
Vessel Model: Custom Built 38
Join Date: Jan 2014
Posts: 4,998
Sounds like L1 on one cord and L1 on the other are somehow tied together. If they are by chance in phase, no problem. If they are out of phase as they certainly would be on a 50A through a splitter, dead short.

Sounds like you have some funky wiring.

Plug in one cord, then test the receptacle for the other cord (not connected) and see if there are volts. Should be none, but suspect there are.
__________________

Ski in NC is online now   Reply With Quote
Old 05-01-2019, 05:52 AM   #3
Member
 
City: Jacksonville
Country: United States
Vessel Name: Water Lily
Vessel Model: TMC Custom 41 Trawler & S-2 10.3 Sail
Join Date: Nov 2018
Posts: 17
Thanks
I will check for voltage when I go to the boat Thursday evening.
BigTime is offline   Reply With Quote
Old 05-01-2019, 07:14 AM   #4
Guru
 
Cigatoo's Avatar
 
City: Narragansett Bay
Country: New England
Vessel Model: Grand Banks 36
Join Date: Sep 2016
Posts: 660
Checking for voltage as Ski said is a good thought.

Another thought......In the event that you have only one cord plugged in do you have the option of connecting the 2 ac panels together? Sometimes there is a switch that would allow this so that you can supply 30 amps to both panels with one 30 amp cord. If that switch could be accidentally left on (normally their is a lock out to prevent this from occurring) that would cause your problem.
Cigatoo is offline   Reply With Quote
Old 05-01-2019, 08:46 AM   #5
TF Site Team
 
Bacchus's Avatar
 
City: Seneca Lake NY
Country: US
Vessel Name: Bacchus
Vessel Model: MS 34 HT Trawler
Join Date: Nov 2014
Posts: 2,572
Is the pedestal 50A 240V or 120V?
Same for splitter.... 2 different 50A "Y" splitters and they arent interchangable.
interchangeable.
__________________
Don
2008 MS 34 HT Trawler
"Bacchus"
Bacchus is offline   Reply With Quote
Old 05-01-2019, 09:26 AM   #6
Veteran Member
 
City: Raymond NH
Country: USA
Vessel Name: Mischief Managed II
Vessel Model: 1992 Tollycraft 44 CPMY
Join Date: Oct 2018
Posts: 79
My guess is that the two 120V services are tied together on the hot sides in the boat. I'm pretty sure they can be tied together on the neutrals, so I would say it's probably just a polarity issue. With the boat completely disconnected from shore power and no inverter or genset operating, check continuity between the hot inputs on both 30 amp inlets. They should not be connected.



That said, my boat has a switch that combines the two panels in case I want both panels fed from one source and that switch left on would cause the issue you are experiencing. If you have a switch that does this, make sure it's off.

Mischief Managed is offline   Reply With Quote
Old 05-02-2019, 05:40 AM   #7
Member
 
City: Jacksonville
Country: United States
Vessel Name: Water Lily
Vessel Model: TMC Custom 41 Trawler & S-2 10.3 Sail
Join Date: Nov 2018
Posts: 17
Thanks very much for the help. I slipped down to the boat last night and this is what I found.
With one plug plugged in I had full voltage on the hot of the unused receptacle and everything from both panels was working. I then started thinking about a switch.

Last week , before I changed slips, I had discovered an issue with the selector switch for GEN-OFF-SHORE. I had been trying to get my generator to operate the boat I would start the genset with selector on SHORE and every time I would switch to GEN the main breaker physically located on the genset would trip. I accidentally discovered that if I first powered down the boat by turning off the power pedestal then bringing on the genset by selecting GEN all was fine and the generator would run everything on the boat.
So with this in mind I discovered that by switching from SHORE to OFF I no longer had voltage at the unused receptacle and could plug my second cord in without issue. I did note that with only one cord plugged in it would always power both panels on either SHORE or OFF position.

I will investigate further when I have both daylight and a clearer mind, but a resolution may have to wait for my next month visit to the yard, I'm not sure I have the understanding to work this out.
Thanks again for the help.
BigTime is offline   Reply With Quote
Old 05-02-2019, 06:30 AM   #8
Guru
 
psneeld's Avatar
 
City: Avalon, NJ
Country: USA
Vessel Name: Freedom
Vessel Model: Albin 40
Join Date: Oct 2011
Posts: 18,731
Just a quick read without full understanding of your issue...


My boat had twin 30A that were separate on the shore power setting on the selector switch.


When on genset, a jumper carried power to both 30A panel sections.


Where your selector switch (rotary or slide over breakers) is, look for a set of jumpers (power and neutral).


Take some pics of the back of this area and it may be easier to help in diagnosing your issue.
psneeld is offline   Reply With Quote
Old 05-02-2019, 07:22 AM   #9
Senior Member
 
City: Green Cove Springs, Florida
Country: USA
Join Date: Feb 2012
Posts: 303
Send a message via Skype™ to bglad
I think Ski & Psneeld are on the right track.

120-volt boats that have two 30-amp cords or single 240/50 will typically have the AC generator wired straight 120 (versus 240). The transfer switch on the generator side will have a jumper between the two hot legs. The shore side should not. Sounds like in your case the shore side has the jumper too. No problem in phase. You get more power. Out of phase you get something else!
bglad is offline   Reply With Quote
Old 05-02-2019, 08:19 AM   #10
Veteran Member
 
City: Raymond NH
Country: USA
Vessel Name: Mischief Managed II
Vessel Model: 1992 Tollycraft 44 CPMY
Join Date: Oct 2018
Posts: 79
Quote:
Originally Posted by BigTime View Post
Thanks very much for the help. I slipped down to the boat last night and this is what I found.
With one plug plugged in I had full voltage on the hot of the unused receptacle and everything from both panels was working. I then started thinking about a switch.

Last week , before I changed slips, I had discovered an issue with the selector switch for GEN-OFF-SHORE. I had been trying to get my generator to operate the boat I would start the genset with selector on SHORE and every time I would switch to GEN the main breaker physically located on the genset would trip. I accidentally discovered that if I first powered down the boat by turning off the power pedestal then bringing on the genset by selecting GEN all was fine and the generator would run everything on the boat.
So with this in mind I discovered that by switching from SHORE to OFF I no longer had voltage at the unused receptacle and could plug my second cord in without issue. I did note that with only one cord plugged in it would always power both panels on either SHORE or OFF position.

I will investigate further when I have both daylight and a clearer mind, but a resolution may have to wait for my next month visit to the yard, I'm not sure I have the understanding to work this out.
Thanks again for the help.

Seems like somebody re-purposed your GEN-OFF_SHORE switch to tie the two panels together when in either GEN or SHORE. It would be a great use of your time to make a wiring diagram of how it is right now and make some new labels for the switch.
Mischief Managed is offline   Reply With Quote
Old 05-02-2019, 07:42 PM   #11
Member
 
City: Jacksonville
Country: United States
Vessel Name: Water Lily
Vessel Model: TMC Custom 41 Trawler & S-2 10.3 Sail
Join Date: Nov 2018
Posts: 17
Quote:
Originally Posted by Mischief Managed View Post
Seems like somebody re-purposed your GEN-OFF_SHORE switch to tie the two panels together when in either GEN or SHORE. It would be a great use of your time to make a wiring diagram of how it is right now and make some new labels for the switch.
Yes
Next rainy day I will make a wiring diagram.
Thanks all
BigTime is offline   Reply With Quote
Old 05-02-2019, 08:25 PM   #12
Guru
 
Comodave's Avatar
 
City: Au Gres, MI
Country: US
Vessel Name: Never Say Never
Vessel Model: President 41 DC
Join Date: Jul 2015
Posts: 3,662
Does the slip with the 50 amp service have the new GFI? Maybe the slip with the 2 30 amp outlets does not. It sounds like maybe your neutrals are comingled on the boat. How experienced are you with marine electrical systems? If you donít have a good handle on it maybe you should call in a certified marine electricial to diagnose the problem. If you donít get it right it could cause a fire or worse.
Comodave is online now   Reply With Quote
Old 05-03-2019, 12:42 AM   #13
Senior Member
 
City: Seattle
Country: USA
Vessel Name: Conundrum
Vessel Model: Nordlund 63' Pilothouse
Join Date: Feb 2017
Posts: 111
Quote:
Originally Posted by Comodave View Post
Does the slip with the 50 amp service have the new GFI? Maybe the slip with the 2 30 amp outlets does not. It sounds like maybe your neutrals are comingled on the boat. How experienced are you with marine electrical systems? If you donít have a good handle on it maybe you should call in a certified marine electricial to diagnose the problem. If you donít get it right it could cause a fire or worse.


I think you are on to something with regards to the newer marina power systems. We have the new pedestals in neighboring marinas with ELCI. We were tripping 30A breakers when connecting our 50A cord to 2x30A with a Y adapter. Our boat electrician told me that I can't use the Y adapter with the 30A pedestals with ELCI. straight 50A to a single 30A is fine.
tozz is offline   Reply With Quote
Old 05-03-2019, 12:50 AM   #14
Guru
 
Comodave's Avatar
 
City: Au Gres, MI
Country: US
Vessel Name: Never Say Never
Vessel Model: President 41 DC
Join Date: Jul 2015
Posts: 3,662
I have twin 30s on my boat. I had to replace my main electrical panel and separate all the neutrals which took several days of tracing wiring. I have a 50amp to twin 30s adapter but I have not tried it on a GFI equiped dock yet. A lot of people are having problems around here since the marinas are upgrading to the GFIs on the docks. So many of the boat owners with tripping issues will insist that their boat does not have a problem but it trips the GFIs...
__________________

Comodave is online now   Reply With Quote
Reply

Thread Tools Search this Thread
Search this Thread:

Advanced Search
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off





All times are GMT -5. The time now is 10:22 AM.


Powered by vBulletin® Version 3.8.8 Beta 4
Copyright ©2000 - 2019, vBulletin Solutions, Inc.
Search Engine Optimization by vBSEO 3.6.0
Copyright 2006 - 2012